floydie: as an electrician i can say that some of you have misread what i said...
the breaker is specc'd to protect the wiring. period.
the size of cable used in a run is calculated by the allowable volt drop in the longest cable run so theoretically you could have a long lighting circuit fed by 2.5mm but only having a 10A breaker. . In 2011 they doubled the allowable volt drop so now you can actually have longer runs for a size of cable.
Yes socket outlets are only 10A rated, but thats just how it is and how its always been, the socket is the weak link. a single socket outlet fed by 2.5mm TPS on a 20A breaker is perfectly legal.
99% of houses are specced for 10A lighting circuits and 20A power outlets. 16A circuits are so rare now i dont think ive seen one in years i used 16A as an example as 16A is very common in those old push in breakers. thats because some of those old power circuits are only 1.5mm cable, whereas now all power ccts are 2.5mm.
5 amp lighting circuits are very rare. even 1mm tps is rated for 10A you dont derate a breaker to allow for volt drop...thats the wrong way to do it, you are supposed to up the cable size
having cable in insulation makes no difference, as i said before the volt drop allowed went from 2.5% to 5% allowing greater tolerance. a single cable run is not going to generate enough heat by itself even at max VD.
floydie: the insulation factor is so small, it wont make any appreciable difference in most house runs.
IMO derating cables by using smaller breakers is not best practice...
And if you look in the new regs...the VD has been increased from the old 2.5% back in the regs update in (2011?) although i always use 2.5 anyway.
floydie: no thats not right.
I worked for a contracting firm at the time and all our calcs changed to 5% pretty much as soon as the law was changed. it also changed in gencalc. the inspector confirmed this change as it just didnt seem right at the time. i couldnt understand why they tighten up the regs but loosen the allowable VD.
floydie: AS/NZS300:2007 clause 3.6.2
it doesnt say anything about the Installation splitting percentages in such a way. IT'S A PERCENTAGE...thats the point. you calc it on the MAXIMUM DEMAND or the MCB rating of the circuit you dont add up volt drops you add up maximum demand. every sub circuit is now calc'd at 5% because the upstream cable needs to be able to carry the maximum demand of all the ccts at .....5%
Whether its 5% of 10A or 5% of the mains maximum demand...its still 5%.
3.6.2 Value
The cross-sectional area of every current-carrying conductor shall be
such that the voltage drop between the point of supply for the low
voltage electrical installation and any point in that electrical
installation does not exceed 5% of the nominal voltage at the point of
supply.
3.6.2 Value
The cross-sectional area of every current-carrying conductor shall be
such that the voltage drop between the point of supply for the low
voltage electrical installation and any point in that electrical
installation does not exceed 5% of the nominal voltage at the point of
supply.
floydie: which is calc'd from max demand values..the sub cct will always be a smaller contributer than in the mains.
anyway your points simply reinforce my point...20A breaker for power circuits and 10A for lighting even factoring insulation in most modern homes. no point overthinking things.
You can never have enough Volvos!
There's mention of it here http://www.electricalforum.co.nz/index.php?action=more_details&id=1367272357 but the conclusion seems to be that the inserts are no longer available.
nickb800: Does anyone know anything about using inserts to protect users from live terminals when replacing breakers?
There's mention of it here http://www.electricalforum.co.nz/index.php?action=more_details&id=1367272357 but the conclusion seems to be that the inserts are no longer available.
I replaced my plug in rewirable fuses with NZI MCBs, and noticed there can be a small (say 1mm gap) between the body of the MCB and ceramic base. What's best practice for this?
Matthew
nickb800: Does anyone know anything about using inserts to protect users from live terminals when replacing breakers?
There's mention of it here http://www.electricalforum.co.nz/index.php?action=more_details&id=1367272357
mdooher:nickb800: Does anyone know anything about using inserts to protect users from live terminals when replacing breakers?
There's mention of it here http://www.electricalforum.co.nz/index.php?action=more_details&id=1367272357 but the conclusion seems to be that the inserts are no longer available.
I replaced my plug in rewirable fuses with NZI MCBs, and noticed there can be a small (say 1mm gap) between the body of the MCB and ceramic base. What's best practice for this?
No the inserts are no longer available. The reason is the inserts were designed to be placed in the ceramic base of the old rewirable fuse and then the breaker plugged in over it. This is no longer allowed. If you wish to replace a ceramic fuse with a plug in breaker you must get a sparky to replace the base as well.
If you have a ceramic base with a new plug-in breaker attached you will notice they don't mate properly leaving exposed contacts for fingers to touch. Obviously this is not permitted.
|
![]() ![]() ![]() |