#177585 7-Aug-2015 15:37
Send private message

Hi all,

Just wondering if anyone knows how much power a heat pump on standby would use? i.e. how much power does it use when you've switched it off with the remote, but not flicked the large power switch located outside. 

I'm sure power use by the heat pump is minimal, but am still interested to know (it's a very old, inefficient one - 12 years+ I think), and as it's internally wired I can't just plug in a power meter. I've searched online but can't find anything besides this table summary. It mentions air conditioners (it's American), but I'm not sure if that would be equivalent to our heat pumps or not.

http://standby.lbl.gov/summary-table.html

Thanks!

View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3
  #1360732 7-Aug-2015 15:50
Send private message

My underfloor (air-to-water) heatpump draws about 45W when it is *off*. For that reason I switch it off at the wall (external isolation switch) at the end of winter as 45W for 24/7 adds up!

Not sure about normal air-to-air units.



kiwichick12

20 posts

Geek


  #1360741 7-Aug-2015 16:07
Send private message

Wow that's a lot! I hope regular ones don't use that much.

Batman
Mad Scientist
29760 posts

Uber Geek

Trusted
Lifetime subscriber

  #1360805 7-Aug-2015 18:01
Send private message

i want to know too!



JayADee
2148 posts

Uber Geek


  #1360834 7-Aug-2015 18:51
Send private message

Well damn, I didn't even think of that. Now I also want to know!

Geektastic
17942 posts

Uber Geek

Trusted
Lifetime subscriber

  #1360845 7-Aug-2015 19:11
Send private message

I found an info sheet for a Fujitsu split unit that listed standby use at 9 watts.





timmmay
20575 posts

Uber Geek

Trusted
Lifetime subscriber

  #1360923 7-Aug-2015 21:29
Send private message

My UPS uses 15W when it's turned off. I've never measured my heat pumps, you'd need a clamp meter or something. I might turn them off in summer too, but then we use them for air conditioning.

Geektastic
17942 posts

Uber Geek

Trusted
Lifetime subscriber

  #1360936 7-Aug-2015 22:23
Send private message

timmmay: My UPS uses 15W when it's turned off. I've never measured my heat pumps, you'd need a clamp meter or something. I might turn them off in summer too, but then we use them for air conditioning.


Ditto. I doubt that there are more than 30 days a year when ours are not working one way or the other for at least part of the day or night.





 
 
 

Cloud spending continues to surge globally, but most organisations haven’t made the changes necessary to maximise the value and cost-efficiency benefits of their cloud investments. Download the whitepaper From Overspend to Advantage now.
kiwichick12

20 posts

Geek


  #1360938 7-Aug-2015 22:34
Send private message

I'm surprised they don't all have to state their idle power use somewhere in the heat pump specs, considering power usage:heat output is what they're graded on. 9watts per hour equates to 6.48kwh per month (based on 30 days) if idle the whole time. Or around $1.70-ish, $20+ a year. Not much, but still money wasted; and when you add it to the idle power use of other devices, it sure adds up.

Geektastic
17942 posts

Uber Geek

Trusted
Lifetime subscriber

  #1360945 7-Aug-2015 23:30
Send private message

kiwichick12: I'm surprised they don't all have to state their idle power use somewhere in the heat pump specs, considering power usage:heat output is what they're graded on. 9watts per hour equates to 6.48kwh per month (based on 30 days) if idle the whole time. Or around $1.70-ish, $20+ a year. Not much, but still money wasted; and when you add it to the idle power use of other devices, it sure adds up.


Meh. It's just money.





KGM

KGM
5 posts

Wannabe Geek


  #1360990 8-Aug-2015 08:13
Send private message

I have a Mitsubishi Unit. It Draws 0.7A while not running.

P = VI
= 230 * 0.7
= 161W

Multiply this by 24 hrs to give the daily power usage..

24*161 = 3864W
=3.86kWhr / day

Power Consumption for Jan was 122.37kWHr, Feb 114.71kWHr & Mar was 125.69kWHr. The only runtime during that period was for 33 minutes in Feb.

Having now accumulated the data for a calendar year to get a base line, I will be turning off the heat pump at the isolator for the summer months, where I am not using it.

I am told that the majority of the power consumption is due to the crankcase heater & not the electronic controls of the heat pump. Refrigeration engineers may be able to advise on this. 



kiwichick12

20 posts

Geek


  #1361015 8-Aug-2015 09:35
Send private message

3.86kWh a day? That equates to ~ $30 month! I'd definitely be keeping that sucker turned off.

timmmay
20575 posts

Uber Geek

Trusted
Lifetime subscriber

  #1361037 8-Aug-2015 09:48
Send private message

Anyone know what a Nocria Awtz24l uses? How about a Daikin FTXS60FVMA?

jmh

jmh
458 posts

Ultimate Geek


  #1361041 8-Aug-2015 10:08
Send private message

Gosh, you add that to the cost of HRV, and constantly broadcasting phones and wifi, it's no wonder my power bills are so high.  

wsnz
649 posts

Ultimate Geek


  #1361437 9-Aug-2015 10:41
Send private message

If anyone does decide to turn off the heat pump at the isolator for an extended period of time, make sure that before using the heat pump again, you comply with the minimum amount of time (up to a full day) indicated in the manual for the crank-case heater to warm up the compressor otherwise damage can occur to the compressor. In most cases the warranty will be voided if you don't follow those minimum guidelines.

 

Also make sure that the unit has been thoroughly dried by using the heat mode for an hour or two, before decommissioning.

MadEngineer
4271 posts

Uber Geek

Trusted

  #1361482 9-Aug-2015 12:17
Send private message

kiwichick12:(it's a very old, inefficient one - 12 years+ I think),

When did you last have it serviced?  I highly suggest that you do then when the electrician comes to check it out you can ask them to check how much it's drawing when idle.  If they're good they'll likely try to sell you on the benefits of upgrading to a modern inverting unit (yours probably just turns off and on to maintain a temperature rather than trickling heat) to which you can consider or politely decline ...




You're not on Atlantis anymore, Duncan Idaho.

 1 | 2 | 3
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.