I am familiar with USB chargers, but they have nothing to do with this conversation. No-one has offered any proof of this statement that a dual outlet can only supply two loads totalling 10A and not 10A per outlet (which is how they are labelled).
Please try to play nicely and get along with each other.
And consider the PDL644 - a four-gang outlet with four 10A sockets that has the same rating as those above. I think that speaks for itself.
What about a PDL 693/2? Two individual outlets on one faceplate.
@irongarment thats not how it works.
go download the AS/NZS standard and do some reading instead of posting incorrect and potentially dangerous information.
RunningMan:
What about a PDL 693/2? Two individual outlets on one faceplate.
Easiest way is to go and search for the Sdoc, this will contain the answers
Jase2985:@irongarment thats not how it works.
go download the AS/NZS standard and do some reading instead of posting incorrect and potentially dangerous information.
Hi, you must remember that the rating of the MCB that feeds a single circuit has to take into account the overall length of that circuit, hence technically a 2.5mm TPS cable can be protected by a 20A MCB, but as the circuit lenth increases this must be derated, therefore its common to have 16A MCBs on house power outlet circuits.
So yes you are correct you can in theory connect two 10A loads to a dual outlet and assuming there is a 20A MCB supplying that circuit its all fine and dandy, however in reality cable lengths may crimp that back to 16A.
Just a point on tone of voice, I am sure you are level headed and not trying to be offensive, but the folk that have responded here are mostly professionals who do this work everyday, just like most of us early on in your work life you learn some basic rules and understandings and automatically apply them to everday work, these automated duties typically deliver trade related compliant outcomes, please offer some respect for those that have come here to offer the advise in their own time.
Cyril
cyril7:Hi, you must remember that the rating of the MCB that feeds a single circuit has to take into account the overall length of that circuit, hence technically a 2.5mm TPS cable can be protected by a 20A MCB, but as the circuit lenth increases this must be derated, therefore its common to have 16A MCBs on house power outlet circuits.
So yes you are correct you can in theory connect two 10A loads to a dual outlet and assuming there is a 20A MCB supplying that circuit its all fine and dandy, however in reality cable lengths may crimp that back to 16A.
Just a point on tone of voice, I am sure you are level headed and not trying to be offensive, but the folk that have responded here are mostly professionals who do this work everyday, just like most of us early on in your work life you learn some basic rules and understandings and automatically apply them to everday work, these automated duties typically deliver trade related compliant outcomes, please offer some respect for those that have come here to offer the advise in their own time.
Cyril
irongarment:cyril7:
Hi, you must remember that the rating of the MCB that feeds a single circuit has to take into account the overall length of that circuit, hence technically a 2.5mm TPS cable can be protected by a 20A MCB, but as the circuit lenth increases this must be derated, therefore its common to have 16A MCBs on house power outlet circuits.
So yes you are correct you can in theory connect two 10A loads to a dual outlet and assuming there is a 20A MCB supplying that circuit its all fine and dandy, however in reality cable lengths may crimp that back to 16A.
Just a point on tone of voice, I am sure you are level headed and not trying to be offensive, but the folk that have responded here are mostly professionals who do this work everyday, just like most of us early on in your work life you learn some basic rules and understandings and automatically apply them to everday work, these automated duties typically deliver trade related compliant outcomes, please offer some respect for those that have come here to offer the advise in their own time.
Cyril
Thanks for that. It is a thoughtful reply. Most of the replies have been regurgitation of speculation and hearsay with no facts to back them up, or no evidence of any reasoning behind them. I thoroughly respect professionals who can state their opinion based on sound logic, or recite facts as facts.
I realise now that only one socket is tested, but I still fail to see why drawing 10A each from two outlets in the same box is any different to drawing 10A each from two single sockets sitting side by side. If this was the case people would be advised and the government would insist on an appropriately worded warning label in the outlet, just as they do for power boards and other electrical items.
More than likely the way the screw terminal is bonded to the internal links to pins on the outlet is the reason why "up to 16A" is stated.
yep the common conductor components are the key detail here.
Cyril
RunningMan:this is also rated at only 10A. Even though you could run two individual cables to it — which it’s designed for eg where you could have each cable then remotely individually switched. The issue would be if you were daft enough to daisy chain one outlet to the other where the termination at the back of the common would then have to carry the load of both. Instead of wiring it like that you’d just buy a 695.What about a PDL 693/2? Two individual outlets on one faceplate.
MadEngineer: . The issue would be if you were daft enough to daisy chain one outlet to the other where the termination at the back of the common would then have to carry the load of both. Instead of wiring it like that you’d just buy a 695.
|
![]() ![]() ![]() ![]() |