HarmLessSolutions
969 posts

Ultimate Geek

Subscriber

  #3325879 29-Dec-2024 13:25
Send private message quote this post

Jase2985:

 

dantheperson: 
Have you been checking mains voltage levels? I got the email this morning saying the inverter restarted yesterday afternoon due to high voltages. Output would have been curtailed long before it got to the point of restarting. I'm starting to grow a hunch that voltage management is worse on weekends and holidays.

 

for me its defiantly related to what others are doing, if they are at home there seems to be more AC and other usage which lowers the grid voltage.

 

Vector is running our area at the higher end of the acceptable voltage range. which when a few people are generating power via solar it pushes the grid voltage up even more into that area where the inverter starts to curtail generation to compensate and not contribute to the issue anymore.

 

I'd put money on it being related to grid voltage being too high. The relationship with it worsening on weekends and/or holidays will be due to commercial use being lower maybe as well as domestic use increasing slightly. If your local network has other solar customers on it the increased export by them, and you, will also be increasing grid voltages. Your own consumption (displacing export) will also serve to lower your local grid voltage as I observe when we plug in our EVSE at peak generation times.

 

The underlying problem is that the lines companies' grid infrastructure is pretty crude and archaic so in order to provide their customers who are furthest from the transformer/voltage regulators an acceptable grid voltage after transmission resistance voltage drop they just crank up the supplied voltage at the source, and bad luck for us solar owning customers who suffer the consequences we're seeing here.

 

We had an interesting conversation with our neighbour a couple of days back. She works for Powerco and is aware of the excess voltage issue we are having so has been asking a few questions at her work. It seems the transformer and voltage regulator that were installed down the road from us a few months back was intended to address low voltage issues for some more remote customers. Bingo, that was when our current problems started! Now to get Powerco to analyze the data from the voltage logger they have in place and work out how they can provide an acceptable grid voltage to us.

 

@LightbulbNeil, If your 15kW 3 phase Fronius runs the same Solarweb monitoring package as our 8.2 Primo Fronius then go into the Analysis option, then History, then go to the Devices and tick both the Meter and inverter boxes. Then go into the Channels and tick the Power MPP1 & MPP2, plus as many other arrays the inverter has incoming and tick the Voltage AC L1 (and possibly other options to see all your phases). Then click Okay.

 

You should see something like this now (perhaps with more lines for more arrays and phases):

 

 

Note the grid voltage was in excess of 246V at 13:00 but dropped to ~241V when I plugged our Polestar in to charge for a couple of hours. Also the 5kW phase export cap is ensured by dropping current from MPP1 array and this was occurring either side of the EV charging but the excess grid voltage is causing the inverter to struggle to export even 4.5kW, as well as restricting total generation. The way our installer describes the situation at play is that the inverter sees excessive grid voltage and decreases its output to avoid worsening the situation. This de-rating occurs when the grid exceeds 243V (as our nominal voltage is supposed to be 230V +/- 6%, so 243.8V maximum. Beyond that voltage the inverter restricts output with a hard limit being set at 249V when it will shut down until the grid voltage stabilises closer to 'normal'. We are seeing reductions of around 10% in our export and generation levels compared to this time last year. Last summer we saw generation sitting at 8.2kW for a few hours over the middle of the day but now struggle to make 7.7kW, despite 9.5kW of panels feeding the inverter.

 

These parameters are in line with standard AS/NZS 4777.2:2020 so long as your installer has put these in place. The problem, at least in our case is that our grid voltage is looking for like 240V being nominal but the inverter must legally be set to 230V. From comments from earlier posts it seem at least one lines company is still working to AS/NZS 4777.2:2015 which has wider parameters so it really is the 'wild west' out there as far as lines companies' behaviour is concerned. Also there is a ray of hope on the horizon as standard AS/NZS 4777.2:2024 which comes into force in a couple of months allows for 230V +/-10% setting on inverters which will solve our problems at least for a while, until solar uptake increases further which is likely to impact on grid voltages.

 

Also the cooling issues you have had may be linked to excessive grid voltages I'm guessing. I know when I'm near the inverter and watching the output yo-yo due to grid conditions it does seem that the cooling fan is putting in plenty of effort so the inverter seems to be working hard to cope with the situation.

 

 





https://www.harmlesssolutions.co.nz/


LightbulbNeil
57 posts

Master Geek


  #3325886 29-Dec-2024 13:48
Send private message quote this post

That maybe what it is. The voltage for export got to 245.5v yesterday and today has been 246.7v. Maybe with alot of people being away there is excess energy in the grid for Hamilton this weekend.
Will check in January with the installer and get Fronius NZ to look at all the data. We are not capped for export fof our system, but effectively we are capped by the lines voltages.
Thanks for the replies.
Neil Lickfold.
Ps, does a 1100 w/m2 mean that thd panels will be capabke of producing 10% more during that condition assuming no high cloud etc?

  #3325887 29-Dec-2024 14:00
Send private message quote this post

LightbulbNeil: That maybe what it is. The voltage for export got to 245.5v yesterday and today has been 246.7v. Maybe with alot of people being away there is excess energy in the grid for Hamilton this weekend.
Will check in January with the installer and get Fronius NZ to look at all the data. We are not capped for export fof our system, but effectively we are capped by the lines voltages.
Thanks for the replies.
Neil Lickfold.
Ps, does a 1100 w/m2 mean that thd panels will be capabke of producing 10% more during that condition assuming no high cloud etc?

 

100% the inverter is limiting the output power based on that voltage, it will drop by 7.272% per volt over its setting of either 5 or 6% country grid voltage of 230V, so 242V or 244V

 

It also limits based on reactive power, which is impacted by power factor so the inverter might be making 8,000Var but the active power might be 7,500W so the inverter is still working hard to produce its maximum output but the power factor is driving down the output we look at which is the Watts.

 

What the lines companies are doing about this, who knows but when NZ only have 2-3% residential solar uptake compared to Australia which has 20+% and we seem to be having more issues than they have had it seems like something needs to be done.


LightbulbNeil
57 posts

Master Geek


  #3325899 29-Dec-2024 14:20
Send private message quote this post

We tried testing using 9kw of power,
The solar production did not change at all.
Only the export amount dropped.
Thanks for the help and replies.
Neil

HarmLessSolutions
969 posts

Ultimate Geek

Subscriber

  #3325900 29-Dec-2024 14:21
Send private message quote this post

Jase2985:

 

........

 

What the lines companies are doing about this, who knows but when NZ only have 2-3% residential solar uptake compared to Australia which has 20+% and we seem to be having more issues than they have had it seems like something needs to be done.

 

 

We're a long way behind Australia so far as our grid compatibility with distributed generation (i.e. solar). Our two countries share the same electrical standards (AS/NZS 4777) but NZ seems to be slow to follow suit when changes occur. Australia reduced the nominal grid voltage from 240V to 230V over the past decade, state by state, in order to provide a buffer when solar generation increase started impacting grid voltages and therefore threatened infrastructure and in theory NZ should have followed suit. The problem is that so much of the lines companies' infrastructure is outdated and unable to be upgraded short of replacing assets, and Powerco is one of the worst in this respect.

 

As a result cheap shortcuts are being actioned in order to band aid issues that occur. The situation of increasing voltage at input point in order to address inadequate voltage at the far end of their transmission system is one such cheap and nasty shortcut and the issues we're discussing here is the result.

 

What worries me is that the lines company charge increases that are coming down the line next year are justified in order to upgrade grid infrastructure, so does that mean us Powerco customers will be on the receiving end of some of the biggest increases? Currently the daily fixed charge here is $1.38 but our installer has associates in Central Otago whose customers are now paying $5/day. That $1,800/year takes a lot of export to offset and is a great incentive to upgrade any sizeable PV installation towards off-grid ability, particularly if grid voltages are diluting generation output in a grid tied situation I guess.





https://www.harmlesssolutions.co.nz/


  #3325901 29-Dec-2024 14:25
Send private message quote this post

LightbulbNeil: We tried testing using 9kw of power,
The solar production did not change at all.
Only the export amount dropped.
Thanks for the help and replies.
Neil

 

but did it drop the voltage at the grid (smart meter or other) if the voltage is still high, and it can still be when you have a large load and the grid voltage is still high then its not going help with the inverter output.

 

 

 

 


HarmLessSolutions
969 posts

Ultimate Geek

Subscriber

  #3325902 29-Dec-2024 14:32
Send private message quote this post

LightbulbNeil: We tried testing using 9kw of power,
The solar production did not change at all.
Only the export amount dropped.
Thanks for the help and replies.
Neil

 

I've seen that same situation. The inverter is stepping its output down due to excessive grid voltage and whether you're consuming or exporting that generation doesn't seem to impact the inverter's performance.

 

Also from what I understand the voltage the inverter is seeing is at your feed-in point (meter) but this may differ from that in the lines your supply comes from, particularly if like in our case the length of cabling into your property is significant and/or the cable thickness is a restricting factor. The analogy I'm envisaging is that voltage is 'pressure' and if the length and size of the cabling is deficient that will cause a 'bottleneck' as it goes to or from the public grid.

 

In this respect excessive grid voltage becomes extra 'back-pressure' for your inverter to work against.





https://www.harmlesssolutions.co.nz/


  #3325903 29-Dec-2024 14:33
Send private message quote this post

HarmLessSolutions:

 

Jase2985:

 

........

 

What the lines companies are doing about this, who knows but when NZ only have 2-3% residential solar uptake compared to Australia which has 20+% and we seem to be having more issues than they have had it seems like something needs to be done.

 

 

We're a long way behind Australia so far as our grid compatibility with distributed generation (i.e. solar). Our two countries share the same electrical standards (AS/NZS 4777) but NZ seems to be slow to follow suit when changes occur. Australia reduced the nominal grid voltage from 240V to 230V over the past decade, state by state, in order to provide a buffer when solar generation increase started impacting grid voltages and therefore threatened infrastructure and in theory NZ should have followed suit. The problem is that so much of the lines companies' infrastructure is outdated and unable to be upgraded short of replacing assets, and Powerco is one of the worst in this respect.

 

As a result cheap shortcuts are being actioned in order to band aid issues that occur. The situation of increasing voltage at input point in order to address inadequate voltage at the far end of their transmission system is one such cheap and nasty shortcut and the issues we're discussing here is the result.

 

What worries me is that the lines company charge increases that are coming down the line next year are justified in order to upgrade grid infrastructure, so does that mean us Powerco customers will be on the receiving end of some of the biggest increases? Currently the daily fixed charge here is $1.38 but our installer has associates in Central Otago whose customers are now paying $5/day. That $1,800/year takes a lot of export to offset and is a great incentive to upgrade any sizeable PV installation towards off-grid ability, particularly if grid voltages are diluting generation output in a grid tied situation I guess.

 

 

We are already on a 230V grid, but it hardly ever looks that way. i saw 233.6v at 2145 last night when the hot water cylinder came on, and 229V the previous night about the same time. average would be about 239V well above the 230 nominal but still within the regulations

 

From what I've seen unless you are a low user then that daily charge is low for a standard user, if they have been consistent with all their connections etc then no wonder they are behind with money for infrastructure. Auckland when i was looking was $2 - $3 per day for standard user.


HarmLessSolutions
969 posts

Ultimate Geek

Subscriber

  #3325910 29-Dec-2024 15:02
Send private message quote this post

Jase2985:

 

We are already on a 230V grid, but it hardly ever looks that way. i saw 233.6v at 2145 last night when the hot water cylinder came on, and 229V the previous night about the same time. average would be about 239V well above the 230 nominal but still within the regulations

 

From what I've seen unless you are a low user then that daily charge is low for a standard user, if they have been consistent with all their connections etc then no wonder they are behind with money for infrastructure. Auckland when i was looking was $2 - $3 per day for standard user.

 

 

We are on a Low User plan with Octopus because as would be expected our electricity demand from the grid is miniscule as our annual generation is close to our total generation for the year.

 

You're seeing much lower grid voltages than yours. It is extremely rare for us to see 235V or below here. We are seeing what we would expect to if our nominal supply voltage was 240V nominal.





https://www.harmlesssolutions.co.nz/


HarmLessSolutions
969 posts

Ultimate Geek

Subscriber

  #3325977 29-Dec-2024 16:55
Send private message quote this post

Having just taken a look at the poletop transformer serving our property I see it is a 50kVA Etel one. According to Etel's spec's the lower end of the LV voltage from these is 240V. It seems my observations that the grid voltage we're seeing is nominally 240V may well be the case. Time for some questions to Powerco in the New Year I think.





https://www.harmlesssolutions.co.nz/


  #3325983 29-Dec-2024 17:28
Send private message quote this post

HarmLessSolutions:

 

Having just taken a look at the poletop transformer serving our property I see it is a 50kVA Etel one. According to Etel's spec's the lower end of the LV voltage from these is 240V. It seems my observations that the grid voltage we're seeing is nominally 240V may well be the case. Time for some questions to Powerco in the New Year I think.

 

 

Most of them appear to be 240V. They do say HV tappings +2.5% to -7.5% in 2.5% steps. So would either use 234V or 240V i would say. I don't know enough about them, but would they use 246V and let the loads sag the voltage down?


LightbulbNeil
57 posts

Master Geek


  #3326077 29-Dec-2024 21:34
Send private message quote this post

So when I did my test today, the voltage dropped by 5 V to 240.1v  .  After the test it went back to 245.32v.  The PV production stayed around the 13.4 kW or so. 

 

I don't have the log in to see the temp data etc of the inverter. But will see if I can get that to look at that data too.

 

Our house is wired with 16mm cable from the street box to the house. Total length to the Meter board from the street box is about 32m distance.

 

Its possible with the last upgrades that happened that some kind of metering is taking place. Could still be the voltage thing of course.

 

If they ever do bring in ridiculous daily charges, will then look seriously at off grid solutions and a large battery to get us through winter. 

 

Edit,

 

Back on the 26th Dec, we had peak generation of 15.15kW and the AC line voltage was 245.09.  but it does not keep making power at that rate for very long. it's like its over heating or something. I can't see what the peak solar energy was for that day, as that is not kept in the history data. 

 

So I am now thinking more along the lines that there is something not correct with the box itself.

 

Neil


dantheperson
174 posts

Master Geek


  #3326088 29-Dec-2024 22:37
Send private message quote this post

LightbulbNeil:

So when I did my test today, the voltage dropped by 5 V to 240.1v  .  After the test it went back to 245.32v.  The PV production stayed around the 13.4 kW or so. 


I don't have the log in to see the temp data etc of the inverter. But will see if I can get that to look at that data too.


Our house is wired with 16mm cable from the street box to the house. Total length to the Meter board from the street box is about 32m distance.


Its possible with the last upgrades that happened that some kind of metering is taking place. Could still be the voltage thing of course.


If they ever do bring in ridiculous daily charges, will then look seriously at off grid solutions and a large battery to get us through winter. 


Edit,


Back on the 26th Dec, we had peak generation of 15.15kW and the AC line voltage was 245.09.  but it does not keep making power at that rate for very long. it's like its over heating or something. I can't see what the peak solar energy was for that day, as that is not kept in the history data. 


So I am now thinking more along the lines that there is something not correct with the box itself.


Neil



But if u r on 3 phase, then r u checking voltages on each phase? Maybe the load u added dropped the voltage on phase 1 but 2 and three still saw reduced output?

HarmLessSolutions
969 posts

Ultimate Geek

Subscriber

  #3326109 30-Dec-2024 09:06
Send private message quote this post

Jase2985:

 

HarmLessSolutions:

 

Having just taken a look at the poletop transformer serving our property I see it is a 50kVA Etel one. According to Etel's spec's the lower end of the LV voltage from these is 240V. It seems my observations that the grid voltage we're seeing is nominally 240V may well be the case. Time for some questions to Powerco in the New Year I think.

 

 

Most of them appear to be 240V. They do say HV tappings +2.5% to -7.5% in 2.5% steps. So would either use 234V or 240V i would say. I don't know enough about them, but would they use 246V and let the loads sag the voltage down?

 

Are you (or anyone else on Geekzone) familiar enough with transformers to know what tap position this is? The 'arm' seems linked into #2 but the "Tap Position" arrow above indicates #3.

 





https://www.harmlesssolutions.co.nz/


  #3326164 30-Dec-2024 12:25
Send private message quote this post

HarmLessSolutions:

 

Jase2985:

 

HarmLessSolutions:

 

Having just taken a look at the poletop transformer serving our property I see it is a 50kVA Etel one. According to Etel's spec's the lower end of the LV voltage from these is 240V. It seems my observations that the grid voltage we're seeing is nominally 240V may well be the case. Time for some questions to Powerco in the New Year I think.

 

 

Most of them appear to be 240V. They do say HV tappings +2.5% to -7.5% in 2.5% steps. So would either use 234V or 240V i would say. I don't know enough about them, but would they use 246V and let the loads sag the voltage down?

 

Are you (or anyone else on Geekzone) familiar enough with transformers to know what tap position this is? The 'arm' seems linked into #2 but the "Tap Position" arrow above indicates #3.

 

 

 

The need to start investing in and installing these

 

http://www.eteltransformers.co.nz/wp-content/uploads/2022/09/Voltage-regulation-WEB.pdf 

 

Have asked a question about the transformer to someone in the know


1 | ... | 68 | 69 | 70 | 71 | 72 | 73 | 74 | 75 | 76 | 77 | 78 | ... | 98
View this topic in a long page with up to 500 replies per page Create new topic



News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.