mdav056

607 posts

Ultimate Geek

Subscriber

#269683 1-Apr-2020 22:04
Send private message

I have an F&P fridge/freezer which runs off a kitchen circuit that is protected by a wall-mounted RCD.  It sometimes pops the RCD off, resulting in disaster if we missed the off.  I *think* I have seen this discussed before on GZ, but I can't find the discussion.  Has anyone any ideas about how I can stop this happening (apart from running a long lead across the kitchen floor...).

 

Thanks for any help -

 

 





gml


Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3
  #2452652 1-Apr-2020 22:08
Send private message

does the RCD pop with any other loads connected? when you test the RCD does it test fine?




mdav056

607 posts

Ultimate Geek

Subscriber

  #2452655 1-Apr-2020 22:11
Send private message

It's a brand new RCD, properly installed about 6 months ago, and it is the only appliance running off the RCD.  But I haven't tried other loads (and hard to do so -- it only does this every 2-3 weeks).





gml


sparkz25
750 posts

Ultimate Geek
Inactive user


  #2452688 1-Apr-2020 22:39
Send private message

how old is the fridge?




fe31nz
1229 posts

Uber Geek


  #2452706 1-Apr-2020 23:51
Send private message

We have a heater on an RCD that can trigger its RCD sometimes when it is turned off.  I would expect that it would be caused by the back EMF from the electric motor when it stops.  So your fridge may be the same.  If you can, see if the RCD is triggering when the fridge turns its compressor off when it reaches the setpoint temperature.  Or maybe just turn it off at the plug while the compressor is running, and see if that can trigger the RCD.  A call to F&P tech support would seem to be a good idea also - they may know about the problem, if they have anyone on duty at the moment: 0800-372-273.


surfisup1000
5288 posts

Uber Geek


  #2452707 1-Apr-2020 23:57
Send private message

mdav056:

 

I have an F&P fridge/freezer which runs off a kitchen circuit that is protected by a wall-mounted RCD.  It sometimes pops the RCD off, resulting in disaster if we missed the off.  I *think* I have seen this discussed before on GZ, but I can't find the discussion.  Has anyone any ideas about how I can stop this happening (apart from running a long lead across the kitchen floor...).

 

Thanks for any help -

 

 

 

 

May have been me   .. our F&P fridge/freezer was popping our RCD -- F&P diagnosed a failed defrost heating element. Over time our fridge related RCD trips occurred more frequently.    

 

https://www.geekzone.co.nz/forums.asp?forumid=141&topicid=191412

 

Check if your model has a defrost element. You might have to call a service agent. From memory, it was around $200 to fix. 


snnet
1410 posts

Uber Geek


  #2452708 1-Apr-2020 23:58
Send private message

Common for fridges to do this, had it a few times. Needs some kind of repair, can't remember what sorry. Clients usually end up with a new fridge.

 

You might want to check its not something else on the same circuit though like a jug with the base that seperates from the actual jug - have had moisture in the contacts of the base before causing intermittent tripping on a particularly painful job where every time I went to trace the fault they'd put the jug in a cupboard (despite asking what was being used at the time), and finally the last time there it was on the bench.


Goosey
2829 posts

Uber Geek

Subscriber

  #2452787 2-Apr-2020 09:50
Send private message

My mums F&P fridge freezer did this... popped RCD. 

 

Tech replaced a small part... for the life of me I cant remember what it was called.... It was somthing to do with the compressor and temp sensor...

 

I can vaguely remember interpreting the part as a simple diode rectifyer. 

 

 

 

 


 
 
 

Move to New Zealand's best fibre broadband service (affiliate link). Note that to use Quic Broadband you must be comfortable with configuring your own router.
Zeon
3916 posts

Uber Geek

Trusted

  #2452789 2-Apr-2020 09:53
Send private message

Just an idea for the short term - could you put a simple plug in light on the same plug point. Then if you notice the light off you know the RCD has tripped?





Speedtest 2019-10-14


BlinkyBill
1443 posts

Uber Geek
Inactive user


  #2452807 2-Apr-2020 10:25
Send private message

Why would anyone put a fridge on an RCD, what’s wrong with the normal circuit board protections?


elpenguino
3421 posts

Uber Geek


  #2452815 2-Apr-2020 10:43
Send private message

BlinkyBill:

 

Why would anyone put a fridge on an RCD, what’s wrong with the normal circuit board protections?

 

 

RCDs are normal protection , now. Rewire-able fuses are rightly a thing of the past.

 

It does high light an issue though. Some houses will have their circuits wired through a few RCDs and if a fault on any circuit that shares the RCD trips the RCD and you don't realise, there goes your fridge/freezer contents.





Most of the posters in this thread are just like chimpanzees on MDMA, full of feelings of bonhomie, joy, and optimism. Fred99 8/4/21


  #2452817 2-Apr-2020 10:46
Send private message

BlinkyBill:

 

Why would anyone put a fridge on an RCD, what’s wrong with the normal circuit board protections?

 

 

As I understand it, if a sparky puts in a new circuit, or adds power points to an existing circuit, then the new / changed circuit has to go on an RCD - it's in the Wiring Regulations.

 

Or so my sparky told me


elpenguino
3421 posts

Uber Geek


  #2452820 2-Apr-2020 10:50
Send private message

PolicyGuy:

 

BlinkyBill:

 

Why would anyone put a fridge on an RCD, what’s wrong with the normal circuit board protections?

 

 

As I understand it, if a sparky puts in a new circuit, or adds power points to an existing circuit, then the new / changed circuit has to go on an RCD - it's in the Wiring Regulations.

 

Or so my sparky told me

 

 

That's correct. One way to meet the requirements is to use power points with RCDs built in, which might be what OP has.





Most of the posters in this thread are just like chimpanzees on MDMA, full of feelings of bonhomie, joy, and optimism. Fred99 8/4/21


dan

dan
1134 posts

Uber Geek

Lifetime subscriber

  #2452822 2-Apr-2020 10:53
Send private message

i had a issue with the Fridge popping the RCD, was a faulty element of some sort, it was a pretty easy fix and cost less than a couple of hundred dollars with parts and onsite labour, the tech knew exactly what it would

 

be when he turned up


BlinkyBill
1443 posts

Uber Geek
Inactive user


  #2452840 2-Apr-2020 11:18
Send private message

Interesting. The Wiring Regulations were updated in 2018 and from November 2018 there were new RCD regulations to conform to. The regulations beefed up the requirement for RCD’s in many/most domestic circumstances and brought NZ more in line with AU requirements.

 

More interestingly, there are 294 new requirements as from Nov 2018, for wiring, compared with a very much smaller set of changes previously - 87 over the previous 30-odd years.

 

More good reasons for using an electrician, I guess.


nickb800
2716 posts

Uber Geek

Trusted

  #2452851 2-Apr-2020 11:38
Send private message

BlinkyBill:

 

Interesting. The Wiring Regulations were updated in 2018 and from November 2018 there were new RCD regulations to conform to. The regulations beefed up the requirement for RCD’s in many/most domestic circumstances and brought NZ more in line with AU requirements.

 

More interestingly, there are 294 new requirements as from Nov 2018, for wiring, compared with a very much smaller set of changes previously - 87 over the previous 30-odd years.

 

More good reasons for using an electrician, I guess.

 

 

My understanding is that RCD has been required for new socket outlets since the 2007 standard. Under 2007 regs there was an exemption for things that were hard wired in like hot water cylinders and ovens, but the 2018 standard get rid of that exemption. However, I understand the 2018 standard isn't in legal effect, and it sounds like it will be revised before it comes into legal effect - which may mean that hard wired things can continue to be installed without RCD protection. 

 

As a 'loophole', presumably you could in theory chop the plug off your fridge and hard wire it to negate the need for an RCD? Not that it would be very practical. 


 1 | 2 | 3
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.