I wonder if it has anything to do with the power factor of computers etc and other appliances with AC motors etc that have a certain amount of non-sinewave feedback, as opposed to pure resistive loads. I thought power meters were actually supposed to measure the average power.


Having designed a few power meters in the past of which there are many thousands in current use throughout the world I might comment here.

Modern electronic power meters have the ability to record both active and reactive power, however in single phase domestic situations only your active power is registered for consumption, so if your load presents a poor power factor then that reactive component does not contribute to your bill. Naturally its in the retailer (and lines companies) interest to ensure that the power factor is within a manageable limit.

Older ferraris meters in theory do the same but with nowhere near the accuracy over the same dynamic range as modern electronic solutions.

Cyril



gzt

gzt
17160 posts

Uber Geek

Lifetime subscriber

  #430460 24-Jan-2011 10:04
Send private message

@sattv - just making sure we get this right - your Elster gREX D AMi meter was replaced with another Elster gREX D AMi meter. The replacement reads high. Is this correct?




Signature goes here.


Damager
2125 posts

Uber Geek


  #430730 24-Jan-2011 21:12
Send private message

cyril7:
I wonder if it has anything to do with the power factor of computers etc and other appliances with AC motors etc that have a certain amount of non-sinewave feedback, as opposed to pure resistive loads. I thought power meters were actually supposed to measure the average power.


Having designed a few power meters in the past of which there are many thousands in current use throughout the world I might comment here.

Modern electronic power meters have the ability to record both active and reactive power, however in single phase domestic situations only your active power is registered for consumption, so if your load presents a poor power factor then that reactive component does not contribute to your bill. Naturally its in the retailer (and lines companies) interest to ensure that the power factor is within a manageable limit.

Older ferraris meters in theory do the same but with nowhere near the accuracy over the same dynamic range as modern electronic solutions.

Cyril


Been quite interesting about the comparison's of the new smart meters and their accuracy.

Cyril can you please give an example of an appliance presenting only active power  for consumption against a non smart meter? Just trying to understand the situation in layman's terms. As i understand it, a pure resistive load presents a constant load that is easily measured. An unbalanced load presents varying levels load of which only some or the average load is recorded as consumption on the meter.

 




- Telstra HTC Touch Pro2 - Energy ROM WM6.5.5 20 Oct/Cyanogen Mod Froyo 2.2 - R.I.P
- AT&T Galaxy S Captivate 16GB on XT (now with brother)
- Samsung Galaxy S2 on XT- Runs ICS 4.0.3 Resurrection Remix 9.2
- Business Hours - Work In The Electricity Industry, After Hours - DJ/Turntablist - Will Scratch Vinyl For Free'
- What's next??? S3?



richms
28198 posts

Uber Geek

Trusted
Lifetime subscriber

  #430738 24-Jan-2011 21:29
Send private message

With AC you cant just average the current and the voltage and get a true watt reading. While none were dumb enough to do that (unlike the first versions of some plug in meters seemed to) there is still an issue of how often you sample. They have to take great care not to overcharge, which would happen if they just used the peak current in the sample period so there is some really agressive lowpass filtering going on in them.

You need to get the current and voltage at that moment and calculate the instantaneous wattage and then average that. The higher the sample rate that is done at then the more accurate you get. Its not uncommon to find the peak wattage of some loads to be kilowatts. I am suprised that the questionable power supply companies dont put that on the side of them instead of the the current BS of several 100 watts.

I get the feeling that some of the plug in type meters are not even sampling continuously either which is another gotcha if you have something like my friends DIY reflow oven that is only on for some cycles and not others.

If you want to see how bad you can do it and still get somewhat usable results, look at the tweet-a-watt project, on AC cycle every 2 seconds is sampled, 17 samples (I think from memory) and then calculated on. And its not that bad for accuracy compared to the first revision of the elto plugin meter.




Richard rich.ms

SATTV

1648 posts

Uber Geek

ID Verified

  #430760 24-Jan-2011 22:01
Send private message

@gzt We had an ADR remote read meter for about 3 years, then a new  Elster gREX D AMi meter was replaced with another Elster gREX D AMi meter. It was the first Elster that was reading High.

John




I know enough to be dangerous


richms
28198 posts

Uber Geek

Trusted
Lifetime subscriber

  #430762 24-Jan-2011 22:03
Send private message

I am wondering if they are calibrating the new ones lower and will slowly edge it up to accurate over time to appease those that dont like to suddenly pay what they are actually using. I am assuming they can remotely read and manipulate the calibration registers inorder to create a fudge factor in them.




Richard rich.ms

MikeSkyrme
272 posts

Ultimate Geek

Trusted

  #430771 24-Jan-2011 22:21
Send private message

Shouldn't fiscal / tariff meters be built to a specification? It would interesting to see the spec that they are manufactured to. Anyone have any ideas where this might be found?




Michael Skyrme - Instrumentation & Controls

 
 
 

Move to New Zealand's best fibre broadband service (affiliate link). Free setup code: R587125ERQ6VE. Note that to use Quic Broadband you must be comfortable with configuring your own router.
richms
28198 posts

Uber Geek

Trusted
Lifetime subscriber

  #430774 24-Jan-2011 22:26
Send private message

When I suggested the same thing for internet traffic I was laughed at.




Richard rich.ms

MikeSkyrme
272 posts

Ultimate Geek

Trusted

  #430782 24-Jan-2011 22:34
Send private message

I do not understand why you would be laughed at.....
A similar example would be petrol / diesel pumps. The meters used on these are built to a specification and have to be calibrated at regular intervals.




Michael Skyrme - Instrumentation & Controls

gzt

gzt
17160 posts

Uber Geek

Lifetime subscriber

  #430881 25-Jan-2011 09:33
Send private message

MikeSkyrme: Shouldn't fiscal / tariff meters be built to a specification? It would interesting to see the spec that they are manufactured to. Anyone have any ideas where this might be found?

Designed, built, and tested to these standards:

ANSI C12.20-2010

ANSI C12.1-2008

IEC62053-11

IEC62053-21

IEC62053-22

Note: The links go to table-of-contents style previews.




Signature goes here.


gzt

gzt
17160 posts

Uber Geek

Lifetime subscriber

  #430887 25-Jan-2011 09:59
Send private message

And for communication:

[quoting wikipedia:]ANSI C12.18 is an ANSI standard that describes a protocol used for two-way communications with an electricity meter, mostly used in North American markets.The C12.18 standard is written specifically for meter communications via an ANSI Type 2 Optical Port, and specifies lower-level protocol details. ANSI C12.19 specifies the actual data tables.ANSI C12.21 is an extension of C12.18 written for modem instead of optical communications, so is better suited to automatic meter reading.


ANSI C12.18-2006

ANSI C12.19-2008


ANSI C12.21-2006

ANSI C12.22-2008

Again, previews only.





gzt

gzt
17160 posts

Uber Geek

Lifetime subscriber

  #430888 25-Jan-2011 10:05
Send private message

The Elster gRex D also claims compliance with an Australian standard:

NMI M 6* (Metrological and Technical Requirements)

*complete document




Signature goes here.


gzt

gzt
17160 posts

Uber Geek

Lifetime subscriber

  #430926 25-Jan-2011 11:23
Send private message

webwat: I wonder if it has anything to do with the power factor of computers etc and other appliances with AC motors etc that have a certain amount of non-sinewave feedback, as opposed to pure resistive loads. I thought power meters were actually supposed to measure the average power.


With respect to comments already made by [richms] and [Cyril7] about power factor and sampling, your comments could also refer to metering challenges created by harmonics and harmonic distortion generated by switchmode power supplies etc.

Anyone with an IEEE membership or library access like to summarise the metering conclusions from these documents?  :   )

Revenue metering in the presence of distortion and unbalance: myths and reality
Efficiency of active electrical power consumption in the presence of harmonic pollution: a sensitive analysis
Should a utility meter harmonics?







 





savag3
188 posts

Master Geek


  #430991 25-Jan-2011 12:49
Send private message

MikeSkyrme: I do not understand why you would be laughed at.....
A similar example would be petrol / diesel pumps. The meters used on these are built to a specification and have to be calibrated at regular intervals.

Yes its actually a legal requirement for anyone selling goods by weight or measure (Weights and Measures Act)
I can't see how you can justify requiring the scales at the supermarket checkout to be certified but yet there are no requirements for selling data by the gigabyte.

1 | 2 
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.