gregmcc:
A voltage spike is NOT a current spike, two different things, if the voltage is dropping when the current increases then there is a wiring problem.
I never said it was the same thing? I said that a surge when power is restored is not a voltage surge so wont cause damage.
And no there is no wiring problem when the voltage drops on a massive inrush current, its just ohms law and 400+ amps of inrush due to the large number of SMPS and electronically ballasted lamps with totally empty filter caps to fill and minimal power factor correction inductors because they are small loads so dont have to have them fitted.
gregmcc:
Again the switch in the meter box is exactly that, a switch, if 'They' have required you to fit a circuit breaker in there as well the reason is more than likely the pole fuses are under rated for your load, looks like the power company got you to fix their problem at your cost
At the time the pole down the driveway was flagged as "do not climb" and to upgrade the supply from the pathetic 63A one that the people that built the place had put in we would have had to pay to replace the pole at a massive expense. They basically said pay for the next call out for the pole fuse or get a breaker put in so that you can reset it. The 6kw spa pool is gone now and I am down to 3 people in the house so there isnt 4 fan heaters running at the same time over winter anymore so its not an issue. The pole has been replaced for whatever reason at no cost to anyone down the drive way so I can go to 3 phase here if the need arises in the future but I don't foresee that happening.
gregmcc:richms:
The increase in voltage is slower after an external power outage as everyones houses are full of loads that are pulling their inrush surge, so there is a massive voltage drop in the system.
again not correct, there are many rules and regulations to ensure that this should not happen, correct cable sizing for connected loads etc, maximum demand calculations.
The regs have heaps of room for non steady state voltages. A second or so of under voltage is not of any concern to any gear, and most stuff gets tested on a supply that is ramped up even slower than a supply being livened up. Maximum demand calculations is based on steady state currents not the inrush of every single house coming back on line at the same time.
You have a massive amount of capacitance in all the appliances in the house, and that voltage cant go from 0 to 380 instantaneously. Ramp up and inrush is normal and allowed for. Its just when you are a geek with a hell of a lot of stuff the standard breakers tend to trip a little too easily.