Geekzone: technology news, blogs, forums
Guest
Welcome Guest.
You haven't logged in yet. If you don't have an account you can register now.


Ironsfan

13 posts

Geek


#311119 15-Dec-2023 19:20
Send private message

Any help would be most appreciated.

 

Need to run power to a shed that is 35m from house. Now I have come across some 10mm 2core which I think after using my poor google search skills would be ok but not sure. It is tricab 2 x 10mm2 PV1*-Fi98 Pv cable 0.9/1.5kv DC as/nz35033 lszh 120. Hoping I can run this and put an earth rod in at the shed. Hopefully someone out there knows the answer.


Create new topic
tweake
2391 posts

Uber Geek


  #3172179 15-Dec-2023 19:38
Send private message

ask your sparky. as its going to require fuse board board work that home owners are not allowed to do. 




Scott3
3970 posts

Uber Geek

Lifetime subscriber

  #3172189 15-Dec-2023 20:38
Send private message

You can find calculators online. I.e.

https://www.jcalc.net/cable-sizing-calculator-as3008

 

But the required sizing is going to be entirely depending on things you haven't listed, like required current, and conductor material.

Note that the nominal voltage in NZ is 230v.

And that any work inside the switchboard is required by law to be done by a registered electrician, who will need to do the calculation themselves anyway, so you might as well jump to that step.


  #3172190 15-Dec-2023 20:52
Send private message

That's PV cable, and rated for DC usage only. There appears to be a remarkable gap in our standards in that, as best I can see, there is no explicit requirement to have the cable rated for the voltage present on it.

 

It's only two cores. While it is in some circumstances permissible to use a two core cable with a separate earth stake and MEN link, this is only where there are no other conductive services or structures linking the two buildings - no ethernet, no copper water pipes, no metal fences, nothing. Generally, you should expect to use twin and earth (TPS, flat or circular) or two-core neutral screen. You could also use three sets of conduit wire, which would need to be in conduit for the whole length.

 

As single insulated cable, it must be enclosed in conduit for its entire length to provide a second layer of protection. You haven't said whether you intend to run it overhead, underground, or in some other way. Overhead cables have special requirements, underground generally needs conduit unless it's armoured cable or neutral screen in soft soil/sand. 

 

Sizing is another matter altogether; you'll need to determine the expected loading and protection, and the actual cable length between the switchboards, not just the physical distance.

 

 

 

Consult your electrician. 




  #3172198 15-Dec-2023 22:31
Send private message

There is no standard as/nz35033. Tricab means that it is a flexible cable, which is not allowed for fixed wiring.


  #3172199 15-Dec-2023 22:37
Send private message

Heavy duty flexible cable is allowed for use in installations as fixed wiring. The intended purpose of that cable is for fixed PV arrays. 

 

 

 

AS/NZS 5033 sets out the requirements for PV systems. Most likely the leading 3 is a miss-transcribed s.


Ironsfan

13 posts

Geek


  #3172312 16-Dec-2023 11:37
Send private message

 This was to give me some idea whether to buy this cable as it was at a good price. However after reading the reply's I think I'll leave it be.

 

Thank you everyone for your reply's.

 

 


SATTV
1648 posts

Uber Geek

ID Verified

  #3172355 16-Dec-2023 14:55
Send private message

Ironsfan:

 

Any help would be most appreciated.

 

Need to run power to a shed that is 35m from house. Now I have come across some 10mm 2core which I think after using my poor google search skills would be ok but not sure. It is tricab 2 x 10mm2 PV1*-Fi98 Pv cable 0.9/1.5kv DC as/nz35033 lszh 120. Hoping I can run this and put an earth rod in at the shed. Hopefully someone out there knows the answer.

 

 

No, this is not suitable, you can not put in a second earth rod.

 

There can be a potential difference between the earths and cause all sorts of issues.

 

If a separate earth cable was run then that May be suitable be suitable.

 

 

 

A quick google says this is for Photo Voltaic installs, so may not be suitable.

 

John 

 

 





I know enough to be dangerous


 
 
 

Trade NZ and US shares and funds with Sharesies (affiliate link).
  #3172360 16-Dec-2023 15:08
Send private message

SATTV:

 

Ironsfan:

 

Any help would be most appreciated.

 

Need to run power to a shed that is 35m from house. Now I have come across some 10mm 2core which I think after using my poor google search skills would be ok but not sure. It is tricab 2 x 10mm2 PV1*-Fi98 Pv cable 0.9/1.5kv DC as/nz35033 lszh 120. Hoping I can run this and put an earth rod in at the shed. Hopefully someone out there knows the answer.

 

 

No, this is not suitable, you can not put in a second earth rod.

 

There can be a potential difference between the earths and cause all sorts of issues.

 

If a separate earth cable was run then that May be suitable be suitable.

 

 

 

A quick google says this is for Photo Voltaic installs, so may not be suitable.

 

John 

 

 

 

 

Don't quote me on the latest rules, but previously you certainly could run a 2 wire sub-main and drive a separate earth rod.


  #3172533 16-Dec-2023 21:37
Send private message

Yeah, outbuildings clause, 5.5.3.1 (b) Separate MEN installation.

 

NOTE: Particular care is required where conductive pipes and such items as
telecommunication cable sheaths, covered walkways, etc may be continuous
between separate buildings and thus establish a parallel earth/neutral path.

 

Falls in the not recommended category, and there were suggestions that it wouldn't be OK to put e.g. EV chargers on them. Also, as it involves work on a main earthing system, it would arguably be subject to inspection.

 

 

 

Better to use 2C+E TPS or 2C NS, e.g.

 

 

 

https://express.ecsnz.com/en/lapp-8100679-olflex-power-ns-neutral-screen-cable-2x10

 

https://express.ecsnz.com/en/lapp-8100673-olflex-power-ns-neutral-screen-cable-2x6

 

https://express.ecsnz.com/en/lapp-3803844a-black-circular-tps-xple-3g10

 

 


Daynger
435 posts

Ultimate Geek


  #3172679 17-Dec-2023 14:21
Send private message

tweake:

 

ask your sparky. as its going to require fuse board board work that home owners are not allowed to do. 

 

 

 

 

No, he should ask the Inspector that will be signing off the work any questions.

 

All homeowner work MUST be inspected by an electrical inspector who will do the connections at any switchboard as homeowners are not allowed to do any work on switchboards.

 

ECP51.


  #3172766 17-Dec-2023 16:44
Send private message

Yes, certain work done under homeowner exemptions including IIRC any new cable must be inspected by an inspector, not just an electrician

 

However, some inspectors do not want to do actual electrical work for insurance/other reasons, so it's possible the homeowner would do some parts, an electrician would connect it, and an inspector would inspect it.

 

I think we were largely assuming that OP would supply the cable, and an electrician would do the rest, bypassing the requirement for an actual inspector unless a main earthing system was involved. 


raytaylor
4017 posts

Uber Geek

Trusted

  #3173529 19-Dec-2023 22:32
Send private message

I regularly ask my electrician this question. 
We do work on secondary buildings with radio antennas and have to bond the antennas and mast both to a nearby earth rod at the secondary building, as well as to the electrical earth. 

I get it explained to me each time by the electrician and I think i have remembered now... its okay as long as we have used TPS cable between the buildings and the neutral is only bonded to earth in the main fuse board, and not the remote fuse board. 

Then the earth wire in the TPS cable (so 2 core wont work without an earth wire, hence TPS) is used to bond the two earth rods together so there isnt any potential earth voltage difference. 

By only having neutral bonded to earth at the main fuse board, it stops the earth wire between the buildings from carrying current except in a fault condition where it causes (and encourages) the RCD to trip. 

 

 

 

So yes to OP - you should just be using TPS cable and nothing else - unless its high current or three phase then talk to your electrician about options for neutral screen cable and the implications that creates. 





Ray Taylor

There is no place like localhost

Spreadsheet for Comparing Electricity Plans Here


  #3173534 19-Dec-2023 22:58
Send private message

Neutral screen doesn't really change anything; it's just a more robust cable. It's still available with between two and five conductors, but the colour codes change a bit - two core NS will have red & white or red & blue inner cores, plus the unmarked screen that you would terminate and mark as an earth at both ends, and mark the second conductor (white or blue) as a black neutral. 


Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.