#312671 7-May-2024 08:28
Send private message

Hi all,

 

Calling all electricians....
the kitchen is getting renovated and it got to the stage of the cooktop replacement.
the new cooktop is 6000W.
and from what I can see there is a circuit breaker with a label "Merlin Gerin Multi9 D60 C32 - 240/415 4500"
The current cooktop is 5000W and always worked fine.
from what I can see the oven is using the same circuit breaker as well.

 

in my view the circuit breaker needs to be replaced as 4500W is below of the current and new cooktop W.
Builder who is doing the renovation said that his electrician confirmed that there is no need to upgrade the wiring or circuit breaker.

 

can i have second opinions please?
I don't want to engage another electrician at this stage but if it is needed I will.

 

 

thank you for your help.


View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2
thewabbit
127 posts

Master Geek

ID Verified

  #3227242 7-May-2024 08:35
Send private message

Not an electrician, but I understand that circuit breakers are there to protect the wiring, not the appliance. IE, stop the wires in your wall from heating up and causing a fire. If the circuit breaker needs upgrading, it likely means the the wiring will also need upgrading and therefore isn't suitable for a 6kw appliance.

In other words, if you don't trust your builders sparky, get your own to give an opinion. 




  #3227251 7-May-2024 09:01
Send private message

Can't comment on the specifics in your case but I recently had a new induction cooktop installed and the Sparky ran a new circuit breaker from the distribution panel and all new dedicated wiring to the new cooktop. The previous ceramic cooktop and wall oven were on the same breaker and wiring. 

 

For 6,000W I would want dedicated wiring and breaker just for that appliance. I expect your builder is relying on you never needing to run all burners at maximum simultaneously.


samgdan

160 posts

Master Geek


  #3227252 7-May-2024 09:06
Send private message

that was my expectation as well, having everything on (cooktop and stove) in my opinion it will need a wiring or circuit breaker upgrade or run some dedicated wires for the cooktop.

 

yes most likely we wont have everything on at the same time, however it is a possibility that we need to consider.




jonathan18
7413 posts

Uber Geek

ID Verified
Trusted

  #3227266 7-May-2024 09:47
Send private message

Yeah, this is the reason why we’ve decided to stick with a reticulated gas hob with our new kitchen, whereas we’d have otherwise chosen to switch to an induction hob - not only would we would needed to have new wiring (from one end of the house to the other) run back to the distribution board, we’ve also run out of space in the distribution board for a new circuit breaker so a new board would have been required. Would have been one expensive change-over…

Spyware
3762 posts

Uber Geek

Lifetime subscriber

  #3227280 7-May-2024 11:02
Send private message

C32 is 32A or 7.2 kW. 4500 is the rated breaking capacity in amps.

 

Note: Not an electrician.





Spark Max Fibre using Mikrotik CCR1009-8G-1S-1S+, CRS125-24G-1S, Unifi UAP, U6-Pro, UAP-AC-M-Pro, Apple TV 4K (2022), Apple TV 4K (2017), iPad Air 1st gen, iPad Air 4th gen, iPhone 13, SkyNZ3151 (the white box). If it doesn't move then it's data cabled.


samgdan

160 posts

Master Geek


  #3227286 7-May-2024 11:23
Send private message

I have used multiple calculators online and it seems that the Builder electrician is right. 

 

 

 

 

 


  #3227311 7-May-2024 13:10
Send private message

And if your using the Oven and Cooktop at the same time?


 
 
 

Move to New Zealand's best fibre broadband service (affiliate link). Note that to use Quic Broadband you must be comfortable with configuring your own router.
johno1234
2805 posts

Uber Geek


  #3227319 7-May-2024 13:33
Send private message

Senecio:

 

And if your using the Oven and Cooktop at the same time?

 

 

It would pop the breaker so no big deal?

 

We used to have a freestanding 90cm range with 4 place induction cooktop. It had a potential current drain that would keep the Huntly power station online but was on the original range's wiring. Never once did pop the breaker as we never had cause to put all the elements on maximum plus oven heating up. And we cook a lot.

 

 


timmmay
20580 posts

Uber Geek

Trusted
Lifetime subscriber

  #3227390 7-May-2024 15:50
Send private message

The oven with induction hob we got about 5 years ago was rated higher than our circuit breaker. My neighbor who's an electrician had a practical opinion: if the breaker ever blows let me know and we'll look at what we need to fix. Since the breaker is protecting the wiring at the existing level and we've never tripped the breaker I guess it's fine. If I was putting in a new one that was much higher current I might look at it though.


mkissin
389 posts

Ultimate Geek

ID Verified

  #3227396 7-May-2024 16:11
Send private message

Circuit breakers have a time component to them. That one is a 32A breaker with a C characteristic curve.

 

That means it'll give you a 100% over-rate for a full minute before it's guaranteed to pop. That ends up being 15kW for a full minute, which is an alarming amount of energy (enough to raise 2 liters of water from frozen to a full boil).


Daynger
435 posts

Ultimate Geek


  #3227483 7-May-2024 19:14
Send private message

6000W is only 26.whatever Amps.

 

Circuit breaker is fine, the 4500 is the PSSC rating, not the wattage of what itll run.

 

Im an electrician.


samgdan

160 posts

Master Geek


  #3227562 8-May-2024 08:30
Send private message

good morning everyone,

 

thank you for all the replies it seems that the builder electrician is correct. I will let them proceed with the work and see is any issues arise.

 

cheers.


Zeon
3916 posts

Uber Geek

Trusted

  #3227876 8-May-2024 12:45
Send private message

Even if it were insufficient whats the chance you have all elements on full power and the oven going at the same time? If the breaker trips in the future do something about it at that time?

 

The size of the breaker that can be installed will depend on the cross section of the wire in the wall. If its 6mm2 then its a matter of just changing the breaker should it be a problem - 5 minute job.





Speedtest 2019-10-14


Daynger
435 posts

Ultimate Geek


  #3228060 8-May-2024 19:32
Send private message

Zeon:

 

Even if it were insufficient whats the chance you have all elements on full power and the oven going at the same time? If the breaker trips in the future do something about it at that time?

 

The size of the breaker that can be installed will depend on the cross section of the wire in the wall. If its 6mm2 then its a matter of just changing the breaker should it be a problem - 5 minute job.

 

 

 

 

You wont be changing the breaker to a bigger on on 6mm2.


Zeon
3916 posts

Uber Geek

Trusted

  #3228241 9-May-2024 10:20
Send private message

Daynger:

 

Zeon:

 

Even if it were insufficient whats the chance you have all elements on full power and the oven going at the same time? If the breaker trips in the future do something about it at that time?

 

The size of the breaker that can be installed will depend on the cross section of the wire in the wall. If its 6mm2 then its a matter of just changing the breaker should it be a problem - 5 minute job.

 

 

 

 

You wont be changing the breaker to a bigger on on 6mm2.

 

 

6mm2 is allowed for up to 40A in NZ:
https://www.level.org.nz/energy/electrical-design/wiring/wiring-materials/





Speedtest 2019-10-14


 1 | 2
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.