Bung:gregmcc:Bung: The only thing typically 10A is the cheap breaker built into plug strips. The fuse or breaker rating is determined by the .cable and its surroundings. Short term current higher than nominal probably wouldn't trip either. In an office if you ever manage to trip the breaker it's surprising sometimes how many other computers are affected.
I think you need to re-read what you said here, the fuse or breaker rating IS NOT determined by the cable and it's surrroundings, you need to go and take a look at a circuit breaker and read the number on it, a 10A circuit breaker has a rating of 10 amps.
Step back a bit. How does the rating of the protection get chosen? Do you see 1 socket and put in a 10 amp breaker or do you look at the appropriate breaker for the size of cable and how surrounded in insulation it will be?
]
Strictly speaking the circuit breaker is chosen to protect the cable, so a 2.5mm cable could have a 20-25A breaker on it even though the socket outlets are rated for 10A.
You should never try and draw more than 10A from a 10A rated plug/socket, doing this over an extended period can cause overheating and a fire.