Happy to answer any questions, I installed my underfloor system myself and just got a plummer to hook up the heat pump.
Mike
SumnerBoy: FYI - this is the heatpump I have (http://www.waterheating.co.nz/Products/Residential/Underfloor+Heating/7GUb9-1/). It is 9kW and has an onboard circulating pump and buffer tank which means you just hook the flow/return pipes to your underfloor manifold and turn it on. My house is 260sqm, two story (including a 48sqm garage which I don't heat). The ground floor foot print is about 150sqm (excl. garage) and this 9kW unit works great - remembering I only run it from 9pm till 7am. In the middle of winter it runs full time during that period, but for example at the moment it turns on at 9pm and usually flicks off again about 2-3am.
MikeAqua: Have you considered a ground to water heat pump?
Efficient and the capital outlay maybe justified by the longer heating season in Dunedin.
SumnerBoy: FYI - this is the heatpump I have (http://www.waterheating.co.nz/Products/Residential/Underfloor+Heating/7GUb9-1/). It is 9kW and has an onboard circulating pump and buffer tank which means you just hook the flow/return pipes to your underfloor manifold and turn it on. My house is 260sqm, two story (including a 48sqm garage which I don't heat). The ground floor foot print is about 150sqm (excl. garage) and this 9kW unit works great - remembering I only run it from 9pm till 7am. In the middle of winter it runs full time during that period, but for example at the moment it turns on at 9pm and usually flicks off again about 2-3am.
The concrete slab should have a thermal break and perimeter insulation along the edge. 80% of concrete heat loss is from the edge.
Windows and doors should be thermally broken if they're aluminium. The standard R2.2 and R3.2 insulation in the walls and ceiling is too low but it's normal for over 50% of heat loss in a new house to be through the windows because of poor quality products an excessive glass area.
Many people have had problems with ducted heat pumps because they are difficult to install and as so few are installed in New Zealand the installers may not know what they're doing.
Many underfloor hydronic systems in New Zealand have been installed directly into the concrete slab so the slab itself must be heated. There are systems where you can have the pipes installed over the slab inside a plastic interlayer that goes over the concrete and under the floor. As that isn't directly heating the concrete it may be more responsive. Central heating can be set up to have different parts of the house as separate zones.
The Hot Water Heat Pumps company does a range that can supply hot water for both central heating and general usage. The Daikin Altherma can be set up to provide the house's hot water and summer cooling too. The Altherma is probably more efficient but it should have a higher price tag.
Dunedin doesn't have very cold temperatures but they won't work as efficiently at 0 degrees as at 7.
Hydronic heat pumps can be set up to work with radiator central heating too if you don't want underfloor heating. Underfloor provides the most even heating as heat rises.
Ground source heat pumps are more suitable in places with geothermally warmed earth or large seasonal differences. As the underground temperature stays stable across the year it allows a heat pump to work well when the air is too cold for air source heat pumps to work efficiently. They may make sense in places like parts of Central Otago and Rotorua but I doubt the economics add up for them in any coastal area.
|
![]() ![]() ![]() |