Bung: It's another on/off functional switch. If it can't be locked against inadvertent operation it's not an isolating switch. The circuit breaker would be the isolation point.

 

 

 

an isolator switch isn't defined as if it's lockable or not, it's the separation between electrical contacts in it's off position.

 

 

 

Isolators aren't required on GPO sockets 32A or less, a fixed wired bathroom heater does need an isolator as a point of isolation is needed for a fixed wired appliance.

 

 

 

Some circuit breakers don't meet the "isolation" standard as the contact distance in the off position doesn't meet the distance requirements




Bung
6479 posts

Uber Geek

Subscriber

  #1699069 5-Jan-2017 21:06
Send private message

Greg is right that contact gap also comes into it but an isolator is more than a simple switch. The last thing you want to do is just switch the lights off for example before working on the fitting then have someone walk in and switch the lights on.

geekIT

2419 posts

Uber Geek


  #1699211 6-Jan-2017 09:31
Send private message

 Gregmcc and Bung: Thanks for the clarification. So, to get back to my original question, is the 10 amp light switch that's alongside the wall heater in my nephew's bathroom, a proper setup? Not quite sure how high it is but I had to stretch to reach it. And it definitely renders the heater inoperable.





'Those who can make you believe absurdities can make you commit atrocities.' Voltaire

 

'A patriot must always be ready to defend his country against his government.' Edward Abbey

 

 

 

 

 

 




Goosey
2829 posts

Uber Geek

Subscriber

  #1699260 6-Jan-2017 10:51
Send private message

geekIT:

 

 Gregmcc and Bung: Thanks for the clarification. So, to get back to my original question, is the 10 amp light switch that's alongside the wall heater in my nephew's bathroom, a proper setup? Not quite sure how high it is but I had to stretch to reach it. And it definitely renders the heater inoperable.

 

 

 

 

You did say there was a pull cord right?

 

 


geekIT

2419 posts

Uber Geek


  #1699286 6-Jan-2017 11:59
Send private message

Yes, goosey. There's a built-in pull-cord.





'Those who can make you believe absurdities can make you commit atrocities.' Voltaire

 

'A patriot must always be ready to defend his country against his government.' Edward Abbey

 

 

 

 

 

 


Goosey
2829 posts

Uber Geek

Subscriber

  #1699300 6-Jan-2017 12:18
Send private message

geekIT:

 

Yes, goosey. There's a built-in pull-cord.

 

 

 

 

Isnt that all you need then. If you wanted to 'isolate' live supply then reach up and flick the switch off. 

 

This is how all my bathroom heaters have worked in places I have lived. 

 

 

 

 


geekIT

2419 posts

Uber Geek


  #1699499 6-Jan-2017 17:59
Send private message

But...

 

No, I'd better not say anything in case I'm accused of being 'abrasive'.





'Those who can make you believe absurdities can make you commit atrocities.' Voltaire

 

'A patriot must always be ready to defend his country against his government.' Edward Abbey

 

 

 

 

 

 


 
 
 

Move to New Zealand's best fibre broadband service (affiliate link). Note that to use Quic Broadband you must be comfortable with configuring your own router.
  #1699557 6-Jan-2017 20:12
Send private message

In my opinion a 10A rated isolation switch is not suitsble for a 10A load. It should be at least rated at 15A. In time a 10A switch will fail.

  #1699587 6-Jan-2017 20:43
Send private message

larknz: In my opinion a 10A rated isolation switch is not suitsble for a 10A load. It should be at least rated at 15A. In time a 10A switch will fail.

 

really? im pretty sure the standard says they must be tested and capable of sustaining x% more than their rating for x time to be able to put the rating on it (i dont have the standard in front of me)

 

most if not all multi boards are only rated to 10A and people plug 2.4kw heaters into them all the time with no issues.


lxsw20
3552 posts

Uber Geek

Subscriber

  #1699609 6-Jan-2017 21:43
Send private message

I know of at least one decent commercial fire from plugging a heater into a cheap multi board. Certainly not recommended. 


richms
28172 posts

Uber Geek

Trusted
Lifetime subscriber

  #1699612 6-Jan-2017 21:53
Send private message

lxsw20:

 

I know of at least one decent commercial fire from plugging a heater into a cheap multi board. Certainly not recommended. 

 

 

I think that is more a result of the terrible quality of cheap powerstrips. Like this one.

 

 

I was at bunnings once and someone was returning an equally bad looking one because it tripped out when they used the kettle and the microwave and it was useless if it cant run 2 things and why put four sockets on it when it cant even run 2 things. Some people no clue.

 

 





Richard rich.ms

  #1699613 6-Jan-2017 21:54
Send private message

I have seen many instances where a 10A switch has failed because of overheating. A 10A switch is cheaper than a 15A or 20A switch, so some sparkies will use them to save money.

1 | 2 
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.