Obraik:
It mostly followed the plans, the only difference is that the ERVs return vent is in the hallway rather than the kitchen/dining area as it is on the above plan.
The evening and this morning were much improved after changing it to use the controllers sensor yesterday afternoon. I set it to 22 overnight this time and when we got up this morning the controller was showing the room was 21 - no hoody or socks required this time. I also changed the fan behaviour for cooling mode - it was set to run the fan at the set speed when it wasn't actively cooling so I've set it to the setting that puts it into low-low mode. The fan for heating mode was set to turn off when it wasn't actively heating, so I didn't need to adjust that.
good to see you got the temp problem sorted. however that and other things tells me this was never setup properly in the first place.
the big problem is that you need to have the hvac fan running all the time for the ERV to work properly. the hvac is what distributes the air. with the hvac off the ventilation air is going to come out of the hvac return vents, and probably blow a bit of dust off the filters back into the air. especially as the ERV return is in the same space. ie the ventilation air will go down the hvac return to the ERV return and not mix with the house air effectively doing nothing. so you need to set it so fan runs all the time. the other option is to put one ways or dampers on the returns so if the hvac is off they shut and ventilation air is forced through the hvac piping, but remember that it will take the easy route so it won't be well distributed. another crude way is to put the vent supply in the hallway, so ventilation air goes into the hallway and is picked up by the hvac returns. when hvac is not running it then distributes by the hallway, which is not great.
disappointing to see the ERV outlet and inlet so close to each other. should really be a lot further apart.
does the ERV have a separate air filter? common trick is for them to use the built in filter which is only there to protect the core not clean the air. plus that filter may be hard to find in years to come. far better to have a standard sized filter placed before it so it does the air cleaning. also looks like its a long way from the access hatch so you will have fun changing filters. might be a good idea to move the ERV intake down to the garage and have a separate filter mounted by the access hatch.
no mention on returns from each room.
how is the bathroom ventilation done? its pretty common to use the ERV as the bath room vents. otherwise you need to factor in make up air for the bath fans as well as the range hood. hows that been done?
the kitchen hvac vent should have been further away. by placing it so close to the rangehood it reduces the effectiveness of the range hood (assuming ceiling vent). the best is a floor vent so replacement air comes up from underneath.