tweake:
you need a fan for the ventilation. just putting a duct to the return won't do anything. a simple cheap ventilation system kit would work ok. hook that up to the return or vent next to the return (which is easier to get to work when heating is off).
you can't just put a damper in that will block off the return and feed in outside air. that can cause damage to your house as it will pressurize the living hell out of the house.
@tweake - perhaps I wasn't clear enough, I wasn't meaning 'just put a duct'.
The damper was going to go in between the return intake and the brivis unit (which has the fan inside), so the brivis unit will suck air from which ever intake duct is open (either return vent in house, or external intake)
So:
Damper in position 1 (normal): duct between inside return vent and brivis unit is OPEN, and duct to outside is CLOSED, meaning brivis unit sucks in air from inside the house, and recirculate back around house
Damper in position 2: duct between return vent and brivis unit is CLOSED, duct to outside is OPEN, brivis unit when running in fan mode will suck air from outside and then push around the house
Isn't that essentially what a summer air system does on any other heat trans / ventilation type system?