timmmay:
The single RCD thing was just my assumption based on knowing nothing.
@snnet what's the difference between an RCCB and RCBO? A quick google suggests RCCB is a residual current device but doesn't have overload protection (circuit breaker) whereas the RCBO has both RCD and a circuit breaker built in. An RCBO sounds better to me. Also sounds like an RCB with three separate circuit breakers (MCBs) after it would do a similar job?
Not sure if this is relevant, but we use Electric Kiwi and have a free hour of power a day so for an hour a day we put a lot of current through. Two big heat pumps, a fan heather, clothes drier, dish washer, hot water cylinder, maybe 50A.
My two quotes are:
- $2700 company: Flush mount switchboard (PDL), upgrade to include MCBs and Vynco RCBOs and keep existing time clocks in their current configuration.
- $1400 company: A new recessed distribution board will be installed (Vynco), complete with main switch, Vynco RCCB safety switches and MCB’s. Connection of all sub-circuits to new sub circuit protective devices.
The price difference is not as important to us as quality and longevity. Any thoughts?
Correct, an RCCB does not have overload protection - it only has residual current protection so a circuit breaker is required (in this case) for each circuit downstream from it. Having one double pole RCCB and three single pole circuit breakers after it will do the exact same job as a single RCBO, the only thing is the "nuisance tripping" factor meaning if one of those circuits has a residual current fault, you lose all three circuits while that RCCB is tripped - however - this is the standard normal installation method in NZ and you normally wouldn't expect to have a fault condition.
Some things can cause an RCBO/RCCB to trip like kettles that have a detachable base (sometimes moisture builds in the contacts on the base causing the RCCB/RCBO to operate, have seen similar with toasters, exterior lights filling with water....etc) -- just saying this so you're aware
An RCBO is typically a single pole (RCCBs take up two poles) and it is a combined RCD and breaker in one. They are useful for things that you don't want to be part of a common RCCB set for example, I use one for the communications cabinet in a retirement village I am undertaking at the moment - In each separate dwelling, I don't want other things to cause the cabinet to power down as it houses the nurse call systems etc for that dwelling, so I have it totally separate, but still protected.
$1400 is closer to what I would expect the cost to be for a switchboard upgrade as you have described, assuming there are no cables that need completely replacing etc.
Since the installation will still contain MCBs for things like oven, hob, hot water, heat pumps (things that are not required to be RCD protected and in fact are likely to trip an RCD) so I think the first quote you have is for RCBOs - individual RCDs/Breakers
Quality and longevity - between RCBOs and RCCBs, there really isn't much difference. I wouldn't expect you to experience constant faults - it's not normal. If you have things that you'd prefer did not lose power in the event of a separate circuit activating the RCCB, you could discuss having that particular circuit on an RCBO instead (like what I mentioned above about my job with comms cabinets)
Though I will mention again -- I'm pretty sure the contractor in the cheaper quote could use a better brand for the same price (my wholesaler will sell vynco and schneider to me at the same rate -- and it's based on the "cheaper" vynco pricing, they alter other brands for me), for reasons I'd mentioned in earlier posts. It doesn't happen on every board but it happens and can be annoying having to turn breakers off and back on to get the power back to circuits
Hopefully that helps - and I haven't thrown a spanner in the works!