fe31nz
1232 posts

Uber Geek


  #3019360 10-Jan-2023 00:25
Send private message

The reason is simple - the heat pump only reads the air temperature at its intake.  In high wall units, that intake is on the top of the heat pump, so it is reading the air temperature quite high up in the room.  Hot air rises, so the temperature at the top of the room is always significantly hotter than lower down.  The humans in the room, unfortunately, are normally rather lower down than the intake air temperature sensor.  So the heat pump never has an actual room temperature to work from.  What most manufacturers do is to subtract an arbitrary number from the intake temperature reading and use that as the guessed real room temperature at human level.  There is no way to adjust that arbitrary number for the room which the heat pump is installed in, or its position in the room.  There is no option to do calibration.  So you just have to set the heat pump setpoint temperatures to whatever works to produce the desired temperature at human level.  For example, our big Panasonic heat pump in the kitchen needs to be set to 19 if we want about 22 on heating, and to 23 if we want 24 on cooling.  Things are further complicated by the flow of heat in and out of the room.  For example, if we are heating in winter before the sun starts to shine in through the windows, we may need to set it to 20 to get 22, but when the sun is shining, 19 works.  This seems to be a result of how the airflow works in the room to distribute the heat, and what the heat gradient is from ceiling down to the floor.  If you really want the setpoint to mean what it says, you need to use a temperature sensor away from the heat pump at human level and unaffected by the airflow.  And it will need to be calibrated for the room.  And recalibrate it if you rearrange the room in a way that affects the airflow.  I do wish that heat pump manuals actually mentioned this problem!

 

So to emphasise the basic point here, the setpoint numbers on a heat pump are not calibrated - they do not match real temperatures.  You just use whatever setting works.




timmmay

20581 posts

Uber Geek

Trusted
Lifetime subscriber

  #3019371 10-Jan-2023 07:15
Send private message

fe31nz:

 

The reason is simple - the heat pump only reads the air temperature at its intake.  In high wall units, that intake is on the top of the heat pump, so it is reading the air temperature quite high up in the room.  Hot air rises, so the temperature at the top of the room is always significantly hotter than lower down.  The humans in the room, unfortunately, are normally rather lower down than the intake air temperature sensor.  So the heat pump never has an actual room temperature to work from.  What most manufacturers do is to subtract an arbitrary number from the intake temperature reading and use that as the guessed real room temperature at human level.  There is no way to adjust that arbitrary number for the room which the heat pump is installed in, or its position in the room.  There is no option to do calibration.  So you just have to set the heat pump setpoint temperatures to whatever works to produce the desired temperature at human level.  For example, our big Panasonic heat pump in the kitchen needs to be set to 19 if we want about 22 on heating, and to 23 if we want 24 on cooling.  Things are further complicated by the flow of heat in and out of the room.  For example, if we are heating in winter before the sun starts to shine in through the windows, we may need to set it to 20 to get 22, but when the sun is shining, 19 works.  This seems to be a result of how the airflow works in the room to distribute the heat, and what the heat gradient is from ceiling down to the floor.  If you really want the setpoint to mean what it says, you need to use a temperature sensor away from the heat pump at human level and unaffected by the airflow.  And it will need to be calibrated for the room.  And recalibrate it if you rearrange the room in a way that affects the airflow.  I do wish that heat pump manuals actually mentioned this problem!

 

So to emphasise the basic point here, the setpoint numbers on a heat pump are not calibrated - they do not match real temperatures.  You just use whatever setting works.

 

 

That makes sense. I can see the temperature inside the Daikin and in the room, the Daikin is usually 2-3 degrees warmer, for the reason you said which is heat effectively rises. The manufacturer differential makes sense as well, as this is a smaller room, ceiling not quite as high and is sloped. Setting to what works is probably the only practical option. Thanks for the interesting analysis :)


timmmay

20581 posts

Uber Geek

Trusted
Lifetime subscriber

  #3019372 10-Jan-2023 07:18
Send private message

Here's why I don't use auto mode.

 

  • I initially had the unit in heat mode 21 degrees started by automation, it was idle. The room temperature was 21.5 degrees, the heat pump temperature was 23 degrees.
  • I thought I'd try auto mode as suggested.
  • As soon as I hit auto, for some reason the unit decided it needed to cool the room, and went into cooling mode. When it did that it changed to the last preset temperature for auto, which was 20 degrees.
  • I then noticed it was getting colder and changed it back to heat mode

It might work better if I started it out in auto mode. I'll change my automation and see what happens tomorrow.

 

 

 

 

 




insane
3240 posts

Uber Geek

ID Verified
Trusted

  #3019419 10-Jan-2023 09:21
Send private message

Does Daikin not have a service menu like this Panasonic?

Offers some temp offset settings and some limits too.



There's another section that shows what the expected resistance output of the temperature sensors is at various temperatures. Presumably you could 'tweak' it by physically adding another resistor if you're off by a little.


timmmay

20581 posts

Uber Geek

Trusted
Lifetime subscriber

  #3019428 10-Jan-2023 09:47
Send private message

insane: Does Daikin not have a service menu like this Panasonic?

Offers some temp offset settings and some limits too.

 

I'm not aware of that being available, but if it is I'd like to have a look.


tweake
2391 posts

Uber Geek


  #3019681 10-Jan-2023 16:37
Send private message

timmmay:

 

 

 

It's not overshooting. The fan can be completely off, set to heat mode 22, the room is 24 degrees, and it will start off and heat the room. It's not just blowing air about. It's not overshooting if it starts up explicitly. The unit is sized about right for the room. Thanks for the thought though.

 

 

if its heating above the setpoint, thats overshoot. like wise with cooling, if it cools down past set point that over shoot. regardless of if it starts higher or not.

 

 


tweake
2391 posts

Uber Geek


  #3019684 10-Jan-2023 16:44
Send private message

fe31nz:

 

The reason is simple - the heat pump only reads the air temperature at its intake.  In high wall units, that intake is on the top of the heat pump, so it is reading the air temperature quite high up in the room.  Hot air rises, so the temperature at the top of the room is always significantly hotter than lower down.  The humans in the room, unfortunately, are normally rather lower down than the intake air temperature sensor.  So the heat pump never has an actual room temperature to work from.  What most manufacturers do is to subtract an arbitrary number from the intake temperature reading and use that as the guessed real room temperature at human level.  There is no way to adjust that arbitrary number for the room which the heat pump is installed in, or its position in the room.  There is no option to do calibration.  So you just have to set the heat pump setpoint temperatures to whatever works to produce the desired temperature at human level.  For example, our big Panasonic heat pump in the kitchen needs to be set to 19 if we want about 22 on heating, and to 23 if we want 24 on cooling.  Things are further complicated by the flow of heat in and out of the room.  For example, if we are heating in winter before the sun starts to shine in through the windows, we may need to set it to 20 to get 22, but when the sun is shining, 19 works.  This seems to be a result of how the airflow works in the room to distribute the heat, and what the heat gradient is from ceiling down to the floor.  If you really want the setpoint to mean what it says, you need to use a temperature sensor away from the heat pump at human level and unaffected by the airflow.  And it will need to be calibrated for the room.  And recalibrate it if you rearrange the room in a way that affects the airflow.  I do wish that heat pump manuals actually mentioned this problem!

 

So to emphasise the basic point here, the setpoint numbers on a heat pump are not calibrated - they do not match real temperatures.  You just use whatever setting works.

 

 

back to what i mentioned before, high walls are meant to be installed at a certain height no doubt thats the height the sensor is calibrated for. what i noticed with mine that in the instructions that came with it, the required height is higher than what the wall is. that may trick the unit into making the room hotter.

 

odds are our heat pumps are designed for a different market.

 

i was originally looking at getting a wall controller. i wonder if that would fix the issue because the wall controller has its own temp sensor and they are required to be installed at a certain height.


 
 
 

Move to New Zealand's best fibre broadband service (affiliate link). Free setup code: R587125ERQ6VE. Note that to use Quic Broadband you must be comfortable with configuring your own router.
Stu1
1769 posts

Uber Geek

ID Verified
Subscriber

  #3019853 11-Jan-2023 09:26
Send private message

fe31nz:

 

The reason is simple - the heat pump only reads the air temperature at its intake.  In high wall units, that intake is on the top of the heat pump, so it is reading the air temperature quite high up in the room.  Hot air rises, so the temperature at the top of the room is always significantly hotter than lower down.  The humans in the room, unfortunately, are normally rather lower down than the intake air temperature sensor.  So the heat pump never has an actual room temperature to work from.  What most manufacturers do is to subtract an arbitrary number from the intake temperature reading and use that as the guessed real room temperature at human level.  There is no way to adjust that arbitrary number for the room which the heat pump is installed in, or its position in the room.  There is no option to do calibration.  So you just have to set the heat pump setpoint temperatures to whatever works to produce the desired temperature at human level.  For example, our big Panasonic heat pump in the kitchen needs to be set to 19 if we want about 22 on heating, and to 23 if we want 24 on cooling.  Things are further complicated by the flow of heat in and out of the room.  For example, if we are heating in winter before the sun starts to shine in through the windows, we may need to set it to 20 to get 22, but when the sun is shining, 19 works.  This seems to be a result of how the airflow works in the room to distribute the heat, and what the heat gradient is from ceiling down to the floor.  If you really want the setpoint to mean what it says, you need to use a temperature sensor away from the heat pump at human level and unaffected by the airflow.  And it will need to be calibrated for the room.  And recalibrate it if you rearrange the room in a way that affects the airflow.  I do wish that heat pump manuals actually mentioned this problem!

 

 

 

So to emphasise the basic point here, the setpoint numbers on a heat pump are not calibrated - they do not match real temperatures.  You just use whatever setting works.

 



Dumb question If I set my daiken on heat at 21degrees will the fan slow down and stop at that temp? I did a test gave up after 90 minutes it was still going and hadn’t reached the temp. The daiken techs seemed to think that’s normal . My central heating stops when it reach’s 21 but my heat pump won’t?


  #3019856 11-Jan-2023 09:33
Send private message

is the fan on auto too?

 

i would have thought if it was on a fixed speed then the fan would keep going, the unit would just ramp down its heating/cooling output till it turned off at the set temp. The fan would keep running.

 

In auto (Fan speed) the fan would slow down to its slowest speed. as it still needs to be bringing air into the unit to be monitoring the temp.


timmmay

20581 posts

Uber Geek

Trusted
Lifetime subscriber

  #3019862 11-Jan-2023 09:45
Send private message

Jase2985:

 

is the fan on auto too?

 

i would have thought if it was on a fixed speed then the fan would keep going, the unit would just ramp down its heating/cooling output till it turned off at the set temp. The fan would keep running.

 

In auto (Fan speed) the fan would slow down to its slowest speed. as it still needs to be bringing air into the unit to be monitoring the temp.

 

 

The fan behavior changes depending on mode:

 

  • Cool: fan runs all the time
  • Heat: fan runs until up to heat, then it occasionally spins up on a very low speed to check the temperature in the room
  • Auto: fan seems to only run when required, including on cool

I tend to use a fixed fan speed in both modes, as the unit on auto selects a very low fan speed. I want the fan speed higher to push the air out through the room, and to mix the air up a bit so the heat gets down to the floor level.


insane
3240 posts

Uber Geek

ID Verified
Trusted

  #3019875 11-Jan-2023 10:18
Send private message

timmmay:

 

....

 

I tend to use a fixed fan speed in both modes, as the unit on auto selects a very low fan speed. I want the fan speed higher to push the air out through the room, and to mix the air up a bit so the heat gets down to the floor level.

 

 


Well that explains a lot, you need to leave the fan on auto or it's going to keep pulling residual heat from the coil/heat exchanger.

 


Do you have a "powerful" option that you can use in conjunction with the auto fan speed? 

 

 


  #3019881 11-Jan-2023 10:24
Send private message

even on the lowest fan speed it will still mix the air in the room, all be it a little slower.


timmmay

20581 posts

Uber Geek

Trusted
Lifetime subscriber

  #3019892 11-Jan-2023 10:34
Send private message

insane:

 

Well that explains a lot, you need to leave the fan on auto or it's going to keep pulling residual heat from the coil/heat exchanger.

 

Do you have a "powerful" option that you can use in conjunction with the auto fan speed? 

 

 

I don't understand how you came to that conclusion. My understand of fan speed is simply that when the system is in heat / cool mode that's the fan speed to use. The fan turns off when the unit is up to heat, just like auto mode.

 

I use a higher fan speed because I often see the temperature at the Daikin is say 24 degrees, but the temperature at my desk is 22 - 23 degrees. The higher fan speed pushes the air harder and reduces stratification.


insane
3240 posts

Uber Geek

ID Verified
Trusted

  #3019894 11-Jan-2023 10:45
Send private message

@Timmmay - My Panasonic and Mitsubishi units fans seem to keep running if I manually set a fan speed. As best I understand the compressor then throttles / stops / starts to regulate temperature. That removes one of the units tools to regulate room temperature.

 

Granted I may be mistaken, and your Daikin could behave differently


timmmay

20581 posts

Uber Geek

Trusted
Lifetime subscriber

  #3019943 11-Jan-2023 10:52
Send private message

Daikin behaves differently from Panasonic / Mitsubishi then. The fans only run when required to achieve the setpoint.


1 | 2 | 3 | 4
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.