#302990 9-Jan-2023 10:20
Send private message

I recently got a small Daikin Cora FTXM25UVMZ highwall heat pump for my office, which is about 4x2m with standard ceiling heights. It's mounted high up at one end of the office, pointed down the office. It has a thermostat inside it, and I have a temperature sensor on my desk.

 

Overall it works quite well, but it overheats the room. The screenshot below from the Daikin app is showing:

 

  • The heat pump is set to 21 degrees on heating
  • The inside temperature is 25 degrees
  • The outside temperature is 17 degrees
  • The temperature at my desk is 24.2 degrees

 

 

Even though the heat pump knows it's 25 degrees inside, the unit is on and actively heating. Once I turned it down to 20 degrees it turned off. If I set it to 23 degrees, which is about what I like, it reaches about 25 - 26 degrees.

 

The differential changes. If I set it to 20 degrees first thing in the morning the office will be heated to about 21 / 22 degrees. I can't just subtract say 3 degrees (set it to 20 degrees for target of 23 degrees) and set it to that temperature.

 

Does anyone know any way to have the Daikin heat to its setpoint then stop? I could do something in Home Assistant to tweak things, but I'd prefer not to. I could also call the installer, my electrician, I suspect they'd say "I don't know we just install them".

 

 

 


Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3 | 4
dahc
35 posts

Geek
+1 received by user: 10

ID Verified
Lifetime subscriber

  #3018911 9-Jan-2023 11:00
Send private message

I've found that using the heat or cool option usually pushes past by the set temperature but about a degree. I usually use auto unless I'm particular about wanting it to blow hot or cold. Have you tried auto?

 

From the manual: In AUTO operation, the system selects an appropriate operation mode (COOL or HEAT) based on the indoor temperature and starts the operation.

 

 




timmmay

20858 posts

Uber Geek
+1 received by user: 5350

Trusted
Lifetime subscriber

  #3018912 9-Jan-2023 11:10
Send private message

I don't use auto modes on heat pumps. Older models especially can cycle between heating and cooling. One degree over is fine, but this can be heating when it's already four degrees over the setpoint.


insane
3324 posts

Uber Geek
+1 received by user: 1006

ID Verified
Trusted
2degrees
Subscriber

  #3018920 9-Jan-2023 11:35
Send private message

I think it's because of the units size. I have a 1.6kw unit in my office and a 2kw in my master bedroom.

I used to have a 3.5kw in the master bedroom and had similar experiences as it was overkill, so moved it to my granny flat living area where it's perfect.

Perhaps get a sensibo to override it's enthusiasm?

Otherwise try running it on the quiet/eco mode?

Having said that, surely there is way to recalibrate it?



timmmay

20858 posts

Uber Geek
+1 received by user: 5350

Trusted
Lifetime subscriber

  #3018925 9-Jan-2023 11:54
Send private message

I'm not sure the unit turns on when it's already up to temp because it's oversized. The unit seems properly sized - in the dead of winter I need the 3.5kw of heat at times, and now in summer being cold sometimes hot others it ticks along rather than cycling constantly. 

 

I don't think it needs calibration, as it seems to know the temperature. It might just be a setting that needs to be adjusted. It might just be the way it works, and I have to get used to it.


neb

neb
11294 posts

Uber Geek
+1 received by user: 10018

Trusted
Lifetime subscriber

  #3018927 9-Jan-2023 11:59
Send private message

There's something a bit odd about the Daikin Coras, we have one too and to get the temperature to (say) 22 degrees on a hot day need to set it to 23 or 24. Same with heating in winter, setting it to 21 gets the room a lot warmer than 21.

djtOtago
1181 posts

Uber Geek
+1 received by user: 605


  #3018929 9-Jan-2023 12:00
Send private message

timmmay:

 

I don't use auto modes on heat pumps. Older models especially can cycle between heating and cooling. One degree over is fine, but this can be heating when it's already four degrees over the setpoint.

 

 

Have you actually tried this unit on Auto?

 

The two Daikins in the office I use, work pretty good on Auto. They are floor units however.


 
 
 
 

Shop now on Samsung phones, tablets, TVs and more (affiliate link).
kobiak
1615 posts

Uber Geek
+1 received by user: 551

Trusted

  #3018941 9-Jan-2023 12:18
Send private message

I have similar "issue" with my AUX 3.5kw heat pump (only reason I got larger unit because price was cheap). also in the small bedroom (9sqm + 6sqm hallway on the ground floor) used for office. I set unit to 21C and have couple temp sensors. it was more around 25+C constantly heating... and I come up to this 19-20C set temp. AUTO speed. Gives me around 22C, which I'm happy. it goes quit, sometimes stops, usually when sun is out in the afternoon. When I do AUTO for heating/cooling - obviously it's blowing cold air right on my head when it hits the 23-24C internal temp :D so nope.





helping others at evgenyk.nz


timmmay

20858 posts

Uber Geek
+1 received by user: 5350

Trusted
Lifetime subscriber

  #3018981 9-Jan-2023 13:18
Send private message

djtOtago:

 

Have you actually tried this unit on Auto?

 

The two Daikins in the office I use, work pretty good on Auto. They are floor units however.

 

 

I've never run an air conditioner on auto.... until today. I'm giving it a go now. The room was 24 degrees, I set it to auto / 23 and it didn't do anything. Setting it to 22 and it's working. Interestingly when it's on cool the fan goes whether or not it's cooling or down to temp, with auto the fan stops when it's down to temp. Useful to know :) I'll experiment a bit , try auto for heating tomorrow morning, and use whichever works best.


timmmay

20858 posts

Uber Geek
+1 received by user: 5350

Trusted
Lifetime subscriber

  #3018982 9-Jan-2023 13:19
Send private message

kobiak:

 

I have similar "issue" with my AUX 3.5kw heat pump (only reason I got larger unit because price was cheap). also in the small bedroom (9sqm + 6sqm hallway on the ground floor) used for office. I set unit to 21C and have couple temp sensors. it was more around 25+C constantly heating... and I come up to this 19-20C set temp. AUTO speed. Gives me around 22C, which I'm happy. it goes quit, sometimes stops, usually when sun is out in the afternoon. When I do AUTO for heating/cooling - obviously it's blowing cold air right on my head when it hits the 23-24C internal temp :D so nope.

 

 

I think I'll probably just have to take your approach and set the temperature to what works, ignoring the number. The annoying part is it's different on each mode. I may automate the tweaking in Home Assistant.

 

 

 

Thanks all for your thoughts. If anyone has a solution to make the thermostat accurate, great, but I'm not sure it's a solvable problem.


neb

neb
11294 posts

Uber Geek
+1 received by user: 10018

Trusted
Lifetime subscriber

  #3018983 9-Jan-2023 13:22
Send private message

timmmay:

I've never run an air conditioner on auto.... until today. I'm giving it a go now. The room was 24 degrees, I set it to auto / 23 and it didn't do anything. Setting it to 22 and it's working. Interestingly when it's on cool the fan goes whether or not it's cooling or down to temp, with auto the fan stops when it's down to temp. Useful to know :) I'll experiment a bit , try auto for heating tomorrow morning, and use whichever works best.

 

 

A problem with the "don't use auto mode" on heat pumps is that it dates from 15-20 years ago when they would mindlessly oscillate from heating to cooling mode to try and keep at the set point. Is this advice still relevant for today's systems?

timmmay

20858 posts

Uber Geek
+1 received by user: 5350

Trusted
Lifetime subscriber

  #3018999 9-Jan-2023 13:34
Send private message

neb: A problem with the "don't use auto mode" on heat pumps is that it dates from 15-20 years ago when they would mindlessly oscillate from heating to cooling mode to try and keep at the set point. Is this advice still relevant for today's systems?

 

Probably not. The current models have outdoor unit sensors so they can work things out more accurately.

 

I'm not sure if my Airtouch unit has access to the Daikin outdoor unit sensors. It doesn't expose that information to the user through the GUI or API. I don't use that one on auto anyway, we commonly have one room quite warm from the sun and the others cooler so I have to schedule things a bit carefully.


 
 
 

Support Geekzone with one-off or recurring donations Donate via PressPatron.
openmedia
3449 posts

Uber Geek
+1 received by user: 877

Trusted

  #3019004 9-Jan-2023 13:51
Send private message

timmmay:

 

I recently got a small Daikin Cora FTXM25UVMZ highwall heat pump for my office, which is about 4x2m with standard ceiling heights. It's mounted high up at one end of the office, pointed down the office. It has a thermostat inside it, and I have a temperature sensor on my desk.

 

Overall it works quite well, but it overheats the room. The screenshot below from the Daikin app is showing:

 

  • The heat pump is set to 21 degrees on heating
  • The inside temperature is 25 degrees
  • The outside temperature is 17 degrees
  • The temperature at my desk is 24.2 degrees

 

I've had a similar issue with my Mitsubishi. The unit often thinks it is quite a different temperature to the room and I think it is because the temp sensor is close to the hole in the wall they use for the piping.

 

I generally don't set it to cool, I set it to dry which achieves the temperature balance I require.





Generally known online as OpenMedia, now working for Red Hat APAC as a Technology Evangelist and Portfolio Architect. Still playing with MythTV and digital media on the side.


richms
29098 posts

Uber Geek
+1 received by user: 10208

Trusted
Lifetime subscriber

  #3019009 9-Jan-2023 13:59
Send private message

neb:

 

A problem with the "don't use auto mode" on heat pumps is that it dates from 15-20 years ago when they would mindlessly oscillate from heating to cooling mode to try and keep at the set point. Is this advice still relevant for today's systems?

 

Its irrelevent now with them all being inverter ones. What the problem is caused by is that they try to be too smart based on the limited input they have from a sensor on the device itself which is clearly not the room temperature.

 

Why none of the aircons have a wireless temperature sensor for them is something I don't understand. Hell, they all still use a prehistoric IR remote protocol that makes it so you have to aim the remote like a 2000s dvd player.





Richard rich.ms

timmmay

20858 posts

Uber Geek
+1 received by user: 5350

Trusted
Lifetime subscriber

  #3019010 9-Jan-2023 13:59
Send private message

openmedia:

 

I've had a similar issue with my Mitsubishi. The unit often thinks it is quite a different temperature to the room and I think it is because the temp sensor is close to the hole in the wall they use for the piping.

 

I generally don't set it to cool, I set it to dry which achieves the temperature balance I require.

 

 

There is often a differential between the desk and heat pump temperature, but I can see what temperature it thinks the room is as well.

 

My understanding of how "dry" works is it cycles between hot and cold, so it's not very efficient. The cooling mode dehumidifies but also cools the room, so it switches to heating for a while to keep the temperature up. You might find your power bill goes down if you use one cycle and set the temperature to about where it needs to be.


richms
29098 posts

Uber Geek
+1 received by user: 10208

Trusted
Lifetime subscriber

  #3019011 9-Jan-2023 14:02
Send private message

timmmay:

 

There is often a differential between the desk and heat pump temperature, but I can see what temperature it thinks the room is as well.

 

My understanding of how "dry" works is it cycles between hot and cold, so it's not very efficient. The cooling mode dehumidifies but also cools the room, so it switches to heating for a while to keep the temperature up. You might find your power bill goes down if you use one cycle and set the temperature to about where it needs to be.

 

 

Not anymore, dry just runs it in cool but a slower fan speed so the air has time to condense out. In winter its useless to keep a room warm and dry and I run a normal dehumidifier.