kiwikurt:

Curious as to what settings changes you made

 

It was a bit of a painful process to be honest - I used some Xiaomi temp sensors (with screen) in each bedroom (also used Home Assistant so I could monitor the data)

 

Then changed the following:

 

Initial Settings

 

Temp Sensor - Indoor Unit

 

Detailed Settings (adjust these settings with caution as there is all sorts of configuration stored here!)

 

Setting # 36 change it from 0000 -> 0001 (this shows the AC intake temp on the screen)

 

 

 

This allowed me to track what temp the rooms were and what the unit was seeing.

 

Then in the detailed settings there are 2 individual settings for "Heating Intake Temperature Shift" and "Cooling Intake Temperature Shift" 

 

I forget what the default values were, but i think one was 4degrees from memory, this was causing a massive overshoot for my situation. I adjusted these based on the temps I was seeing and found the sweet spot. (It also took over 6months as I had to wait for summer and winter!)




kiwikurt
33 posts

Geek


  #3153968 31-Oct-2023 12:02
Send private message

eluSiveNZ:

kiwikurt:

Curious as to what settings changes you made


It was a bit of a painful process to be honest - I used some Xiaomi temp sensors (with screen) in each bedroom (also used Home Assistant so I could monitor the data)


Then changed the following:


Initial Settings


Temp Sensor - Indoor Unit


Detailed Settings (adjust these settings with caution as there is all sorts of configuration stored here!)


Setting # 36 change it from 0000 -> 0001 (this shows the AC intake temp on the screen)


 


This allowed me to track what temp the rooms were and what the unit was seeing.


Then in the detailed settings there are 2 individual settings for "Heating Intake Temperature Shift" and "Cooling Intake Temperature Shift" 


I forget what the default values were, but i think one was 4degrees from memory, this was causing a massive overshoot for my situation. I adjusted these based on the temps I was seeing and found the sweet spot. (It also took over 6months as I had to wait for summer and winter!)



Wow good work! We have only 3 outlets and the other half is very resistant to any automation changes I make so may see how this summer goes. But that's really interesting.

iceteap3

40 posts

Geek


  #3155191 2-Nov-2023 22:43
Send private message

timmmay: I suggest taking a step back and consider zoning / individual room control, or high real units. Without zoning / ITC you will probably be unhappy with the system. Highwall units are simpler and work well, but can be louder.

Standard ducting is R0.6, I paid to upgrade to R1.0 as some approximations I did suggested payback period was less than a year. I suspect R1.6 will also be worthwhile. If your ducting runs are short there's less benefit.

 

 

 

An update - We had a person from AES come in today to show us the Fujitsu offerings with Zone control. 

 

Fujitsu ARTH45KHTA-HP (high performance model) 

 

15kW heating, 12.5kW cooling 

 

8 outlets, inc. WIFI, inc. R1.0 ducting 

 

6 individual zones with their own temp sensors controlled using the Fujitsu tablet controller (AnywAIR system)   

 

$ 13.8k NZD

 

Almost all specs are equal to or better than the Mitsi unit at $13k (i.e noise levels, capacity, other) but for an approx. 800 extra dollars. Im more concerned with reliability, quality, life span with the Fujitsu.

 

Has anyone got/can comment on a Fujitsu ducted system or the Anywair zoning system? I wonder how it compares to Airtouch/other controllers.

 

 

 

 




timmmay
20574 posts

Uber Geek

Trusted
Lifetime subscriber

  #3155208 3-Nov-2023 06:56
Send private message

I don't know anything about Fujitsu ducted units, but we had a Fujitsu high wall for 10 years that worked very well. The indoor unit was quite loud, but the outdoor unit was quiet, but it was quite high capacity unit which may be why it was loud inside. I would generally consider Fujitsu a good brand, with their own zone control with too much control. It's definitely worth following up and learning more about.

tweake
2391 posts

Uber Geek


  #3155493 3-Nov-2023 15:45
Send private message

iceteap3:

 

An update - We had a person from AES come in today to show us the Fujitsu offerings with Zone control. 

 

Fujitsu ARTH45KHTA-HP (high performance model) 

 

15kW heating, 12.5kW cooling 

 

 

so only 50% oversized. 😞


timmmay
20574 posts

Uber Geek

Trusted
Lifetime subscriber

  #3155497 3-Nov-2023 15:52
Send private message

There's a whole range of Fujitsu heat pumps in that series from 7.1kw to at 15.5kw. Instead of the ARTH45KHTA model there's the ARTH30KHTA 10kw and ARTH36KHTA 11.2kw, which would take the minimum power down from 4.2kw to 2.7kw - that would help a lot.

 

It says it has 'zone control' "This function enables efficient air-conditioning by selecting specific zones from the various zones divided within the indoor space.". It doesn't say it has a temperature sensor in each room, which is what you really need.


iceteap3

40 posts

Geek


  #3155507 3-Nov-2023 16:19
Send private message

We've had a remeasure of the house and it actually seems like its slightly larger than previously thought. The previous few ignored the common hallway areas and the visit from AES also mentioned that we should probably use 60w/m3 because of the number of floor to ceiling windows.

 

Seems like the house does need a larger unit ? (100m2 x 2.4m ceilings = 240m3 , 240m3 x 60 W/m3 = 14400W)

 

 

 

This is the zone controller that comes with it (including 6 Bluetooth temp sensors) 

 

https://www.fujitsugeneral.co.nz/anywair/ducted 

 

  


 
 
 

Cloud spending continues to surge globally, but most organisations haven’t made the changes necessary to maximise the value and cost-efficiency benefits of their cloud investments. Download the whitepaper From Overspend to Advantage now.
itxtme
2102 posts

Uber Geek


  #3155508 3-Nov-2023 16:23
Send private message

Cant comment on the zone control, but we have a Fujitsu 14kw/12.5kw that would be older than 10 years.  Goes perfectly well.  It is slightly loud on the outdoor compressor, but I believe that is the nature of the tech on these older models.  It could be well over 10 years, was old when we moved in 5 years ago.

 


Edit: to add I would happily replace it with another Fujitsu when it gave up the gohst


timmmay
20574 posts

Uber Geek

Trusted
Lifetime subscriber

  #3155515 3-Nov-2023 16:40
Send private message

iceteap3:

 

We've had a remeasure of the house and it actually seems like its slightly larger than previously thought. The previous few ignored the common hallway areas and the visit from AES also mentioned that we should probably use 60w/m3 because of the number of floor to ceiling windows.

 

Seems like the house does need a larger unit ? (100m2 x 2.4m ceilings = 240m3 , 240m3 x 60 W/m3 = 14400W)

 

 

 

This is the zone controller that comes with it (including 6 Bluetooth temp sensors) 

 

https://www.fujitsugeneral.co.nz/anywair/ducted 

 

 

We don't need hallways heated, unless you hang out there a lot the heat from the other rooms should keep it warm enough. The exception could be if the hallway turns into open plan or something odd.

 

Probably best to trust your installer, but maybe mention to them you would rather not oversize the unit so it runs continuously rather than turning off and on all the time.

 

Zone controller is one of those weird ones that only seems to monitor the temperature in one room at a time. From that page 'MainTemp – Acts as an automated MainZone. MainTemp will automatically select the zone with the greatest difference between actual and desired temperatures. Once this zone is selected and the desired temperature is reached, a new room will be selected and the process repeated.". A friend has a similar system at it works ok, not great, but ok. Airtouch monitors the temperature of all rooms at the same time and adjusts the dampers of each. That one is probably ok.

 

Make sure you tell your installers in writing what you want to achieve, that way if it doesn't do it you can say "I told you what I wanted". Something fairly broad such as "keep the north facing rooms cool in summer without making the south facing rooms very cold, and in winter heating all rooms to the desired target temperature without overheating rooms".


tweake
2391 posts

Uber Geek


  #3155516 3-Nov-2023 16:41
Send private message

iceteap3:

 

We've had a remeasure of the house and it actually seems like its slightly larger than previously thought. The previous few ignored the common hallway areas and the visit from AES also mentioned that we should probably use 60w/m3 because of the number of floor to ceiling windows.

 

Seems like the house does need a larger unit ? (100m2 x 2.4m ceilings = 240m3 , 240m3 x 60 W/m3 = 14400W)

 

 

 

This is the zone controller that comes with it (including 6 Bluetooth temp sensors) 

 

https://www.fujitsugeneral.co.nz/anywair/ducted 

 

  

 

 

sounds suspicious. window size is part of the calc already, so you do not increase it because of windows. hallway is often left out because generally it has no external walls (tho it has ceiling and floor) and that generally where the return is so it gets heated by the return flow.

 

also do not calculate by wattage per volume. thats way to crude. there is free calcs around that will do a basic simple calculation which is about the crudest i would do. you measure room sizes and window/door areas, insulation levels and a wild guess at air leakage. window size makes a massive difference to insulation levels.


1 | 2 | 3 
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.