  #2560507 8-Sep-2020 20:43
Send private message

larknz: It could also be a loose connection in the plug

 

Trying a different extension cord and wall socket, that should work it out. It could just be that running 9A through a cord for a solid hour creates heat.




MadEngineer
4591 posts

Uber Geek
+1 received by user: 2570

Trusted

  #2562573 11-Sep-2020 20:07
Send private message

Some maths for you.

 

 

 

Assuming a volt drop of 3V over that extension cord, if you're pulling 9A that means that cable is dissipating 27Watts over its length.

 

Because multiplication gives you the result of watts it should be obvious how things quickly get hot.





You're not on Atlantis anymore, Duncan Idaho.

SomeoneSomewhere
1882 posts

Uber Geek
+1 received by user: 1086

Lifetime subscriber

  #2562682 11-Sep-2020 21:17
Send private message

Watts total is not what matters in a case like this, unless you coil it all up in a pile (you should not do this unless it's a very small load - it cuts the capacity by a lot). Watts per meter is far more important as more meters means it can shed more heat.

 

To get 3V drop from a 9A load on 1mm^2, GenCalc says you would need 7.2m, and it would be running at about 44C if in 30C ambient and laying against a surface but otherwise unenclosed and with no other cables in close proximity.

 

The maths and experimentation has long been done on this. ASNZS 3008 is 150 pages just on sizing cable.

 

If it is hot the whole length of the cord, then that's the cord itself getting warm from load. Hot only at the ends (or one end) indicates a contact or termination problem.




timmmay

20859 posts

Uber Geek
+1 received by user: 5350

Trusted
Lifetime subscriber

  #2562684 11-Sep-2020 21:20
Send private message

I changed my office fan heater to a new extension cable in a new socket. The cable still doesn't get warm, and the end plugged into the wall doesn't get near as hot. I need to mix and match a bit to work out if it's the extension cord or the wall socket, but with a 1000W oil heater using the cord / socket that was getting hot before it's now cold, so probably at least worked around if not solved.

 

Interesting information thanks all.


1 | 2 | 3 | 4 