Topic # 150060 10-Jul-2014 09:01
Send private message

Hello, I'm looking for advice from those with experience or are in similar situation where your aluminum framed single glaze windows have leaked and the wood wall membrane has gone rotten somewhat. I have attached photos. My issue is thus, when I removed the rotten wood membrane to then replace it I found the outer underside of the window frame to be sweating with condensation on the colder days which from what I could see could be why the wood membrane was rotten? Does this mean that the whole window frame could be 'sweating' and the wood frame holding the window frame is also rotten, from what I can see, the wood membrane around the window is exposed, I can't see any other rot. I'm now thinking it's because the window frame is now exposed to the air and it then sweats.

What are your thoughts? Before I replace the wood I'd like to know if I need to take the window out and line 'insulate' the wood from the aluminum window frame.

Thanks in advance.




Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2 | 3
2253 posts

Uber Geek
+1 received by user: 224


  Reply # 1086235 10-Jul-2014 09:18
Send private message

To help with other replies I'd suggest a wider shot showing all of the framing below the window and a definition of what you're calling the "membrane".



8 posts

Wannabe Geek


  Reply # 1086241 10-Jul-2014 09:21
Send private message

Oh, I thought 'membrane' was builders speak for the wood frame that makes up the wall, this is what I mean by membrane is the wood framing wall :-)

I will post a wider shot of the windows this evening. The only rot is in this corner as per the photographs but yes you're right I'll offer more context.

Back soon. Thanks.

 
 
 
 


13333 posts

Uber Geek
+1 received by user: 2245

Trusted
Subscriber

  Reply # 1086278 10-Jul-2014 10:06
Send private message

I don't think it's called a membrane.

I suggest you get a builder in to replace the framing, fingers crossed you can reuse the window.




AWS Certified Solution Architect Professional, Sysop Administrator Associate, and Developer Associate
TOGAF certified enterprise architect
Professional photographer


830 posts

Ultimate Geek
+1 received by user: 259

Trusted

  Reply # 1086286 10-Jul-2014 10:31
Send private message

grahamhowe: Oh, I thought 'membrane' was builders speak for the wood frame that makes up the wall, this is what I mean by membrane is the wood framing wall :-)

I will post a wider shot of the windows this evening. The only rot is in this corner as per the photographs but yes you're right I'll offer more context.

Back soon. Thanks.


In this context I think you're meaning a moisture proof material that goes under the external cladding.  See section 5.1 here http://www.dbh.govt.nz/UserFiles/File/Publications/WHRS/pdf/constructing-cavities.pdf

2708 posts

Uber Geek
+1 received by user: 554


  Reply # 1086288 10-Jul-2014 10:43
Send private message

Glassboy:In this context I think you're meaning a moisture proof material that goes under the external cladding.  


And which by the look of these photos does not appear to exist ( I am assuming the "white" is some sort of firbrelite panel/sheet.

The reason the wood is rotting is because there is no "membrane" between the window frame and the exterior caldding,  (From memory today they would lap the membrane into the bottom of the windows void and then insert the window frame, so any run off from the window is kept away from the framing,

You will need to take the whole window out, replace the surrounding rotten joists and then re affix the window frame to the new framing,

I'm guessing that the timber is all laser frame or otherwise untreated, hence the rot, you will need to replace it with H1.2



8 posts

Wannabe Geek


  Reply # 1086292 10-Jul-2014 10:56
Send private message

Cheers WellyGary. Thats my thoughts too as per the building code seen in new builds to encase the space where the window is being fitting with the membrane. The cladding is exposed as the builders paper has eroded away so I'll then need to renew that, oh and whilst on the job I should re-clad the whole house with proper weatherboarding instead of this 80's fibre cement boarding.

Thanks folks. Much work to be done.

P.S. My father's coming over for his hols this xmas and he's a builder. I'll remind him to bring his tool belt.

4471 posts

Uber Geek
+1 received by user: 1288


  Reply # 1086297 10-Jul-2014 11:01
One person supports this post
Send private message

grahamhowe: [snip] I should re-clad the whole house with proper weatherboarding instead of this 80's fibre cement boarding.


Be careful that isn't an asbestos product - if it is, don't touch it, and get in a company that specifically deals with asbestos removal.

2253 posts

Uber Geek
+1 received by user: 224


  Reply # 1086310 10-Jul-2014 11:17
Send private message

Something seems wrong with the detail below the window where there seems to be some sort of flashing. Was there another piece of horizontal framing forming the sill that has been chopped out? This describes current practice http://www.branz.co.nz/cms_show_download.php?id=dd0bd80c737c9ebf49722dfa128c1db247264ea4

I have had a similar problem with a wooden window where water was leaking past some rusty nails in the central stile. Taping the still framing was well worth it.

Think carefully about changing too much. Changing to weatherboard will mean a building consent and that may lead to having "cavity" fixed rather than direct fixed as you currently have. This will affect all your windows etc.



8 posts

Wannabe Geek


  Reply # 1086312 10-Jul-2014 11:22
Send private message

@Bung. Yes I've chopped out the rotten wood and I'm replacing it with treated framing. I stopped work because of the condensation I spotted on the underside of the window frame and then thought it might be like this all around the frame on colder days and so turned to this great forum, by the way thanks to ALL :-)

No cavity is an issue and yes I was joking about the re-cladding job. I will however when I inspect the insulation in the walls inside the house I will be removing the jib and inspecting the framing around the windows elsewhere in the house.

I think the 'taping' or using installing a membrane around this window will help. Should be interesting removing the window.

My foreman is a father via Skype.

2253 posts

Uber Geek
+1 received by user: 224


  Reply # 1086317 10-Jul-2014 11:30
Send private message

Try a pm to gazbo, he adds value to this sort of thread.

5102 posts

Uber Geek
+1 received by user: 2365


  Reply # 1086696 10-Jul-2014 20:01
Send private message

I suggest you get an aluminium joinery / repair company to look at the windows.  Whether condensation or leaking, there may be a preventative fix for the other windows without removing them.
For example here : http://www.exceed.co.nz/maintenance/services/windows-repairs-faults/
The cladding without cavity is a bit of a concern.  You might be able to get an idea of damp problems from inside - moisture test on the gib, but that may not answer whether it's getting through the cladding etc or there are problems with other windows.  You do need to get this sorted.


gzt

9158 posts

Uber Geek
+1 received by user: 1290


  Reply # 1086702 10-Jul-2014 20:11
Send private message

wellygary: The reason the wood is rotting is because there is no "membrane" between the window frame and the exterior caldding

Very unlikely. Many older houses used similar construction methods and do not have rot around the windows from condensation. It is far more likely there is a minor issue somewhere which is allowing a fair drip of moisture into the cavity every time it rains. Some wider photos are required to educated guess at where that might be. Could be the window itself but there are many other possibilities. For instance a nail worked out of it's hole in the external cladding in exactly the wrong place can be the cause of things like this if left for a few years.

5102 posts

Uber Geek
+1 received by user: 2365


  Reply # 1086902 11-Jul-2014 08:39
Send private message

gzt:
wellygary: The reason the wood is rotting is because there is no "membrane" between the window frame and the exterior caldding

Very unlikely. Many older houses used similar construction methods and do not have rot around the windows from condensation. It is far more likely there is a minor issue somewhere which is allowing a fair drip of moisture into the cavity every time it rains. Some wider photos are required to educated guess at where that might be. Could be the window itself but there are many other possibilities. For instance a nail worked out of it's hole in the external cladding in exactly the wrong place can be the cause of things like this if left for a few years.


From the look of those photo there isn't a cavity.  While cladding might have been direct attached to framing in the past, it might have more likely been packed out to mount cladding flush on to (uneven) framing.  The OP's example has multiple problems.  The window design / flashing system is apparently inadequate.  If water gets in anywhere - window, nail hole or elsewhere, then not only is there nothing to stop it from getting in to the framing, but because the cladding is direct attached, there's no air circulation to dry it out, and there are also no gaps between horizontal dwangs etc and the cladding - so any water which does get in is trapped.   As to whether the cladding is asbestos - then hopefully not - but it needs to be tested.
It won't be what the OP wants to hear, but that's classic "leaky home" failure - and the best way to fix it would be to re-clad bringing it up to code, probably at the same time replacing all the window joinery and insulating exterior walls.  

2253 posts

Uber Geek
+1 received by user: 224


  Reply # 1086917 11-Jul-2014 09:14
Send private message

If its a ground floor window maybe a shot of the outside as well as the wider view inside. What looks like a sill flashing doesn't seem to have much cover over the top of the fibro sheet. If it is a mid to late 80s build it is likely to be the newer asbestos free sheeting that had cellulose fibres instead. I think it got treated like the old fibrolite that could be left unpainted but it should have had edges sealed to stop it absorbing water. On our 86 bach anything covered missed getting paint. I've taken some sheets off to redo the building paper. The good thing is the framing shows no sign of rot or mould even where there's been some dampness.



8 posts

Wannabe Geek


  Reply # 1086924 11-Jul-2014 09:21
Send private message

Thanks further for contributing. I will add further exploration photos this weekend. I have since moving in sealed the outer top and sides (not underneath) of the window frame; no further leaks have appeared so I'm thinking this happened post to us moving in. Thank you previous owner. The window seal is then in question.

Re the cladding this fibre cement cladding has no cavity and isn't nailed to the frame except the very last row on the building which is nailed to stop it flapping in the wind. These nails I have since sealed. I'm getting on top of these little issues.
Because of the window leak the builders paper has detoriated so it will need replacing because I want to install wall insulation.

photos coming soon. Thanks folks.

 1 | 2 | 3
Filter this topic showing only the reply marked as answer View this topic in a long page with up to 500 replies per page Create new topic



Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

UFB connections pass 460,000
Posted 11-Dec-2017 11:26


The Warehouse Group to adopt IBM Cloud to support digital transformation
Posted 11-Dec-2017 11:22


Dimension Data peeks into digital business 2018
Posted 11-Dec-2017 10:55


2018 Cyber Security Predictions
Posted 7-Dec-2017 14:55


Global Govtech Accelerator to drive public sector innovation in Wellington
Posted 7-Dec-2017 11:21


Stuff Pix media strategy a new direction
Posted 7-Dec-2017 09:37


Digital transformation is dead
Posted 7-Dec-2017 09:31


Fake news and cyber security
Posted 7-Dec-2017 09:27


Dimension Data New Zealand strengthens cybersecurity practice
Posted 5-Dec-2017 20:27


Epson NZ launches new Expression Premium Photo range
Posted 5-Dec-2017 20:26


Eventbrite and Twickets launch integration partnership in Australia and New Zealand
Posted 5-Dec-2017 20:23


New Fujifilm macro lens lands in New Zealand
Posted 5-Dec-2017 20:16


Cyber security not being taken seriously enough
Posted 5-Dec-2017 20:13


Sony commences Android 8.0 Oreo rollout in New Zealand
Posted 5-Dec-2017 20:08


Revera partners with Nyriad to deliver blockchain pilot to NZ Government
Posted 5-Dec-2017 20:01



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.