+1 received by user: 94


Topic # 242188 15-Oct-2018 13:25
Send private message quote this post

Seems like a real basic question - but wanting to confirm this so I can understand whats happening. We have the Ci17 heatpump (as detailed here http://www.oasisheatpumps.com/pdf/Oasis-Inverter-Swimming-Pool-Heat-Pump-Specifications-2017.pdf) and reading that spec doc, am I correct in thinking that it shouldn't be drawing any more than 2.86kW of power? I could swear when I last looked at it, it was reporting using approx 4kW :\ 


Filter this topic showing only the reply marked as answer Create new topic
3169 posts

Uber Geek
+1 received by user: 1220

Subscriber

  Reply # 2108172 15-Oct-2018 13:33
Send private message quote this post

How are you measuring that power draw? As lots of devices don't compensate for power factors. Meaning they will often overread power usage on electric motor and electronic device loads.

Try switching off everything in your house except for the heatpump. And see what your electricity meter reports the usage to be.







585 posts

Ultimate Geek
+1 received by user: 94


  Reply # 2108173 15-Oct-2018 13:34
Send private message quote this post

It has a screen/graph on the unit itself reporting the power use and water temps etc


3169 posts

Uber Geek
+1 received by user: 1220

Subscriber

  Reply # 2108188 15-Oct-2018 13:50
One person supports this post
Send private message quote this post

Maybe the inbuilt measuring device is not power factor aware. Meaning that the numbers it is reporting are actually KVA and not KW.

If the inverter doesn't have active Power Factor Correction. The measurement device will over read by 40% or so.

Check that you don't have a fault. Poor water flow through the heatpump will cause excessive power usage.

Otherwise just add your own external monitoring.





6733 posts

Uber Geek
+1 received by user: 593

Trusted

  Reply # 2108202 15-Oct-2018 14:18
2 people support this post
Send private message quote this post

Might be reporting it's heat/cooling output, rather than it's device consumption?




585 posts

Ultimate Geek
+1 received by user: 94


  Reply # 2108203 15-Oct-2018 14:18
Send private message quote this post

Ahh interesting; there are flow restrictor valves installed, as the installer said that they perform better if the flow is restricted...but I wonder if maybe they are restricting things too much...

 

Interesting also to hear the power factor correction - as that would land exactly on the mark (ie its reading 4kW and the spec sheet shows 2.86kW - ie a 40% diff)

 

Thanks for your input Aredwood


3169 posts

Uber Geek
+1 received by user: 1220

Subscriber

  Reply # 2108543 15-Oct-2018 22:08
Send private message quote this post

Check the temp difference between the water inlet and outlet pipes when the unit is running at max output. Typically with pool heaters, there should be almost no temp difference. As there should be plenty of flow so the heat exchanger can work at max efficiency. Otherwise you get higher than necessary compressor discharge temperature and pressure. Which means lower efficiency and more stress on the compressor.

The installation instructions should give a recommendation on the ideal flow rates.





51 posts

Master Geek
+1 received by user: 21


  Reply # 2109110 16-Oct-2018 20:30
Send private message quote this post

Rated current is 17.2A and that's pretty much exactly 4kW. Definitely sounds like that, though it's a daft mistake for them to make.

 

 

 

As above, check your revenue meter and turn off big loads (cooking, hot water, heating) and you should get a pretty good idea of what it's drawing.


191 posts

Master Geek
+1 received by user: 31


  Reply # 2110623 18-Oct-2018 19:29
Send private message quote this post

Do you have access to a clamp meter? If you can measure the current draw you can work out the power consumption.

51 posts

Master Geek
+1 received by user: 21


  Reply # 2110635 18-Oct-2018 19:30
Send private message quote this post

Kickinbac: Do you have access to a clamp meter? If you can measure the current draw you can work out the power consumption.

 

 

 

Depending on the model, loading etc, power factor may not be good. So you need a clamp meter that can measure power, not just current. A bit rarer.


191 posts

Master Geek
+1 received by user: 31


  Reply # 2110636 18-Oct-2018 19:36
Send private message quote this post

I may be wrong but I always understood that inverters (which are basically variable frequency drives) corrected the power factor.

51 posts

Master Geek
+1 received by user: 21


  Reply # 2110637 18-Oct-2018 19:38
Send private message quote this post

Kickinbac: I may be wrong but I always understood that inverters (which are basically variable frequency drives) corrected the power factor.

 

Some do. I believe some can be quite capacitive, and the correction is often calibrated for full load - operation at lower loads isn't such an issue because the current is lower than maximum anyway.

 

I have planned to do some proper measuring but haven't gotten around to it.


Filter this topic showing only the reply marked as answer Create new topic

Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.