Hi. My house has the older style plug in wire fuses on the fuse box. A few have 16 amp circuit breakers. My problem is if the power goes off, when the power comes on again, occasionally the circuit breaker that the 2 fridges is on trips. It must be the initial power on surge.
Reading on the internet, seems there are different surge ratings on circuit breakers. Mine are B, but looks like C might be the answer. A friend suggested I just fit a 16 amp wire fuse... what do you guys think?

 

Thanks

 

Peter.

 

 


View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2
timmmay
20591 posts

Uber Geek

Trusted
Lifetime subscriber

  #2534989 5-Aug-2020 10:39
Send private message

I have circuit breakers in an old house, they never trip when power comes back on. I wouldn't go back to fuse wire, I'd ask an electrician or get one in to have a look.




Jaxson
8044 posts

Uber Geek

Trusted

  #2535010 5-Aug-2020 11:17
Send private message

Personally I'd get that one troublesome unit replaced with a modern device.

After that you'd need to look at why there is such a start up rush, and check if you have heaters/electric blankets etc on that same circuit that could be separated.

 

 

 

At the end of the day, these are protection devices, so they may be telling you something quite valid that you're looking at ways to ignore.


andrewNZ
2487 posts

Uber Geek
Inactive user


  #2535046 5-Aug-2020 12:28
Send private message

Those plug in circuit breakers get temperamental with age particularly the older round button ones.

Combine that with the initial demand of two compressor motors trying to start at once and whatever else is on the circuit...

It'd definitely be worth trying replacing it for a start.

Edit: DON'T replace it with a bigger one! Only an electrician can do that once they have checked that the circut can carry both the rated current of the breaker & the current required to trip the breaker.

Worst case, a larger breaker doesn't trip for a fault and burns your house down.



JeremyNzl
359 posts

Ultimate Geek


  #2535101 5-Aug-2020 12:57
Send private message

When all devices are off and all turned off at once you are getting a maximum demand that could be exceeding you fused limit.

 

Normally this would be brief and most breakers will handle a % of over current for a period,

 

The different curve breakers are for motor starting in industrial or specialized applications where this inrush is expected and very brief. 

 

 

 

For insurance purposes, get a sparky to have a look and test the circuit and identify the sizing of the circuit wire and the load you are running on it.

 

Sometimes there can be something developing and you may be thankful the situation you describe and brought it to your attention. 


Bung
6496 posts

Uber Geek

Subscriber

  #2535103 5-Aug-2020 13:00
Send private message

Do you have to have both fridges on the same cicuit or is it actually a fridge / freezer pair?

timmmay
20591 posts

Uber Geek

Trusted
Lifetime subscriber

  #2535119 5-Aug-2020 13:21
Send private message

It is sometimes worth getting a sparky in when odd things happen. For example, we found sometimes if we touched the metal dishwasher and metal kettle at the same time we sometimes felt a tingling. Electrician found the circuit was faulty, possibly chewed through by rats last year when they were everywhere, and we had to put a new circuit in.


neb

neb
11294 posts

Uber Geek

Trusted
Lifetime subscriber

  #2535132 5-Aug-2020 13:33
Send private message

JeremyNzl:

The different curve breakers are for motor starting in industrial or specialized applications where this inrush is expected and very brief. 

 

 

In terms of fixing this at the other end, you can also get inrush current limiters/motor soft starters that will help deal with this. Alternatively, delay-start devices that ensure all the high-power loads don't start at the same time. So it's quite fixable without having to play Russian roulette with your wiring.

 
 
 

Trade NZ and US shares and funds with Sharesies (affiliate link).
tripper1000
1618 posts

Uber Geek


  #2535241 5-Aug-2020 15:23
Send private message

As others have mentioned the CB's don't last for ever. Replace it and if symptom persist see a professional. 

 

Generally they're designed to remain on for a brief and passing overload and this aspect of the design may have failed. I have also seen them pop at lower and lower currents as they age. Someone may have even dropped it, damaging the internals. 


frankv
5680 posts

Uber Geek

Lifetime subscriber

  #2535266 5-Aug-2020 15:53
Send private message

Plug one of your fridges into another circuit?

 

 


neb

neb
11294 posts

Uber Geek

Trusted
Lifetime subscriber

  #2535400 5-Aug-2020 17:41
Send private message

Speaking of soft starters, there's a bunch of these available from the usual suspects for a lot less than the eyewatering prices local sources charge, but they're handcrafted from the finest Chinesium so who knows how safe/reliable they actually are. Does anyone have any experience with them?

Tracer
343 posts

Ultimate Geek


  #2535474 5-Aug-2020 20:32
Send private message

A B curve breaker is not appropriate for inductive loads like motors. C curve is general purpose and basically all you should find in houses. B and D are for more specialised scenarios.


richms
28192 posts

Uber Geek

Trusted
Lifetime subscriber

  #2535488 5-Aug-2020 21:13
Send private message

I have the same thing if I turn the main switch off, things will trip when I turn it back on, often the 63A on the meter board will. However if its coming back from a powercut its fine, I guess because everyone elses inrush currents are limiting the voltage rise to a degree so its not enough to trigger the magnetic part of the breaker.





Richard rich.ms

gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #2535489 5-Aug-2020 21:17
Send private message

Tracer:

 

A B curve breaker is not appropriate for inductive loads like motors. C curve is general purpose and basically all you should find in houses. B and D are for more specialised scenarios.

 

 

 

 

B curve circuit breakers are quite common in the UK in the domestic area, in NZ C curve are the more common circuit breakers, with D curve usually used for motor related circuits.

 

Unless you have some more specialized knowledge in the electrical area don't go buying a D curve to replace your existing circuit breaker as there are a bunch of other things like loop impedance of the whole circuit to take in to account otherwise the circuit breaker will not trip under fault conditions in the required time - This means fire and/or electric shock.

 

 


Beavis

159 posts

Master Geek


  #2535509 6-Aug-2020 00:04
Send private message

Thanks everyone. I decided just to buy a replacement CB, but this time got a C not a B. Seems to have fixed the problem so far. So faulty CB or one with higher surge capacity. Has fixed problem and don’t see it as a burning down the house issue. Still a 16 amp CB, just may take another second or so...

 

 

 

Thanks.


neb

neb
11294 posts

Uber Geek

Trusted
Lifetime subscriber

  #2536514 8-Aug-2020 00:56
Send private message

Another option is to fit an inrush current limiter, e.g. this Meanwell one, which is fixing the problem rather than bypassing the thing telling you there's a problem (looks like a standard thermistor+relay combo, so the only thing to watch out for is that you don't cycle the equipment on and off rapidly since the thermistors won't cool down and you'll lose the current-limiting). You can get DIN-rail-mount ones that address multiple hard-start loads being connected if that's what's causing it.

 1 | 2
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.