We're looking to put in some irrigation, and the design means we'll need to run a decent length of some 24v cable to power some solenoids.

 

My google-fu is failing me, as I can't find if there's a minimum depth this needs to be buried (inside conduit). I can find the rules for 240V TPS, but am drawing a blank for 24V.

 

Thanks





 Home:                                                           Work:
Home Work


Create new topic
michaelmurfy
meow
13579 posts

Uber Geek
+1 received by user: 10910

Moderator
ID Verified
Trusted
Lifetime subscriber

  #2801250 26-Oct-2021 11:33
Send private message

Like garden lights I don't think there is a specific requirement for low voltage cabling. For example, there is no requirements to even bury the garden light cable (which runs at 24v in my case).





Michael Murphy | https://murfy.nz
Referral Links: Quic Broadband (use R122101E7CV7Q for free setup)

Are you happy with what you get from Geekzone? Please consider supporting us by subscribing.
Opinions are my own and not the views of my employer.




Paul1977

5171 posts

Uber Geek
+1 received by user: 2192


  #2801273 26-Oct-2021 11:58
Send private message

michaelmurfy:

 

Like garden lights I don't think there is a specific requirement for low voltage cabling. For example, there is no requirements to even bury the garden light cable (which runs at 24v in my case).

 

 

Thanks, that makes things easier.


cisconz
cisconz
1348 posts

Uber Geek
+1 received by user: 179

ID Verified
Trusted
Lifetime subscriber

  #2801321 26-Oct-2021 12:53
Send private message

I would highly recommend conduit though (Even if not buried), it protects against the spade and will last a lot longer. 





Hmmmm




coffeebaron
6304 posts

Uber Geek
+1 received by user: 3567

Trusted
Lifetime subscriber

  #2801375 26-Oct-2021 13:53
Send private message

Typically you'd aim for 200mm like short depth fibre, but no official requirement to do so.




Rural IT and Broadband support.

 

Broadband troubleshooting and master filter installs.
Starlink installer - one month free: https://www.starlink.com/?referral=RC-32845-88860-71 
Wi-Fi and networking
Cel-Fi supply and installer - boost your mobile phone coverage legally

 

Need help in Auckland, Waikato or BoP? Click my email button, or email me direct: [my user name] at geekzonemail dot com


SomeoneSomewhere
1882 posts

Uber Geek
+1 received by user: 1086

Lifetime subscriber

  #2801394 26-Oct-2021 14:38
Send private message

I think it's in section 7 of 3000, but by memory it is 'there is no depth or requirement for protection'.

 

 

 

This assumes it is SELV or PELV; i.e. fully isolated from the mains.


raytaylor
4076 posts

Uber Geek
+1 received by user: 1296

Trusted

  #2804321 30-Oct-2021 15:10
Send private message

I say to customers 
"Deeper than a cows hoof if the paddock becomes very muddy"
Or 300mm, whichever is deeper. 

 

Always do conduit. We like using the 16mm irrigation hose from mitre 10 - its super cheap and works as a layer of protection against rodents. 





Ray Taylor

There is no place like localhost

Spreadsheet for Comparing Electricity Plans Here


 
 
 

Stream your favourite shows now on Apple TV (affiliate link).
Froglotion
208 posts

Master Geek
+1 received by user: 78


  #2804548 31-Oct-2021 09:14
Send private message

Could just run battery setup? Mine runs off a 9V battery for the controller which controls two solenoids. 


Bung
6733 posts

Uber Geek
+1 received by user: 2926

Subscriber

  #2804561 31-Oct-2021 09:39
Send private message

raytaylor:

I say to customers 
"Deeper than a cows hoof if the paddock becomes very muddy"
Or 300mm, whichever is deeper. 



The length of the blade on a garden spade should be minimum for anything. I was digging in an area full of macrocarpa roots and didn't realise that the water supply originally looped around the back of the house to a tank. I hit resistance and hit it back harder. The pvc water supply pipe was about 150mm from surface. At least with water you get immediate feedback.