#296131 24-May-2022 13:50
Send private message

Hi,

 

Was planning on swapping out a shaver socket with an RCD socket in the bathroom.   What I have discovered is the socket is wired off one of my lighting circuits so it looks like I will need to get a sparky in to drop a new line and connect it to one of the power circuits given a hairdryer would be borderline on amperage.  Question; is this common practice to have shaver plugs on lightning circuits or just some cowboy wiring?

 

Cheers


Create new topic
wellygary
8328 posts

Uber Geek


  #2917973 24-May-2022 14:01
Send private message

Shaver sockets have a restricted limited load, (much less than 10amp)  so I suspect it was probably legal "back in the day" to run it off a light circuit, 




richms
28191 posts

Uber Geek

Trusted
Lifetime subscriber

  #2917999 24-May-2022 14:51
Send private message

wellygary:

 

Shaver sockets have a restricted limited load, (much less than 10amp)  so I suspect it was probably legal "back in the day" to run it off a light circuit, 

 

 

It was encouraged to do that in the days of fuses as there was a number of outlets per fuse, but the lighting circuit had no such limit. Towel rails too.





Richard rich.ms

Stu1
1769 posts

Uber Geek

ID Verified
Subscriber

  #2918055 24-May-2022 17:12
Send private message

rabba:

Hi,


Was planning on swapping out a shaver socket with an RCD socket in the bathroom.   What I have discovered is the socket is wired off one of my lighting circuits so it looks like I will need to get a sparky in to drop a new line and connect it to one of the power circuits given a hairdryer would be borderline on amperage.  Question; is this common practice to have shaver plugs on lightning circuits or just some cowboy wiring?


Cheers



Couldn’t the sparky connect a RCD at the mains? Then wire up a normal plug in the bathroom? . We found power sockets running off lighting during a reno , must of been relaxed certification back in the day




Daynger
435 posts

Ultimate Geek


  #2918087 24-May-2022 18:18
Send private message

Yes, it was very common to have shaver outlets running on lighting circuits.


gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #2918094 24-May-2022 18:38
Send private message

Stu1:
rabba:

 

Hi,

 

 

 

Was planning on swapping out a shaver socket with an RCD socket in the bathroom.   What I have discovered is the socket is wired off one of my lighting circuits so it looks like I will need to get a sparky in to drop a new line and connect it to one of the power circuits given a hairdryer would be borderline on amperage.  Question; is this common practice to have shaver plugs on lightning circuits or just some cowboy wiring?

 

 

 

Cheers

 



Couldn’t the sparky connect a RCD at the mains? Then wire up a normal plug in the bathroom? . We found power sockets running off lighting during a reno , must of been relaxed certification back in the day

 

could be done, but due to a lighting circuit typically been 1.0mm the circuit breaker would have to be 6A - too small to run a hair dryer.

 

Back in the 70's and 80's when shaver sockets were common, they were usually wired off a light circuit in 1.0mm due to the small load of a shaver it would not cause any overload issues, but converting to a regular socket to run a hair dryer - run a new circuit.

 

 


  #2918121 24-May-2022 19:07
Send private message

Yeah. Going to need to fish or pull a new cable from somewhere else.


Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.