One strand is typically 1.0mm, three strands is typically 1.5mm, and seven strands is 2.5mm. Take those numbers with a grain of salt though, as the only real way to tell what you've got is to read the specs on the outer insulation.
Accurately measure the diameter of one strand of the conductor.
Calculate the cross sectional area of that strand using the formula: A=(pi*diameter^2)/4
Multiply the answer by the number of strands in the conductor.
If it is only a single strand then it is 1mm^2.
3 strands @ 0.95mm dia is 2.13mm^2. So, yes, it is 2.5mm^2 cable.
What did you measure the cable cores with?
As above, more likely to be a 1.5mm cable unless its some oddball or very old one.
What size circuit breaker is protecting the cable?
Our house is mod 60's and has 2.0mm TPS on some of the power circuits, when I got an electrician to change the board he had to shoot out and get 16A breakers instead of the usual 20A breakers.
John
I know enough to be dangerous
SATTV:
Our house is mod 60's and has 2.0mm TPS on some of the power circuits, when I got an electrician to change the board he had to shoot out and get 16A breakers instead of the usual 20A breakers.
John
That will be an old imperial sized cable, 3/036 or something.
https://www.diynot.com/wiki/Electrics:Old-Imperial-cable-sizes
Daynger:What did you measure the cable cores with?
As above, more likely to be a 1.5mm cable unless its some oddball or very old one.
What size circuit breaker is protecting the cable?
SATTV:Our house is mod 60's and has 2.0mm TPS on some of the power circuits, when I got an electrician to change the board he had to shoot out and get 16A breakers instead of the usual 20A breakers.
John
mb82: My house is 1990. Wire for power points is obviously thicker than light switches. It is 3 wire red black and green. 3 strands of copper per wire colour I measured each strand of copper to be about 0.95mm thick. Is this 2 5mm tps cable? Can't see enough of it to read if anything is written on it and crawling in attic trying to see it was not fun
mb82:
Measures the cable with a cheap vernier.
Breaker size interesting 3 circuits are 15amp wire ceramic housing, kitchen and laundry have been changed to 20amp breakers.
Could not see wire size on cable just says:
1368
1989
International industries ltd auckland nz
Elec cable 600/1000v
90s house with ceramic fuses?
I thought it was circuit breakers by then, but its a little before my time.
Are you sure its not an old house that had a remodel in the 90s?
Daynger:mb82:
Measures the cable with a cheap vernier.
Breaker size interesting 3 circuits are 15amp wire ceramic housing, kitchen and laundry have been changed to 20amp breakers.
Could not see wire size on cable just says:
1368
1989
International industries ltd auckland nz
Elec cable 600/1000v
90s house with ceramic fuses?
I thought it was circuit breakers by then, but its a little before my time.
Are you sure its not an old house that had a remodel in the 90s?
I have confirmed the cable size is 3/.036 imperial which is 1.970mm2
Anyone know the rules about swapping from single to double outlets?
larknz: If it has rewireable fuses you were only allowed 2 sockets per circuit, although many have replaced single sockets with doubles.
neb: Friend of mine mentioned in passing today that her house, built as cheaply as possible, used one-size-smaller-than-required cable (I'm guessing 1mm lighting instead of 2.5mm standard) for at least some of the power points. She's running heaters off that... I asked if she could get to any cable run and see how warm it got, but it's all buried inside walls.
|
![]() ![]() ![]() |