#319008 13-Mar-2025 11:27
Send private message

2015 Home Concrete Block home with Double Glazing and DVS.  Currently no condensation throughout, but gets cold in winter and a bit hot summer nights.  So we want to add a ducted heat pump to our home (heat pump will be 12.5kw Daikin or Panasonic with Airtouch 5) 

Heatpump usage patters:  Summer 5pm to 12am to cool lounge and bedrooms.  Spring / Autumn - None.  Winter 5pm - 10am heating.

 


Request:  Could I have your advise as to whether we should retain the DVS system, Buy a new ERV with the ducted heatpump or forget about the ventilation. 

Options: 
(1) Remove DVS and utilise new ducted heatpump only - add ERV in future if necessary
     - Concern that when heat pump not running there is no circulation 
     - Concern that we will begin to have condensation in winter
(2) Retain 3/4 or the DVS outlets (garage, hallway, living, spare bedroom) for the purpose of ventilation (this air would likely be fed around the house by the heat pump system 
     - Concern that when heat pump not running many rooms won't receive the ventilation (only really works if heat pump is on)
     - Lots of ducting in ceiling and extra outlets in house.
(3) Add ERV system to the Heatpump system 
     - Is ERV taking outside air going to add humidity to the home in winter? Unlike our attic DVS.
     - Can the system (managed by Airtouch) be smart and just use ERV for ventilation most of the time except the hours mentioned above when active cooling and heating are required?


For this discussion, money is not an issue.  I believe an ERV unit will be about 3000 dollars extra. 




SECOND QUESTION:  
One vendor has recommended round diffusers as outlets.   Another has recommended linear grills.  The grills look a lot nicer.  Any recommendations or features I should ensure the outlets have?  For example I'm thinking of asking if they can be adjusted to move air down or up. 

 

 


Create new topic
lxsw20
3552 posts

Uber Geek

Subscriber

  #3353394 13-Mar-2025 11:36
Send private message

We are in process of building, our system will be a ducted heat pump connected to a fresh air heat exchanger. (Daikin equivalent of Mitsubishi Lossney) 

 

It would be worth talking to your heat pump installer about a system like this. This way you're pulling fresh warm air in, rather than an EVR and heatpump competing with each other. 




timmmay
20574 posts

Uber Geek

Trusted
Lifetime subscriber

  #3353467 13-Mar-2025 13:17
Send private message

Have a read of this ducted heatpump FAQ.

 

What I did was put the ventilation system output close to the ducted system return grill, and put the ventilation system on a timer. Once a day I turn on ventilation and the ducted heat pump to fan mode to push fresh air around the house. I turned the ventilation system on sometimes when the ducted system is heating or cooling as well. It's a reasonably good and fairly simple solution. Getting an ERV is a better solution, but is it better enough for the cost? Not sure about that one. I have no plans to get an ERV.

 

Linear grills, the MDO ones that can push air in different directions, are significantly better than the round outlets. The round ones often just push air across the ceiling, but it depends on how the air is exiting the room back towards the return grill. Wall / door vents are often better than undercut doors, as you need more undercut than you'd expect - a couple of cm which is weird looking.


tweake
2391 posts

Uber Geek


  #3353715 13-Mar-2025 17:21
Send private message

i'll try to come back to this later, its been a long day.

 

basics, it depends on grill locations. most likely the ventilation grills will be in the wrong location for heating/cooling. so the options are either leave the DVS as is or remove the DVS grills and fix up the ceiling. having two grills can make it look a bit poor but its the cheapest and easiest solution, just install the heat pump system and its done.

 

DVS vers ERV, unless the house is reasonably air tight i doubt the erv will bring much benefit, especially for the cost. i think the biggest problem will be how well the house is insulated. concrete block (ie breeze block) are typically not insulated (and yes nz building code does allow that) but if its is its important to know how its done. also ERV keeps moisture IN a home (as well as keeping moisture out), so you need a way to manage moisture levels or at least measure humidity levels. one of the ways concrete block houses are insulated is with pir/iso panels, which do not allow moisture to go through it (ie stops the house from drying) which means you have to be extra careful with moisture management if you have that system. 




generationy

4 posts

Wannabe Geek


  #3353898 14-Mar-2025 10:56
Send private message

lxsw20:

 

We are in process of building, our system will be a ducted heat pump connected to a fresh air heat exchanger. (Daikin equivalent of Mitsubishi Lossney) 

 

It would be worth talking to your heat pump installer about a system like this. This way you're pulling fresh warm air in, rather than an EVR and heatpump competing with each other. 

 

 

Yes actually this was the type of setup im contemplating.  Using Lossnay for most of the year ventilation (circulation) an heat pump when needed.


generationy

4 posts

Wannabe Geek


  #3353899 14-Mar-2025 11:00
Send private message

timmmay:

 

Have a read of this ducted heatpump FAQ.

 

What I did was put the ventilation system output close to the ducted system return grill, and put the ventilation system on a timer. Once a day I turn on ventilation and the ducted heat pump to fan mode to push fresh air around the house. I turned the ventilation system on sometimes when the ducted system is heating or cooling as well. It's a reasonably good and fairly simple solution. Getting an ERV is a better solution, but is it better enough for the cost? Not sure about that one. I have no plans to get an ERV.

 

Linear grills, the MDO ones that can push air in different directions, are significantly better than the round outlets. The round ones often just push air across the ceiling, but it depends on how the air is exiting the room back towards the return grill. Wall / door vents are often better than undercut doors, as you need more undercut than you'd expect - a couple of cm which is weird looking.

 

 

Thank you of the link - a lot of pages to read through. 
1) ok you've backup my idea about ducted system and DVS together are a possibility. I'll just see how much it is to get the ERV (Lossnay or similar) installed.  I think the installer said its about 3k. 
2) Ok that's the second person that has said the round outlets are fairly poor.  


generationy

4 posts

Wannabe Geek


  #3353903 14-Mar-2025 11:08
Send private message

tweake:

 

i'll try to come back to this later, its been a long day.

 

basics, it depends on grill locations. most likely the ventilation grills will be in the wrong location for heating/cooling. so the options are either leave the DVS as is or remove the DVS grills and fix up the ceiling. having two grills can make it look a bit poor but its the cheapest and easiest solution, just install the heat pump system and its done.

 

DVS vers ERV, unless the house is reasonably air tight i doubt the erv will bring much benefit, especially for the cost. i think the biggest problem will be how well the house is insulated. concrete block (ie breeze block) are typically not insulated (and yes nz building code does allow that) but if its is its important to know how its done. also ERV keeps moisture IN a home (as well as keeping moisture out), so you need a way to manage moisture levels or at least measure humidity levels. one of the ways concrete block houses are insulated is with pir/iso panels, which do not allow moisture to go through it (ie stops the house from drying) which means you have to be extra careful with moisture management if you have that system. 

 

 

 

 

Thanks Tweake.  
I'm leaning towards getting of most of our DVS (just retaining for the garage) and adding a ERV (Lossnay type). We are out of the house quite a lot and it would be good to have ventilation on during that time.  I might need to seal up your leaky front door though. 

 

We are concrete blog but it's all insulated and with Jib so it's quite warm.  

 

Hopefully the Airtouch system will work well with ERV as I'd like it to run in ERV mode a lot. 


tweake
2391 posts

Uber Geek


  #3354018 14-Mar-2025 16:08
Send private message

generationy:

 

Thanks Tweake.  
I'm leaning towards getting of most of our DVS (just retaining for the garage) and adding a ERV (Lossnay type). We are out of the house quite a lot and it would be good to have ventilation on during that time.  I might need to seal up your leaky front door though. 

 

We are concrete blog but it's all insulated and with Jib so it's quite warm.  

 

Hopefully the Airtouch system will work well with ERV as I'd like it to run in ERV mode a lot. 

 

 

an ERV should run all the time. its all about constant ventilation rather than variable ventilation the DVS gives.

 

the tricky thing is integrating it into the ducted heat pump as you need the heat pump fan to be running to circulate the air. have a look at some of the issues found in some recent threads. 

 

the more i've seen of the lossnay the more i'm starting to dislike them (it needs the controller). if Panasonic heat pump is an option then look at Panasonic ERV. ideally try to use the same brand erv and heat pump as eg the Panasonic heatpump controller also does the erv. also i think the Panasonic you can run without needing a controller (i'm not sure on the models we get here as they are fairly new).

 

afaik airtouch doesn't do erv's, but with a good erv you should never need a controller. you set it and leave it to run all the time. 


 
 
 

Cloud spending continues to surge globally, but most organisations haven’t made the changes necessary to maximise the value and cost-efficiency benefits of their cloud investments. Download the whitepaper From Overspend to Advantage now.
raytaylor
4014 posts

Uber Geek

Trusted

  #3355270 19-Mar-2025 16:57
Send private message

I cant remember the specifics of the DVS system but we have heat pumps in our house in addition to an HRV system.  
The reason is that the heat pumps, even if ducted, recirculate air and when not cooling they wont be dehumidifying. 
So the HRV/DVS would be bringing in dry air to prevent mould. 

 

ALSO

 

I like that in winter, i can set the temperature on the HRV to max/27 and on a sunny day and heat up the house with the power consumption of a desk fan.
While no one is at home during the day, the mass in the living space absorbs that heat and releases it into the evening. 
Then we dont need the heat pump system do do any work until later into the evening.  





Ray Taylor

There is no place like localhost

Spreadsheet for Comparing Electricity Plans Here


Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.