qwerty7

434 posts

Ultimate Geek
Inactive user


#97487 15-Feb-2012 15:43
Send private message

I was wondering if anybody wanted to answer some questions that come from my natural curiosity about electricity. I feel I have a reasonable understanding but still have some questions. 

1)How many phases is standard house power in new zealand?  

2)I understand that a ground/earth is in case a hot wire touches a metal cased appliance. But what is the other side of this circuit the electricity goes into the ground through the ground spike or water pipe but then where ?

3)In a power point you have a hot wire a neutral wire and a ground/earth. What is the return path for the neutral wire? Does it travel back through the power lines down the street to the substation where it ground into the earth?

Create new topic
cyril7
9058 posts

Uber Geek

ID Verified
Trusted
Subscriber

  #581911 15-Feb-2012 15:53
Send private message

Hi, one phase is normal, but 2phases in particular with older homes is not uncommon, three phase for domestic is quite rare.
 
The neutral and earth are connected together in the switchboard (and street transformer), this means the phase and neutral are referenced to the earth potential (whatever that may be). If the phase touches the case which is connected to earth then the current flows back to the street transformer via the ground current (yes through the soil).

And yes the current normallly flows between phase and neutral, which are referenced to the ground potential, in theory no current flows through the earth. If a fault condition occurs then that fault current will now flow down the earth rather than the netural, this imbalance in phase/neutral current is what will trip an RCD if in circuit.

hope that helps.
Cyril



stevenz
2802 posts

Uber Geek


  #581924 15-Feb-2012 16:04
Send private message

Similar to this, what would be an expected maximum deviation from norm for supplied voltage\frequency?




cyril7
9058 posts

Uber Geek

ID Verified
Trusted
Subscriber

  #581928 15-Feb-2012 16:08
Send private message

Suppliers are required to maintain the voltage to within +-5% and as for frequency, I could not tell you off the top of my head but the infinite bus that it all is tied to and the level of load and generation resource will dictate how far it steps from the nominal 50Hz. A slowing of frequency (therefore a slowing of all rotating machines on the infinite bus) due to a lack of rotating source machines (generators) compared to the load is what caused the network to faulter a few months back.

Cyril



lchiu7
6472 posts

Uber Geek

Trusted

  #581973 15-Feb-2012 17:44
Send private message

cyril7: Suppliers are required to maintain the voltage to within +-5% and as for frequency, I could not tell you off the top of my head but the infinite bus that it all is tied to and the level of load and generation resource will dictate how far it steps from the nominal 50Hz. A slowing of frequency (therefore a slowing of all rotating machines on the infinite bus) due to a lack of rotating source machines (generators) compared to the load is what caused the network to faulter a few months back.

Cyril


Transpower contracts generators to do frequency keeping. Generators makes offers for this work as for any generation they offer to the market.

I can't remember exactly what the tolerances are but they are something like 49.8 to 50.2 Hz (something like that).  If for whatever reason the frequency drops below certain tolerances frequency keeping stations kick in and if more then load shedding can take place,

As an aside in the SI because of the lack of reactive load (a lot of the load in the SI is from the Aluminium smelter which does not place a reactive load on the network), frequency can go up and there is a need to lower it to the accepted level.

A few months ago was a once in a 40 year event. There was a bus failure at Huntley which I understand caused a cascading trip at the station taking the entire station off line, simplistically speaking. That was about 900MW of generation gone. Of course that meant a drastic drop in frequency. The stations that are contracted to do frequency keeping kicked in to help recover the situation but there was too much generation gone off line for that to work. So AUFLS kicked in (which is Automatic Under Frequency Load Shedding, an appropriate acronym to be sure).

This causes stations/distributors to automatically shed load to reduce the load on the network.  This means areas in the NI lost power as the load shedding occurred.

Note that this entire event took place in about 6-7s and was handled automatically.  If there had to be manual intervention there would not have been enough time to shed the requisite load and the entire network might have collapsed. That would not have been a nice situation!




Staying in Wellington. Check out my AirBnB in the Wellington CBD.  https://www.airbnb.co.nz/h/wellycbd  PM me and mention GZ to get a 15% discount and no AirBnB charges.


qwerty7

434 posts

Ultimate Geek
Inactive user


  #582004 15-Feb-2012 19:14
Send private message

thanks, think i am finally getting my head around this
so i am guessing the power coming into my home is 240 volt single phase. 

the lines running down the street have 3 main wires running along the top (3 phase i guess) then there are 6 wires lower down (3 on each side of the post) which the houses seem to latch onto (there are wires attached to them running down the post. So how do i end up with 240 volt single phase, the 3 phase is stepped down from.. ?

cyril7
9058 posts

Uber Geek

ID Verified
Trusted
Subscriber

  #582007 15-Feb-2012 19:25
Send private message

Hi, in Oz and many other countries its 240V, but in NZ we have 230V.

The poles you see in the street will be carrying the 11kV feed on the 3 top wires, this will be the input to your local street transformer there are only 3wires in delta config, ie just 3 wires with no neutral. The lower 6 wires will be 3phases at LV (400/230V) in Y format, thats three phases plus neutral and the other two are most likely one for street lighting and one for load shed pilot but the exact config may vary from lines co to lines co and area to area.

At the street transformer the delta 11kV is transformed to 400V 3phase (230V/phase) in Y format so 3phases plus neutral and that neutral will be bonded to ground at the street transformer as well as each and every house connection.

Hope that helps

Cyril

Nikoftime
103 posts

Master Geek


  #582312 16-Feb-2012 12:42
Send private message

The New Zealand electricty regulations 1997 are available at
http://energysafety.govt.nz/upload/33242/Electricity_Regulations_1997.pdf
for some further information

 
 
 

Cloud spending continues to surge globally, but most organisations haven’t made the changes necessary to maximise the value and cost-efficiency benefits of their cloud investments. Download the whitepaper From Overspend to Advantage now.
Handle9
11386 posts

Uber Geek

Trusted
Lifetime subscriber

  #582320 16-Feb-2012 12:54
Send private message

qwerty7: thanks, think i am finally getting my head around this
so i am guessing the power coming into my home is 240 volt single phase. 

the lines running down the street have 3 main wires running along the top (3 phase i guess) then there are 6 wires lower down (3 on each side of the post) which the houses seem to latch onto (there are wires attached to them running down the post. So how do i end up with 240 volt single phase, the 3 phase is stepped down from.. ?


3 Phase is 400V potential phase to phase or 230V phase to neutral. It's not stepped down it's just a different potential from phase to nuetral than phase to phase.

http://en.wikipedia.org/wiki/Delta-wye_transformer 

k14

k14
629 posts

Ultimate Geek


  #582334 16-Feb-2012 13:13
Send private message

lchiu7: Transpower contracts generators to do frequency keeping. Generators makes offers for this work as for any generation they offer to the market.

I can't remember exactly what the tolerances are but they are something like 49.8 to 50.2 Hz (something like that).  If for whatever reason the frequency drops below certain tolerances frequency keeping stations kick in and if more then load shedding can take place,

That is correct, the frequency keeper tries to keep their respective islands frequency (NI and SI frequency are independent because of the DC link between islands) between 49.8 and 50.2Hz. When it falls below this threshold instantaneous reserve kicks in which is referred to as FIR and SIR. Fast Instantaneous Reserve is available within 6 seconds and able to be sustained for 60 seconds. Sustained Instantaneous Reserve is available within 60 seconds and able to be sustained for 15 minutes. For over frequency events generators can be armed to trip off if the frequency reaches a certain level, although that is a much lower risk compared to a low frequency.

FYI I am currently the SI frequency keeper. In general it stays between 49.9 and 50.1 for 98% of the time but when it does drop you have no time to react hence the full automation of the system and the AUFULS for backup. I don't want to have to go through a black start (starting the whole island up from scratch!), would take too much time away from sitting on Geekzone Tongue Out

cyril7
9058 posts

Uber Geek

ID Verified
Trusted
Subscriber

  #582338 16-Feb-2012 13:18
Send private message

I don't want to have to go through a black start (starting the whole island up from scratch!), would take too much time away from sitting on Geekzone


And I guess months of endless paper work to follow :)

Cyril

lchiu7
6472 posts

Uber Geek

Trusted

  #582356 16-Feb-2012 13:46
Send private message

From what I have been told when MOW built the power stations they had black start capability. But when the kit was out of maintenance it was deemed not necessary to keep going give the unlikelihood of the event. But the Huntley incident got close!

Now there are two stations (one NI and one SI) that are responsible for black start so that the outage would be minimal (not that it would not a major impact). The spectre of folks driving madly to power stations carrying portable generators to power gates etc. is mind boggling!




Staying in Wellington. Check out my AirBnB in the Wellington CBD.  https://www.airbnb.co.nz/h/wellycbd  PM me and mention GZ to get a 15% discount and no AirBnB charges.


k14

k14
629 posts

Ultimate Geek


  #582366 16-Feb-2012 13:54
Send private message

lchiu7: From what I have been told when MOW built the power stations they had black start capability. But when the kit was out of maintenance it was deemed not necessary to keep going give the unlikelihood of the event. But the Huntley incident got close!

Now there are two stations (one NI and one SI) that are responsible for black start so that the outage would be minimal (not that it would not a major impact). The spectre of folks driving madly to power stations carrying portable generators to power gates etc. is mind boggling!

Yeah the Clyde dam is capable of black starting the SI grid. Whether it actually is successful is another question, you can test as much as you want but you'll never get to do a test on a fully black grid! Not till the time it has to work is upon us.

The whole station will function fine however with power and all generators shut down. Diesel backup generator to power the essential AC systems and UPS's/DC battery backup for control system PC's and generator sensors etc mean that everything is always read to go. It gets quite complex though having Transpower switching in the right transmission lines/busses and getting the right amount of load on a generator (or two) and having a semi stable localised system before the main objective (Tiwai) is bought back on.

Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.