#303640 24-Feb-2023 17:01
Send private message

Hi all,

 

I am having a discussion with my electrician who believes that all EVSE's require a Type B RCD, even the Tesla Wall Connector.

 

He sites a Worksafe guidance quoting Electrolink Issue 135 that states:

 

 

 

 

However, I also note from the Tesla Gen 3 Wall Connector Install Guide https://www.tesla.com/sites/default/files/support/charging/Gen3_WallConnector_Installation_Manual_AU_NZ.pdf

 

 

Does anyone know whether the Worksafe guidance has changed?  and whether a Type B RCD is still a requirement?

 

 


Create new topic
michaelmurfy
meow
13240 posts

Uber Geek

Moderator
ID Verified
Trusted
Lifetime subscriber

  #3041463 24-Feb-2023 17:14
Send private message

Nope. I have got one installed and my Sparky said it doesn't require a Type B RCD, it has leakage detection built in.





Michael Murphy | https://murfy.nz
Referral Links: Quic Broadband (use R122101E7CV7Q for free setup)

Are you happy with what you get from Geekzone? Please consider supporting us by subscribing.
Opinions are my own and not the views of my employer.




  #3041529 24-Feb-2023 18:33
Send private message

The 'guidelines' are not 'law' as such. If you comply with 3000, you're compliant... but worksafe really, really, really wants you to follow the guidance.

 

There's an addendum to the guidelines now: https://www.worksafe.govt.nz/dmsdocument/22031-addendum-to-electric-vehicle-charging-safety-guidelines-2nd-edition/latest

 

I think they're still saying you need to have the type B RCD for a residential install, but it's a mess:

 

 

 

> 2. Where any safety function is not provided as part
of the installed charging station or IC-CPD, the
safety function shall be installed at the origin
of the supplying final subcircuit.

 

Exception proves the rule, so if your IC-CPD/EVSE contains the required safety functions, you don't need them at the board?

 


> 3. Where an EVSE is installed at a residential
installation, the charging final subcircuit shall
be protected by a type B RCD and the subcircuit
shall originate from a MEN switchboard.

 

But if it's residential, you must have a type B at the board, and lesser known, it must be an MEN board. I thought previously they were stating that it must be an MSB or a non-MEN sub-board because they don't want people using MEN subboards where a submain neutral is also acting as an earth...

 

 

 

> Use of RDC-DDs

 

> While the guidelines do not recognise the use of an RDC-DD incorporated into an IC-CPD, they do not prevent the use of an RDC-DD in compliance with IEC 62955 in combination with a type A RCD as an alternative to the use of a type B RCD, provided the RDC-DD and the type A RCD are installed in accordance with the relevant IEC Standards.

 

> While the guidelines do not recognise the use of EVSE that incorporates a type B RCD, they do not restrict the use of EVSE that incorporates a type B RCD without the need to install a Type B RCD protecting the final subcircuit.

 

Sounds like a "you're on your own".

 

> Note: AS/NZS 3000 requires an RCD that provides protection for new final subcircuits installed in a residential installation.

 

Noting that if you do choose to rely on the RDC-DD or type B RCD integrated into the IC-CPD/EVSE, residential installations still need at least a type A RCD protecting the subcircuit cabling*. Which implies that you can choose to rely on the onboard protection in a residential situation.

 

* Which is incorrect, as it's only circuits feeding socket-outlets, lighting, or directly-connected handheld equipment like hair-dryers or tools that require an RCD per 3000. RCDs are not required by 3000 on other circuits such as ovens, water heaters, AC units, and presumably EVSE.

 

 

 

Our regulators need a good slapping.


wonderstuff

110 posts

Master Geek


  #3041539 24-Feb-2023 18:51
Send private message

Yeah it is pretty confusing for end customers and electricians.

 

I was looking through a few other websites too.

 

Another website to look at is Evnex, which is a NZ designer and manufacturer of EV chargers.   On their site they have this page:  https://www.evnex.com/articles/ev-charging-and-type-b-rcds

 

 

This essentially repeats what you have stated above.

 

 

 

 

Here is a thread on the Tesla Motors Club forum about Gen 3 charger installations in NZ.:   https://teslamotorsclub.com/tmc/threads/gen-3-wall-charger-now-on-the-nz-store.231966/

 

 

 

 

 

So it seems acceptable to not need a Type B.



michaelmurfy
meow
13240 posts

Uber Geek

Moderator
ID Verified
Trusted
Lifetime subscriber

  #3041579 24-Feb-2023 19:34
Send private message

Just a note - the Gen 2 Tesla wall connector does require a Type B RCD. The Gen 3 doesn't.

 

During provisioning it has a switch for it in the installer settings and explains what it does:

 

 

 

Do note, while I have a wall connector and have a knowledge about these sorts of things I am not a Sparky. Please ensure you consult with a Sparky and have them configure the wall connector for you (or have them guide you through it) as entering the wrong settings can be dangerous. My Sparky is really knowledgeable about these and he did state the Type B is not required but I do however have a Type A RCD dedicated to the charger.





Michael Murphy | https://murfy.nz
Referral Links: Quic Broadband (use R122101E7CV7Q for free setup)

Are you happy with what you get from Geekzone? Please consider supporting us by subscribing.
Opinions are my own and not the views of my employer.


  #3041638 24-Feb-2023 22:05
Send private message

Ground (continuity) monitoring is not the same as leakage current detection.


Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.