Chorusnz
430 posts

Ultimate Geek

Trusted
Chorus

  #2294745 12-Aug-2019 13:00
Send private message

@sparkz25 as is quite clearly written in the highlighted section that is the requirement for work done on council berm and roadways, not inside individual premises.

 

I’ve said before, this page on the chorus website: https://www.chorus.co.nz/help-and-support/digging/what-trenching is aimed at developers or homeowners who want the Fibre cable run through additional mechanical protection. It details the standards for running your own green PVC conduit that our technicians can haul the Fibre cables through.

 

 

 

@iwanttobeamole running microduct under pavers or stones is a different set of requirements again. If those are pavers for a path that will only get foot traffic then its fine. However if this is done in a shared driveway where vehicles are likely to drive over them we would expect it to be trenched as well.

 

If you could send us a DM with your address. I would like to look into this further.

 

 

 

@Jase2985 no two jobs are the same and as such there is no single piece of documentation that defines the requirements for our technicians to follow. You have taken the details on our website out of context which is why they don’t align with what I have written. This is why we don’t provide the full documentation on our website. Because it would A) be long winded and B) be easily taken out of context.

 

 

 

We do have processes in place to ensure installs are done to standard. However we complete hundreds of installs a day and cannot be everywhere. So if anyone is unhappy with the work done they can raise an issue with us or their broadband provider and we can follow up to ensure its been done to standard. ^Richard




duckDecoy
898 posts

Ultimate Geek

Subscriber

  #2294766 12-Aug-2019 13:48
Send private message

Chorusnz:

 

I’ve said before, this page on the chorus website: https://www.chorus.co.nz/help-and-support/digging/what-trenching is aimed at developers or homeowners who want the Fibre cable run through additional mechanical protection. It details the standards for running your own green PVC conduit that our technicians can haul the Fibre cables through.

 

 

Lets say the installer scopes a plan and says they will micro trench it (I think that's the word), i.e. dig a spade into the dirt and lay the fibre into the ground not within a conduit.  What if I want it in a conduit because i'm paranoid about say the gardening that happens here.  Can I lay conduit 200mm deep rather than the 450mm and have them pull it through?  A tech on one site scope said no.

 

Edit - forgot to tag @Chorusnz


Chorusnz
430 posts

Ultimate Geek

Trusted
Chorus

  #2294824 12-Aug-2019 14:32
Send private message

@duckDecoy the tech would be correct there. If you want PVC pipe (Aka conduit) around the cable then that conduit needs to be buried at 450mm or deeper. That depth is to protect the conduit from cracking if weight is applied to it from walking and other use.

 

You will need to dig the trench yourself to the 450mm depth and lay the conduit with a draw tape so our tech can come and haul the cable through. ^Richard




duckDecoy
898 posts

Ultimate Geek

Subscriber

  #2295117 12-Aug-2019 20:31
Send private message

Chorusnz:

 

@duckDecoy the tech would be correct there. If you want PVC pipe (Aka conduit) around the cable then that conduit needs to be buried at 450mm or deeper. That depth is to protect the conduit from cracking if weight is applied to it from walking and other use.

 

You will need to dig the trench yourself to the 450mm depth and lay the conduit with a draw tape so our tech can come and haul the cable through. ^Richard

 

 

Thanks @Chorusnz.

 

Is it worse to put the regular micro trench cable into a duct that is only 200mm underground?  That's what I was curious about, if it is in the regular sheath wouldn't it be even more protected, even if the duct cracked?  Or is there a reason that is less safe than just having the bare sheath buried.  My mother in law, who is getting fibre, is worried about spading as it runs through her garden.  I would have thought it is additional protection, but are you saying it might be worse?


Chorusnz
430 posts

Ultimate Geek

Trusted
Chorus

  #2296499 13-Aug-2019 13:32
Send private message

Oh for sure it would be even more protected in additional duct, even if that duct was cracked.

 

We direct the duct to be buried at 450mm so it won’t crack. Because if it does, they usually end up filled with dirt that obstructs us from hauling the cables through.

 

In your specific instance I take it you’re wondering why the tech wouldn’t let you lay the green pipe into the 200mm deep trench? I would suggest he is trying to cover himself and his work. We require our technicians adhere to all the standards and so if at some point in the future it was found that he didn’t follow the requirements, resulting in an issue. He would then be liable to make it compliant.

 

If you have the trench and the green pipe, you are welcome to dig it to the 450mm depth and lay the pipe yourself with a draw tape. I’m sure the tech would be happy to haul the cables through then. ^Richard


1 | 2 | 3 
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.