Topic # 115689 3-Apr-2013 17:53
Send private message

Not sure if this is the right category for this thread but....

Does anyone have any idea how much power consumption (in continuous watts or kwh per month) it would take to keep an area the size of a typical bathroom at 21 degrees?

I intend to install a server rack running approx 10 Supermicro servers into a similar space.

This would be in Tauranga where the climate is over 21 degrees 6 months of the year which would also need to be factored in.

Thoughts?

Filter this topic showing only the reply marked as answer Create new topic
3282 posts

Uber Geek
+1 received by user: 208

Trusted

  Reply # 792580 3-Apr-2013 18:10
One person supports this post
Send private message

It obviously depends how much heat the servers are dissipating, surely?



719 posts

Ultimate Geek
+1 received by user: 174

Trusted
Full Flavour

  Reply # 792581 3-Apr-2013 18:12
Send private message

I know it's a piece of string question but I was looking for a ballpark based on other people's experiences.

Assume average dual quad-core Supermicro server @ 50% load.

1741 posts

Uber Geek
+1 received by user: 587

Trusted
Subscriber

  Reply # 792594 3-Apr-2013 18:33
Send private message

myfullflavour: I know it's a piece of string question but I was looking for a ballpark based on other people's experiences.

Assume average dual quad-core Supermicro server @ 50% load.


I'm not trying to be funny but it depends on the load (is how much energy the servers consume) as well as the nature of the building, the solar load etc etc. If you undersize the unit then it consumes more power and never gets to setpoint, if you oversize it you get short cycling or hunting, which consumes lots of power.

You need to talk to a specialist who will come and have a look at your site.

nix

137 posts

Master Geek
+1 received by user: 1


  Reply # 792629 3-Apr-2013 19:31
Send private message

Talk to an installer. They have calculators for this sort of thing.

1076 posts

Uber Geek
+1 received by user: 31


  Reply # 792931 4-Apr-2013 09:22
Send private message

If you can estimate the amount of heat generated by your servers, then you can use the EER rating of a suitably sized heatpump to estimate cooling power consumption. An EER of 4 could be typical (for a heatpump rated at 4kW cooling), so if you had an average load of 2kW of servers, then you would consume an average of 500W of power for air conditioning.

Mad Scientist
18623 posts

Uber Geek
+1 received by user: 2367

Trusted
Lifetime subscriber

  Reply # 792940 4-Apr-2013 09:38
Send private message

there's one way to find out :D

3343 posts

Uber Geek
+1 received by user: 1089

Trusted
Vocus

  Reply # 792944 4-Apr-2013 09:41
Send private message

Yep, whatever power the servers consume, they will exhaust as heat.  So figure that out, then you know the heat capacity needed.  Add the requirements for the room itself as if it were empty, and you're good.  I understand most A/C units run best at around 70-80% of capacity but check with an installer to be sure.

1076 posts

Uber Geek
+1 received by user: 31


  Reply # 793036 4-Apr-2013 11:24
Send private message

ubergeeknz: Yep, whatever power the servers consume, they will exhaust as heat.  So figure that out, then you know the heat capacity needed.  Add the requirements for the room itself as if it were empty, and you're good.  I understand most A/C units run best at around 70-80% of capacity but check with an installer to be sure.


I would check with the manufacturer. Request performance curves if you really care that much.



719 posts

Ultimate Geek
+1 received by user: 174

Trusted
Full Flavour

  Reply # 793156 4-Apr-2013 13:22
Send private message

Appreciate all your help.

6656 posts

Uber Geek
+1 received by user: 568

Trusted

  Reply # 793162 4-Apr-2013 13:33
Send private message

Requesting a no obligation free quote from several installers should see you right.

As above though, most of what you put into the servers power wise will end up as heat. Servers use more power under different loads, so that's a bit of a guestimation. Also the room itself will have different solar gains/load depending on where it's positioned in the building and the buildings construction.

You can't get away from the fact that anything anyone gives you is a guess of varying accuracy, and we're not trying to be dcks about it.

3210 posts

Uber Geek
+1 received by user: 616

Trusted

  Reply # 805372 25-Apr-2013 11:17
Send private message

If you are using 1000 watts of power for the servers, then we could guess thats 1000 watts of heat being generated.

An air conditioner usually has a factor of about 4x efficiency. I forget the exact term but for every 100 watts of power they consume, they can move 400 watts of heat. Though that changes based on the outside temperature because they have to work harder when its hotter outside.

So I would guesstimate that you would use 250-300 watts worth of power if your servers consume 1000watts

300 * 24 = 7,200 watts per day
7,200 / 1000 = 7.2 kilowatts or units of power per day

7.2 * 365 =  2,628 kw per year
2,628 / 12 = 219 kw per month

219 * 0.25 = $54.75 per month (assuming 25 cents per kilowatt or unit)


You will of course get some heat coming in through the walls.
You also dont need a big unit, though you do need to oversize it. Get one designed for a small lounge or a room double or triple the space as most heat pumps are not designed to fight a fan heater (or equivalent)




Ray Taylor
Taylor Broadband (rural hawkes bay)
www.ruralkiwi.com

There is no place like localhost
For my general guide to extending your wireless network Click Here




1984 posts

Uber Geek
+1 received by user: 133

Trusted

  Reply # 825322 25-May-2013 19:50
One person supports this post
Send private message

Handle9:
myfullflavour: I know it's a piece of string question but I was looking for a ballpark based on other people's experiences.

Assume average dual quad-core Supermicro server @ 50% load.


I'm not trying to be funny but it depends on the load (is how much energy the servers consume) as well as the nature of the building, the solar load etc etc. If you undersize the unit then it consumes more power and never gets to setpoint, if you oversize it you get short cycling or hunting, which consumes lots of power.

You need to talk to a specialist who will come and have a look at your site.

I'm not sure if short cycling uses all that much more power but will probably wear out the unit faster.

Problem is you are not cooling the room that much -- you are mostly cooling the servers.
  1. Servers produce whats called a sensible load, meaning they are dry heat -- instead of heat getting into the air from evaporation off warm objects (such as people or concrete walls).
  2. Undersized coolers have to work harder, so may become less reliable and need more maintenance.
  3. Aircon can dry out the air, especially if not designed for computer rooms. This causes problems with static, not ideal around computer equipment.
  4. At some point any aircon needs to be taken down for maintenance or will stop on its own, so plan how this will be handled whether by a second aircon or extractor fans. Redundancy is a good way to handle unplanned cooling outages.
  5. The power consumed by all servers, lighting, fans, the aircon indoor units themselves, and any other equipment is heat generated into the room. Add in the amount of heat coming into the room from outside, and any capacity you want for extra servers in future. The total kilowatts would be the cooling capacity needed -- as a sensible load, not the normal load. Rule of thumb (ie not too accurate) is something like total wattage consumed plus 20%, which probably equates to server consumption plus 50%. Aircon units normally have a total load rating about 10% to 30% above the sensible load but cant remember exactly.
  6. I think mitsubishi used to have an industrial aircon with a high sensible load that didnt dry out the air too much. Otherwise you might find a humidifier is often recommended to maintain correct humidity.
  7. You can save cooling costs a bit by using a cold aisle/hot aisle arrangement and even by using aisle containment to separate cold and hot air, so hot air goes straight into the aircon instead of being mixed in the room. This allows you to use maybe a 23deg or 24deg set point where aircon units are more efficient.




Qualified in business, certified in fibre, stuck in copper, have to keep going  ^_^

Filter this topic showing only the reply marked as answer Create new topic

Twitter »

Follow us to receive Twitter updates when new discussions are posted in our forums:



Follow us to receive Twitter updates when news items and blogs are posted in our frontpage:



Follow us to receive Twitter updates when tech item prices are listed in our price comparison site:





News »

Hawaiki Transpacific cable ready-for-service
Posted 20-Jul-2018 11:29


Microsoft Dynamics 365 Business Central launches
Posted 10-Jul-2018 10:40


Spark completes first milestone in voice platform upgrade
Posted 10-Jul-2018 09:36


Microsoft ices heated developers
Posted 6-Jul-2018 20:16


PB Technologies charged for its extended warranties and warned for bait advertising
Posted 3-Jul-2018 15:45


Almost 20,000 people claim credits from Spark
Posted 29-Jun-2018 10:40


Cove sells NZ's first insurance policy via chatbot
Posted 25-Jun-2018 10:04


N4L helping TAKA Trust bridge the digital divide for Lower Hutt students
Posted 18-Jun-2018 13:08


Winners Announced for 2018 CIO Awards
Posted 18-Jun-2018 13:03


Logitech Rally sets new standard for USB-connected video conference cameras
Posted 18-Jun-2018 09:27


Russell Stanners steps down as Vodafone NZ CEO
Posted 12-Jun-2018 09:13


Intergen recognised as 2018 Microsoft Country Partner of the Year for New Zealand
Posted 12-Jun-2018 08:00


Finalists Announced For Microsoft NZ Partner Awards
Posted 6-Jun-2018 15:12


Vocus Group and Vodafone announce joint venture to accelerate fibre innovation
Posted 5-Jun-2018 10:52


Kogan.com to launch Kogan Mobile in New Zealand
Posted 4-Jun-2018 14:34



Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.

Alternatively, you can receive a daily email with Geekzone updates.