I was looking through the manual for our generator the other day, and there was a section about earthing it if connecting to earthed devices. I don't really understand this. I would think that the generator's 220 volt output would act the same as an isolation transformer, precisely because there is not an earth connection. In a case like this, wouldn't earthing it actually make it less safe? Can someone explain this to me please?

 

 





Plesse igmore amd axxept applogies in adbance fir anu typos

 


 


Create new topic
gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #1765007 16-Apr-2017 13:18
Send private message

Your right about the generator effectively been similar to an isolating transformer. If it's a small generator, typically they are centre tapped 220V generators with the centre tap connected to the earth giving 110V on either pin to the the earth pin, Effectively this makes it a SELV system (segregated extra low voltage) not a low voltage system as it should be. Technically it's illegal to fit a standard NZ 3 pin socket to a generator like this, but it doesn't stop the company who sold it to you from doing that.

 

 




k1w1k1d
1519 posts

Uber Geek


  #1765060 16-Apr-2017 15:57
Send private message
Aredwood
3885 posts

Uber Geek


  #1765061 16-Apr-2017 15:57

If it is a center tapped generator. Never plug it into a caravan or the generator input of a building. As often the neutral and earth are linked together. So you will probably short out one of the generator windings. Or the generator frame will be live with 110V to ground. As a lot of these generators only have overload protection fitted to only 1 of the 110V windings.

They are originally designed for the US market. And have been kludged to provide NZ 230V. Far better will be if their output was completely isolated.







Rikkitic

Awrrr
18657 posts

Uber Geek

Lifetime subscriber

  #1765066 16-Apr-2017 16:22
Send private message

The generator is a Yamaha, so not cheap Chinese. Output is full sine wave 220 vac. There is a warning in the manual that it should be earthed if used with earthed equipment. I don't understand the point of that advice. If it is not earthed, it acts like an isolation transformer and the only way to get electrocuted is to put yourself between phase and neutral. I would think this would be safer than re-introducing a return path via earth. That is why I asked my question, which still isn't answered. Why do it this way at all? Isn't no earth better in this specific situation?

 

 





Plesse igmore amd axxept applogies in adbance fir anu typos

 


 


Rikkitic

Awrrr
18657 posts

Uber Geek

Lifetime subscriber

  #1765078 16-Apr-2017 16:30
Send private message

k1w1k1d: A bit of light reading on this subject; https://www.electricalforum.co.nz/index.php?action=more_details&id=1367459376

 

Thanks for the link. It seems to confirm what I already thought. My little 1.2 kVA petrol generator (which does not have RCD protection) should not be earthed and the advice in the manual is wrong.

 

 





Plesse igmore amd axxept applogies in adbance fir anu typos

 


 


richms
28168 posts

Uber Geek

Trusted
Lifetime subscriber

  #1765085 16-Apr-2017 16:53
Send private message

I got a 3000va one from bunnings to run stuff when vector were replacing a powerpole and I dont recall seeing anything in its manual about earthing anything.





Richard rich.ms

Rikkitic

Awrrr
18657 posts

Uber Geek

Lifetime subscriber

  #1765087 16-Apr-2017 17:01
Send private message

It is definitely there. Very clear. Maybe I will dig it out and copy it.

 

 





Plesse igmore amd axxept applogies in adbance fir anu typos

 


 


 
 
 

Cloud spending continues to surge globally, but most organisations haven’t made the changes necessary to maximise the value and cost-efficiency benefits of their cloud investments. Download the whitepaper From Overspend to Advantage now.
Aredwood
3885 posts

Uber Geek


  #1765142 16-Apr-2017 21:12

Another possibility - does the generator have a 12V output? If so that output might not be isolated from the mains. The generator might have the earth, neutral, 12V neg, and metal frame all electrically linked. If the output is isolated, you want it to be 100% isolated. Not maybe or might be isolated. There is a similar recommendation in the manual that came with my approx 15 year old inverter. It says that if I want to run something that is not inside my car, then I should install an earth stake to the mass of earth.

 

 

 

The only reason I can think of as to why. Is if you get 1 earth fault somewhere, and the frame is isolated from ground. Someone touching the generator frame might then get electrocuted. But you could still manage this hazard by using an RCD on the generator output. The generator manufacturer is probably trying to strike a balance between safety and number of callbacks. Especially as they have no idea and cannot control what their generators will be used for. Someone might even make up a suicide lead (cord with a male plug on both ends) so they can plug 1 end into the generator, and the other end into a power socket in their house. As a very dangerous way of connecting power from the generator to the whole house.






Rikkitic

Awrrr
18657 posts

Uber Geek

Lifetime subscriber

  #1765251 17-Apr-2017 10:26
Send private message

I like the idea of the suicide lead. I actually thought about doing that (just thought about it, no intention to carry through) but decided it would be too risky. The way to do it would be to first switch the main switch off to break the connection to the power lines. We have old house wiring, no RCD, neutral common to earth, wire fuses. On a system like that, I don't see a problem in principle but I still wouldn't do it. With a small generator like we have it just makes more sense to directly connect any devices we want to run.

 

 

 

 

 

 

 

 

 

 





Plesse igmore amd axxept applogies in adbance fir anu typos

 


 


gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #1765254 17-Apr-2017 10:41
Send private message

Rikkitic:

 

I like the idea of the suicide lead. I actually thought about doing that (just thought about it, no intention to carry through) but decided it would be too risky. The way to do it would be to first switch the main switch off to break the connection to the power lines. We have old house wiring, no RCD, neutral common to earth, wire fuses. On a system like that, I don't see a problem in principle but I still wouldn't do it. With a small generator like we have it just makes more sense to directly connect any devices we want to run.

 

 

 

Don't even say stuff like that, no matter how much you say it's a bad idea there is always someone out there who will give it ago......

 

 

 

 

 

 

 

 

 

 

 

 


Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.