Hi, Just need some guidance or direction regarding if we can have 110/120V dedicated wiring socket in NZ homes ?

 

 

 

I bought a device from US and using a 2000W stepdown transformer and its working perfectly fine.

 

Issue is - Transformer makes humming noise 24/7 so I was thinking if I can put that transformer in garage or next to power distribution and have separate switch/breaker and from there a 110/120V wire terminates to wall socket ?

 

So transformer can make humming sound in garage and we can have dedicated 110/120V socket in room with device plugged in.

 

 

 

Any thoughts or ideas or can do or cant do ?

 

 

 

Any expert electricians who can guide or help, will really appreciate.


View this topic in a long page with up to 500 replies per page Create new topic
 1 | 2
Wombat1
586 posts

Ultimate Geek
Inactive user


  #3061236 10-Apr-2023 23:26
Send private message

Some of the older NZ houses have 110V shaver sockets with an an isolating transformer behind them. 

 

Dont think you can install them anymore, and only ever saw them in the bathrooms. 

 

What US appliance is it? The transformer must be very innefficient too. 




CYaBro
4582 posts

Uber Geek

ID Verified
Trusted

  #3061240 11-Apr-2023 00:03
Send private message

My sister bought a house that was built by a Japanese family originally.
It has 110v sockets all over the place, including next to the toilets. 😂
They don’t use them as they don’t have 110v appliances so not sure if they even still work.




Opinions are my own and not the views of my employer.


Bung
6477 posts

Uber Geek

Subscriber

  #3061246 11-Apr-2023 01:24
Send private message

On another forum it was pointed out that now any new socket would need circuit breaker and RCD protection and there's unlikely to be a 110v RCD with NZ approval. Is the device that special that the cost is justified?



Handle9
11386 posts

Uber Geek

Trusted
Lifetime subscriber

  #3061249 11-Apr-2023 05:29
Send private message

I’m pretty sure it’s illegal but @gregmcc would know for sure.

SirHumphreyAppleby
2844 posts

Uber Geek


  #3061252 11-Apr-2023 06:39
Send private message

You may be able to keep it simple and just install direct wiring and treat the appliance and inverter as plug-in equipment.

 

We have an IEC C14 inlet near our UPS, connecting two remote sockets. The inlet is just an off-the-shelf IEC C14 connector mounted in a blank PDL 600-series plate. The electrician made it, and he was incredibly anal when it came to following the rules. If he was willing to sign off on a custom socket, I'm sure using a US plate from a reputable manufacturer isn't out of the question, but it's probably easier to change the plug on the appliance.


johno1234
2793 posts

Uber Geek


  #3061323 11-Apr-2023 08:51
Send private message

Might be cheaper to just buy a new stepdown transformer that is quiet.

 

 


richms
28168 posts

Uber Geek

Trusted
Lifetime subscriber

  #3061377 11-Apr-2023 12:01
Send private message

I was told no way to legally do this with standard US outlets and had to use yellow ceeform ones to be legit. Needed to have a dedicated breaker panel for it and all sorts of carry on like you would do if wiring up a data centre with things from a UPS.

 

I got a long US extension cord and put it down the hole that the dishwasher drain goes out to the basement where I have it plugged into the transformer.

 

A fancy starwars waffle iron is not worth the hassle TBH.





Richard rich.ms

 
 
 

Cloud spending continues to surge globally, but most organisations haven’t made the changes necessary to maximise the value and cost-efficiency benefits of their cloud investments. Download the whitepaper From Overspend to Advantage now.
Wombat1
586 posts

Ultimate Geek
Inactive user


  #3061429 11-Apr-2023 13:36
Send private message

As far as I was aware, it’s illegal to run extension cords through walls or floors etc. you may want to check the legality of that one.

mkissin
388 posts

Ultimate Geek

ID Verified

  #3061518 11-Apr-2023 15:28
Send private message

I think it's more subtle than that. It's illegal to use them as fixed wiring. As long as they're easily removable, you're probably fine.

 

I'm not a registered sparky though.


mdooher
Hmm, what to write...
1424 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #3061563 11-Apr-2023 16:40
Send private message

It is possible, and legal. However you will be dealing with part one of ANZS3000. You will need to upgrade your mains / main fuse to at least 80A and require a certified design.

 

you will be able to use equipment that is certified in another country (USA) for the portions of the installation where that applies.

 

one difficultly is that any appliance that can get near the 230V would need to be approved (or possibly tested) to that voltage (I'd need to check on that one)

 

All work will need to inspected as will any ongoing changes to the system.. even the smallest thing.

 

Getting 120V 60Hz from 230V 50Hz is not impossible but honestly is the cost of an inverter worth it?

 

My own house is done to part one (for different reasons, and only because I could design and wire it myself)

 

My advice is forget it. 





Matthew


gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #3061591 11-Apr-2023 17:44
Send private message

Bung: On another forum it was pointed out that now any new socket would need circuit breaker and RCD protection and there's unlikely to be a 110v RCD with NZ approval. Is the device that special that the cost is justified?

 

 

 

The new (230V) socket that the transformer plugged in to would need to be RCD protected, whatever is plugged in to that is an "accessory or appliance" there is no requirment for an RCD on an accessory or appliance. Keep in mind there would be no RCD protection on a 230V-120V transformer (110V side), but been an isolated supply it would make it harder to receive an electric shock (not impossible though).

 

 

 

 


gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #3061592 11-Apr-2023 17:47
Send private message

mdooher:

 

It is possible, and legal. However you will be dealing with part one of ANZS3000. You will need to upgrade your mains / main fuse to at least 80A and require a certified design.

 

you will be able to use equipment that is certified in another country (USA) for the portions of the installation where that applies.

 

one difficultly is that any appliance that can get near the 230V would need to be approved (or possibly tested) to that voltage (I'd need to check on that one)

 

All work will need to inspected as will any ongoing changes to the system.. even the smallest thing.

 

Getting 120V 60Hz from 230V 50Hz is not impossible but honestly is the cost of an inverter worth it?

 

My own house is done to part one (for different reasons, and only because I could design and wire it myself)

 

My advice is forget it. 

 

 

 

 

Can't do part 1 installs for domestic, must be part 2.

 

can do a part 2 with a certified design.

 

 


mdooher
Hmm, what to write...
1424 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #3061599 11-Apr-2023 18:14
Send private message

Sorry you are incorrect

 

Part one is is allowed as long as supply is above 80A...How do think I did my house?





Matthew


gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #3061602 11-Apr-2023 18:22
Send private message

randhawa012:

 

Hi, Just need some guidance or direction regarding if we can have 110/120V dedicated wiring socket in NZ homes ?

 

 

 

I bought a device from US and using a 2000W stepdown transformer and its working perfectly fine.

 

Issue is - Transformer makes humming noise 24/7 so I was thinking if I can put that transformer in garage or next to power distribution and have separate switch/breaker and from there a 110/120V wire terminates to wall socket ?

 

So transformer can make humming sound in garage and we can have dedicated 110/120V socket in room with device plugged in.

 

 

 

Any thoughts or ideas or can do or cant do ?

 

 

 

Any expert electricians who can guide or help, will really appreciate.

 

 

If you want to make the step down transformer part of the fixed wiring it will be a very expensive exercise, it can be done but be prepared to spend. 

 

Option would be to have an electrician run a 110V circuit with the appropriate circuit breaker to the appliance, and user a permanent connection (like is used on a heated towel rail) for the appliance. If you had a standard US socket it would be difficult to get a signed COC as the outlet would not have a SDOC. You may not need a RCD on a socket supplied from a isolation transformer (this is what the step down transformer does) but this would require further invesgation. This is something you need to engage an electrician for. A permanently connected appliance does not need a RCD protected circuit. (generally, unless there are wet area zoning issues).

 

 


gregmcc
2147 posts

Uber Geek

ID Verified
Trusted
Lifetime subscriber

  #3061605 11-Apr-2023 18:27
Send private message

mdooher:

 

Sorry you are incorrect

 

Part one is is allowed as long as supply is above 80A...How do think I did my house?

 

 

 

 

After looking at the ESR's, you are correct, bet you had a mission finding an inspector who signed off your part 1 install.......

 

 


 1 | 2
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.