timmmay:
That sounds really useful, can you update us once you get more info please?
Our system has four zones, three bedrooms (one spare) and the lounge. Our lounge is the spill zone, because usually an extra degree or two isn't a problem. Sometimes when it's annoying me I configure the spare room as the spill zone, though it's wasteful to heat / cool a room that's not actually being used.
@timmmay there's a somewhat confusing explanation of it starting on page 24 of the latest installation manual.
Spill zone opening works on percentages, whereas a bypass can only be fully open or fully shut. The manual actually suggests (if I understand it correctly) that the best option is to install ducting directly between the supply and return, but rather than installing a bypass damper install a regular zone damper instead and set it as a hidden spill zone. That means that if you're just heating the bedroom and the damper closes to 60% the "bypass" will open to 40% (instead of straight to 100% as it would with the actual bypass kit).
It seems strange that they offer a bypass kit, and then suggest a better way using the standard zone dampers. Maybe I'm misunderstanding it, or maybe a bypass damper is just a cheaper option since it's only fully open or closed.