Geekzone: technology news, blogs, forums
Guest
Welcome Guest.
You haven't logged in yet. If you don't have an account you can register now.


View this topic in a long page with up to 500 replies per page Create new topic
1 | ... | 5 | 6 | 7 | 8 | 9 | 10 | 11 | 12 | 13 | 14 | 15 | ... | 21
timmmay
20581 posts

Uber Geek

Trusted
Lifetime subscriber

  #3315139 2-Dec-2024 13:08
Send private message

Fan speed control isn't sufficient to eliminate spill. You may still have one room that needs only a very small amount of heat, if you give it the whole minimum output of a large heat pump it's going to overheat.

Spill or bypass is unfortunately necessary.



AlDrag

247 posts

Master Geek


  #3315783 4-Dec-2024 07:31
Send private message

Ok I really wanna finalise this today. I have a big problem with doing too much research and hesitating.

So unless someone says otherwise? Even though my house isn't most likely "airtight", ERV is the option to go with, due to being in the humid city of Auckland?

And to deal with humidity from showers/kitchen, I assume the addition of ventilation from an aircon inlet and lossnay inlet (downstairs in the kitchen) will allow the existing bathroom extractor fans and rangehood to perform much better? Even if they aren't directly in the same room?

I'm still trying to decide if airtouch5 is worth it. Our house is pretty small and I assume the internal walls aren't even insulated. But 1 side of the house does get hotter than the other throughout the day.
Mitsubishi does have zone control, but it only allows turning on/off the dampers.

Our attic gets really hot, so worried about the efficiency of the entire system during the day....but I guess it won't be used during the day that often....

timmmay
20581 posts

Uber Geek

Trusted
Lifetime subscriber

  #3315787 4-Dec-2024 07:47
Send private message

I wouldn't have a ducted system without individual room temperature control. If you don't have that, and your air conditioning, one side of the house will be too cold and the other will be too hot. If you're going to do ducted, do it properly.



AlDrag

247 posts

Master Geek


  #3315789 4-Dec-2024 07:52
Send private message

timmmay: I wouldn't have a ducted system without individual room temperature control. If you don't have that, and your air conditioning, one side of the house will be too cold and the other will be too hot. If you're going to do ducted, do it properly.


Right. Cool. Airtouch 5 locked in then (with bypass damper).

One thing I'm confused on, is how to control the lossnay if I have airtouch. I guess it'll just be a set fan speed?

timmmay
20581 posts

Uber Geek

Trusted
Lifetime subscriber

  #3315791 4-Dec-2024 08:15
Send private message

I can't help with Lossnay, best talk to your installer about the details.

tweake
2391 posts

Uber Geek


  #3315942 4-Dec-2024 17:04
Send private message

AlDrag: Ok I really wanna finalise this today. I have a big problem with doing too much research and hesitating.

So unless someone says otherwise? Even though my house isn't most likely "airtight", ERV is the option to go with, due to being in the humid city of Auckland?

And to deal with humidity from showers/kitchen, I assume the addition of ventilation from an aircon inlet and lossnay inlet (downstairs in the kitchen) will allow the existing bathroom extractor fans and rangehood to perform much better? Even if they aren't directly in the same room?

 

while i disagree with using erv/hrv in non-air tight houses, because you want the integration with the heat pump, then yes i would go with erv. but remember you need a way to monitor the homes humidity and at worse end up buying a dehumidifier.  

 

i would not use the bath fans, i'm not sure what would happen with both bath fan and erv exhausting from the bathroom at the same time. i would have to go ask someone about that.

 

IF you can get a duct downstairs then yes the range hood will work a tad better (depending on a lot of factors, you probably won't notice any difference) and you will get some much needed ventilation downstairs.


tweake
2391 posts

Uber Geek


  #3315948 4-Dec-2024 17:06
Send private message

AlDrag: 

One thing I'm confused on, is how to control the lossnay if I have airtouch. I guess it'll just be a set fan speed?

 

lossnay should come with its own controller. not sure of the heatpump controller can do both. its really only the bypass damper that needs controlling. once you set the speeds they never need touching.


 
 
 

Trade NZ and US shares and funds with Sharesies (affiliate link).
AlDrag

247 posts

Master Geek


  #3315969 4-Dec-2024 18:13
Send private message

tweake:

while i disagree with using erv/hrv in non-air tight houses, because you want the integration with the heat pump, then yes i would go with erv. but remember you need a way to monitor the homes humidity and at worse end up buying a dehumidifier.  


i would not use the bath fans, i'm not sure what would happen with both bath fan and erv exhausting from the bathroom at the same time. i would have to go ask someone about that.


IF you can get a duct downstairs then yes the range hood will work a tad better (depending on a lot of factors, you probably won't notice any difference) and you will get some much needed ventilation downstairs.



I assume the bathroom air would be pulled towards the vent with the most pressure but also what's closest to it.

So if an ERV has a permeable core, what happens to the moisture in a bathroom when it's venting?

tweake
2391 posts

Uber Geek


  #3315975 4-Dec-2024 19:13
Send private message

AlDrag: 

So if an ERV has a permeable core, what happens to the moisture in a bathroom when it's venting?

 

the moisture goes through the core into the incoming air stream and goes back into the house. as i mentioned before erv's keep outdoor moisture out, and indoor moisture in. now don't panic, the house volume of air will soak up that moisture just fine. however you do need to monitor the indoor humidity and make sure it doesn't go to high. worse case is you buy a dehumidifier.

 

on the plus side, your keeping outdoor humidity out and thats by far the greater amount of moisture.

 

 


AlDrag

247 posts

Master Geek


  #3315987 4-Dec-2024 21:05
Send private message

Right....I don't even know if I have the option of turning off the ventilator due to having Airtouch5. ugh.

 

 

 

Also, been living in our new house for almost a week now. Loving it, but jesus the sound proofing between each room is pathetic. I think this is due to the large gaps under the doors.
So tempted to now get return air ducts per room and do something about the gap under the doors. Last thing I want to do is keep everyone awake when gaming in my spare room at night or something...I guess I could just get headphones.


tweake
2391 posts

Uber Geek


  #3315988 4-Dec-2024 21:13
Send private message

AlDrag:

 

Right....I don't even know if I have the option of turning off the ventilator due to having Airtouch5. ugh.

 

 

is that a problem? you don't turn it off (except for service).


timmmay
20581 posts

Uber Geek

Trusted
Lifetime subscriber

  #3315989 4-Dec-2024 21:20
Send private message

Maybe there's no insulation in the walls for noise dampening?


AlDrag

247 posts

Master Geek


  #3315991 4-Dec-2024 21:26
Send private message

tweake
is that a problem? you don't turn it off (except for service).


Oh sorry, I just figured you sort of meant that if the humidity does get too high, then turn off ventilation. But I guess you're implying that a dehumidifier would be the only option in that case.

 

 

 

timmmay:

 

Maybe there's no insulation in the walls for noise dampening?

 

 

Most likely not. Pretty sure the building code doesn't require it and doing some reading, apparently the majority of building companies don't bother with internal insulation 😢

But we lived in a 70s home which I assume had no internal insulation, it was waaay quieter. But maybe the walls were just thicker, plus maybe being less airtight helped reduce echo etc?
The old house also had doors that touched the carpet, so I'm thinking that might be the main contributor.

 

I can understand why they undercut the doors, as it does allow fresh air to circulate. Sleeping in our old house with the door closed was unbearable once we woken up.


tweake
2391 posts

Uber Geek


  #3315994 4-Dec-2024 21:33
Send private message

AlDrag:
Oh sorry, I just figured you sort of meant that if the humidity does get too high, then turn off ventilation. But I guess you're implying that a dehumidifier would be the only option in that case.

 

 

yes. if humidity goes to high you would need to run a dehumidifier. unplugging the ventilation is ok for an emergency (or turn it off on the controller). there is just no need to turn it off as far as normal usage goes.


AlDrag

247 posts

Master Geek


  #3315996 4-Dec-2024 21:40
Send private message

tweake:

 

yes. if humidity goes to high you would need to run a dehumidifier. unplugging the ventilation is ok for an emergency (or turn it off on the controller). there is just no need to turn it off as far as normal usage goes.

 

 

 

 

I guess if someone ran a super hot shower for 30 mins without running the extractor fan, all that humidity would fill the house.

So the impression I'm getting, if I don't have a dehumidifer, is that with an ERV, we are able to have a dryer home, as it avoids bringing in Auckland humidity from the outside, but you run the risk of appliances in the house circulating humidity everywhere. Can get the humidity get too low?

HRV will always maintain the same humidity as outside, but probably a little lower due to the a/c. But obviously humidity won't get as low as ERV. I assume no where near as low.

 

Is this accurate? Sorry if I'm slow in understanding.


1 | ... | 5 | 6 | 7 | 8 | 9 | 10 | 11 | 12 | 13 | 14 | 15 | ... | 21
View this topic in a long page with up to 500 replies per page Create new topic





News and reviews »

Air New Zealand Starts AI adoption with OpenAI
Posted 24-Jul-2025 16:00


eero Pro 7 Review
Posted 23-Jul-2025 12:07


BeeStation Plus Review
Posted 21-Jul-2025 14:21


eero Unveils New Wi-Fi 7 Products in New Zealand
Posted 21-Jul-2025 00:01


WiZ Introduces HDMI Sync Box and other Light Devices
Posted 20-Jul-2025 17:32


RedShield Enhances DDoS and Bot Attack Protection
Posted 20-Jul-2025 17:26


Seagate Ships 30TB Drives
Posted 17-Jul-2025 11:24


Oclean AirPump A10 Water Flosser Review
Posted 13-Jul-2025 11:05


Samsung Galaxy Z Fold7: Raising the Bar for Smartphones
Posted 10-Jul-2025 02:01


Samsung Galaxy Z Flip7 Brings New Edge-To-Edge FlexWindow
Posted 10-Jul-2025 02:01


Epson Launches New AM-C550Z WorkForce Enterprise printer
Posted 9-Jul-2025 18:22


Samsung Releases Smart Monitor M9
Posted 9-Jul-2025 17:46


Nearly Half of Older Kiwis Still Write their Passwords on Paper
Posted 9-Jul-2025 08:42


D-Link 4G+ Cat6 Wi-Fi 6 DWR-933M Mobile Hotspot Review
Posted 1-Jul-2025 11:34


Oppo A5 Series Launches With New Levels of Durability
Posted 30-Jun-2025 10:15









Geekzone Live »

Try automatic live updates from Geekzone directly in your browser, without refreshing the page, with Geekzone Live now.



Are you subscribed to our RSS feed? You can download the latest headlines and summaries from our stories directly to your computer or smartphone by using a feed reader.